| I just moved into this house and the gas furnace does not always turn on when it should. I am not sure what model the furnace is but there is a Honeywell S8910U Universal Hot Surface Ignition Module manual next to the furnace. The furnace itself says Rheem on it, but I cannot find a model number. It has four wires going into it, R, W, G and C. R, W, and G are connected to the thermostat. I did have the C wire also connected, but the programmable thermostat manual said the C wire was optional so I disconnected it to see if that helped, but the problem remains. Here is the problem.
The thermostat is set at 70 and when the temp drops to 69 I hear a click coming from the furnace, and then a few seconds later the flame starts, then a minute later the fan starts, and then when the temperature hits 70 the furnace stops. When the furnace is not running the resistance between R and W is infinite. Then when the furnace starts the resistance between R and W drops to about 4 or 5 ohms. It remains there until the target temperature is reached and the furnace shuts off. My understanding is that this is normal. But once every 24 or 48 hours, when the temperature drops it will drop well below 69 and the furnace does not come on, and I do not hear a click. The resistance between R and W is 5 ohms at such times, meaning the thermostat is working and the furnace should be on. But it isn't. If I then flip the circuit breaker open then shut, or if I turn the furnace off at the wall and then back on, or if I move the thermostat from "heat" to "off" and then back to "heat", in all three of those cases the furnace has then started right up like it should. I had a repairman out to look at it and it was working fine when he was here, and he suggested to me that the problem was probably the batteries in the thermostat. Last month (before I moved in - I am renting from a person who just bought the house), this repairman had put in a new igniter for the new owner. The owner also removed the old thermostat but I do not know why. The current thermostat is a Filtrete 3M-22 that was still in the box when I got here so I hooked it up myself with help from there 1-800 line. It was easy to do. I don't know what the symptoms were that caused the owner to call the repairman in the first place or to replace the previous thermostat, and the owner is unreachable so I am trying to figure this out on my own for now. Any suggestions are welcome. Thanks |
Follow-Up Postings:
|
| "or if I move the thermostat from "heat" to "off" and then back to "heat", in all three of those cases the furnace has then started right up like it should." Check every connection for tightness, including the ones at the furnace (and the transformer in the furnace). Finding intermittent problems is always a PITA. You can also raise the thermostat setting to force the furnace on to see what happens. |
Please Note: Only registered members are able to post messages to this forum. If you are a member, please log in. If you aren't yet a member, join now!
Return to the Heating & Air Conditioning Forum
Instructions
- You must be a registered member and logged in to post messages on our forums.
- Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review the contents and make changes.
- After posting your message, you may need to refresh the forum page in order to see it.
- It is illegal to post copyrighted material without the owner's consent.
- HTML codes are allowed in the message field only.
- No advertising is allowed in any of the forums.
- If you would like to practice posting or uploading photos, please visit our Test forum.
- If you need assistance, please Contact Us and we will be happy to help.