Compressor Start Capacitor Question

Posted by sniffdog (My Page) on
Fri, Dec 16, 11 at 7:26

I want to purchase spare parts for my Econar Geosource 2000 GSHP because of recurring failures (all different) and a long wait time to find replacements.

One of the items I am having trouble finding is a Compressor Start Capacitor that exactly matches the specs that are on the current (working) part.

The Econar unit I have is a 5 ton vertical unit with a scroll compressor.

The CSC has the following notes on the can:
60 UF, 370V
40/070/21 P25H
325P808H37N36N4X
20-0374
it is a round can

I found on grainger.com two Dayton CSC's that are close but not exact. Can I use one of these as a replacement - or do I have to match the original exactly?

Dayton 2MEL2: 53-64MFD, 330V
Dayton 2MEL3: 64-77MFD, 330V

I wonder why the original part only has 1 capacitance rating while most of the parts I am finding have a range. Also - what is the signficinace of the 370V rating on the original vs. the 330V rating on the Dayton parts. Can you exaplain why that is?

If I can't use the Dayton parts, can you point me to a source where I can find the CSC that I need?

Thanks


Follow-Up Postings:

 o
RE: Compressor Start Capacitor Question

First off if you go to any corner store you can get a "can" of beer and sit in front of your unit and pound it and your chances of fixing it will remain exactly the same as if you bought a "can" of capacitance and hooked it up. From now on I want you to quit pretending you know how to work on an air conditioner by asking irrelevant questions and go back to your sales cubicle where you obviously have too much time on your hands.


 o
RE: Compressor Start Capacitor Question

I found this capacitor on the Grainger site. It looks like it is a good replacement for what you need. It does not matter that is says "run capacitor". The application determines whether it is a run or start capacitor, not the device itself.

I am not a capacitor expert, but I think the 370V AC rating refers to the maximum allowed peak to peak voltage. If the nomial voltage is 240v AC RMS, then the peak voltage would be about 340v. There is a safety margin in case voltage rises about 240v. If is safe to go higher in voltage rating, but not lower.

Here is a link that might be useful: Run Capacitor, 60 MFD, 370 VAC, Round


 o
RE: Compressor Start Capacitor Question

I think that he is looking for the run cap for the compressor not a run capacitor. Does the unit have a start kit on it?


 o
RE: Compressor Start Capacitor Question

Mike

Thanks very much for the info - I think that is a good match.

I have had several components go out on this unit and everytime the HVAC company comes to fix it I have had long delays in waiting for parts. I just want spares so i don't have to wait for days (sometimes weeks) to get heat.

I have a spare fan, fan relay, fan capacitor. On my list is a magnetic starter switch for the compressor, the starter capacitor and then finally the main computer board itself.

Thanks for the help.


 o
RE: Compressor Start Capacitor Question

Theoretically, you need a capacitor in line for an AC motor to start and run. Usually the values for start and run are different, with start being the larger (and run can be very small). Sometimes the two capacitors are put into the same 'can'. In that case, there will be multiple terminals and two values listed, one larger than the other.

For capacitance values it is ok to be 'in the neighborhood', like 10% or there abouts. For voltage, it should never be less than the stated value on the original.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Heating & Air Conditioning Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Please review our Rules of Play before posting.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here