visionpro iaq keeps defaulting to aux heat..

Posted by chrizg (My Page) on
Mon, Nov 16, 09 at 23:31

Hello all. I just got a new heat pump and furnace installed with a new VisionPRO IAQ controlling the system. Reason for heat pump is I am on propane.

The system is set to run the heat pump until it gets 25 outside. I have the temp drop to 67 after 11pm, and raise to 71 from 6-8am then drop to 67 until 5pm. Every time a new heating cycle starts the IAQ keeps defaulting to Aux Heat (propane furnace) and the temp outside is 40 deg +

I've had my installer back out and he adjusted some settings, but when I got home today, it was back on propane. He said he was going to contact honeywell but I am guessing its a bad IAQ. At first, I could turn the heat off and back on and the heat pump would turn on, but go back to propane on next heating cycle. It will run until the next sleep mode, then next morning on wake, back on Aux heat.

Does anyone have any suggestions? The settings are set that Heat pump is primary, Furnace is Aux. Aux heat runs at 25 or below. The 2deg drop in room temp to run only aux heat is disabled. Setting to run heat pump for a certian amount of time and if it doesn't reach desired temp is disabled.

This is very frustrating as I would like to save on propane after spending as much as I did on the install...


Follow-Up Postings:

 o
RE: visionpro iaq keeps defaulting to aux heat..

So the temp was 71, I raised temp to 73, the heat pump turned on and raised house to 73. 10 minutes later the furnace kicks on?!? Argh!!


 o
RE: visionpro iaq keeps defaulting to aux heat..

It sounds like you already checked, but register 0530 for "Adaptive Intelligent Recovery" should be set to 1. That's from looking at the manual for an 8000 series stat.

It may also be that the stat is still learning how to recover from setback. I think it takes a few days.


 o
RE: visionpro iaq keeps defaulting to aux heat..

hmm, sounds like the 2 degree droop is doing something.
I would make sure that there is no cold air coming from the back of the thermostat where the wires come in.

set your IAQ with these parameters and see what happens
172 system type = 2
200 backup heat (aux) = 1
210 fuel kit option = 0
342 Outdoor Temp sensor = 1 (must have sensor)
345 dual fuel hp control = 2 for a 2F droop with aux lockout
350 balance pnt lockout = 25 (must have out door temp sensor)
360 Aux heat lockout you can set this at 50 or 40 so the propane won't come on before it reaches these temps.

this will create the 2 degree droop for the heatpump and furnace between 50/40F and 25F.


 o
RE: visionpro iaq keeps defaulting to aux heat..

Better look at the 360 setting. Since you are wanting to warm up 4° at the coldest part of the morning, the IAQ likely is calling for backup. If you don't want the gas on, set 360 very low. You can even set it to 25° so you never have backup. You likely also won't warm the house back up in 25° weather either. There's also a setting that if the pump runs X number of minutes and hasn't caught up it goes to gas. That could be doing it too. Lowering 360 should stop that too.

If 345 says no backup, then you got me stumped. Never seen any problems with the logic in these.


 
 

 

 