new heat pumps for cold temperatures
| | |
Posted by greengirl_va (My Page) on Sat, Nov 3, 07 at 15:31
I'm still in research mode with regard to heating and air. The thing I have newly discovered and wish to have anyone comment on are the All Climate or low temperature heat pumps. The two that I see are the Hallowell and the Nyle. Each seems to be manufactured in a different part of the north country and purports to be the perfect answer to efficient heat pump operation at lower than ususal temperatures- ie below 30 degress, in fact even down to
15-0. Supposedly the Hallowell is currently being sold but there is some hold up on the Nyle. Does anyone have any knowledge about either one. They seem like THE next thing and would certainly solve the secondary heat source for lower temp days. |
Follow-Up Postings:
RE: new heat pumps for cold temperatures
| | |
| Bon Air makes one also down to 25 below 0 http://cgi.ebay.com/DUCTLESS-MINI-SPLIT-AIR-CONDITIONER-HEAT-18000-btu-NEW_W0QQitemZ160175816361QQihZ006QQcategoryZ20711QQcmdZViewItem |
RE: new heat pumps for cold temperatures
| | |
| Re: larrylwill ‘Bon Air makes one also down to 25 below 0’ Really? I doubt it. The only heat pump that works effectively at that temperature is a geothermal HP. IMO SR |
RE: new heat pumps for cold temperatures
| | |
| That is exactly what the Hallowell is supposed to do as an air heat pump. It is newer technology and seems sound from testamonials on their web site. Check out uswesco.com, which is the west coast distributor. I plan to contact them tomorrow and find out if it i available on the east coast. I am indeed intrigued! This is a logical progression along the lines of standard stuff, just like the world is pursuing thnings further down the evolutionary line in cars and every other fuel saving avenue. I'll let everyone know what I find out, but would still like any feeback from anyone who has learned about it (them) already. |
RE: new heat pumps for cold temperatures
| | |
| Re: greengirl I looked at the uswesco.com web site. Personally, I think it’s all smoke & mirrors, if it sounds too good to be true – it is! First of all, like most of the air-source heat pump industry, there is nowhere near the full disclosure of specifications you’ll find in most of the ground source heat pump industry. Second, just take a close look at the specs provided on this page of their web site: http://uswesco.com/files/ACHP/Hallowell/pdf/FahrenheitBTUCOP.pdf For example, look at model 42C/46H ºF ACHP Heating Performance. If you examine this chart carefully, you will see that the ‘back-up’, 4.8kW heater, comes on at +30ºF! Not very good at all – especially if your electrical rate is high and this is in addition to the HP running flat out (Primary & Booster) as well! That’s how they claim their units run down to -30º - accurate but misleading. Their best HP is probably no better (hard to tell as they don’t disclose specs fully) than any run of the mill air-source HP designed for the Canadian winter (back-up kicks in at 10ºF to 14ºF). Here in Canada, once this temp. is reached, the HP is switched off completely as it is inefficient to continue running it. If you’re really looking for high efficiency look to geothermal – and yes, it’s going to cost a lot more. Nothing’s free (except the renewable energy you will then be able to extract from the ground). Just for example, take a look at WaterFurnace Envision, with a COP of 5 (30 EER). For every 1kW of electricity you pay for you’ll get 5kW of heat (17,065Btu/h), 4 of which will be free (13,652Btu/h) courtesy of the sun. Also compare the disclosure of specifications between WaterFurnace and Hallowell. You will notice that Hallowell is more like Halloween, where everything is behind a mask. Caveat Emptor SR |
Here is a link that might be useful: WaterFurnace
RE: new heat pumps for cold temperatures
| | |
| Steve: Thanks for finally being upfront about the cost of geothermal and I mean that sincerely. The sticker price should always be in plain site because very few people are able to afford geothermal. I don’t know about the Hallowell system but as a skeptic myself; I will be looking closely into it. This topic does reconfirm my post from a month back however, that technology will continue to improve. With fuel prices rising, it’s a guarantee that someone is working hard and trying to strike it rich by coming up with the next super advanced EHP. It may not be this year or next but there are some super efficient systems in the works. I have been reading about a Japanese company that’s expecting to release a new system in early 2009. I have been having many conversations lately about geothermal with some HVAC consultants and building science guys. I have some questions for you that maybe you can clarify. 1.) There is not a single published "measured energy use" on geothermal that I or anyone I know can find, NOT ONE. There are plenty of statements being made by manufactures but nothing is published. If there is one out there, we are very curious to see it. If you know of one, can you post it please? 2.) The WaterFurnace Envision, with a COP of 5 (30 EER) sounds very impressive but that COP does not calculate the electricity required for the circulation pump. If it does, can you please show me where this is figured into their analysis? A standard EHP does not use a circulation pump. These circulation pumps require a fair amount of electricity to push the liquid through thousands of feet of high resistance piping. Our findings are once you figure in the electric usage of the circulation pump, it lowers the COP to a 4 or 3.5 with is now in the range of a traditional Electric Heat Pump. 3.) A question has come up from a homeowner with geothermal living in the far north east. For the last three years, they are seeing their utility bills rising during the winter months. After calculating in rate increases, it looks like over the last three winters, they are using 10% more electricity to heat their home with geothermal. Apparently this homeowner uses the system to heat but very little if any for cooling. This unbalanced usage is lowering the loop field temperatures and making the system less efficient. Have you ever heard of this issue? Just another FYI, I found a homeowner at my church who recently converted from a natural gas/AC system to a new geothermal, closed loop system. They are now saving 25% in their utility bills over the last 11 months and they are very pleased with their geothermal decision. Unfortunately, their old system was installed almost 30 years ago. I didn’t have the heart to tell them that they would be saving close to that on their utility bills anyway if they used today’s high efficiency equipment. The only difference is they spent mucho dinero for the geothermal. Thanks, P.S. Stop stealing my "Caveat Emptor" statement! |
RE: new heat pumps for cold temperatures
| | |
| "Bon Air makes one also down to 25 below 0" - NFW. I can type the meaning of those 3 letters if you need me to. 25 below zero? Don't be fooled by something you read. |
RE: new heat pumps for cold temps
| | |
| GreenGirl: Are you looking to put this heat pump in Virginia? Is your house all-electric? What are your electric rates ($ per kw-hour)? |
RE: new heat pumps for cold temperatures
| | |
| I am in VA and our electricity at this time is an average of 6.36 cents, with it being 5.92 in winter. I am doing more research on the Hallowell and am quite far from dismissing it. I will let everyone know whether Steve is right or not. Check out the manyfacturer's web site at gotohallowell.com. And for the record there is so back up heat source per se so that statement is incorrect. Supposedly part of the beauty of it. There is no new technology involved at all, just different and more extensive configurations of that which is in other units. Sometimes too good to be true is just the new curve... Thanks to all who are interacting! Let's all keep up the dialogue and not get perturbed at disagreement because we all may benefit from a new discovery. |
RE: new heat pumps for cold temperatures
| | |
| If GreenGirl is in the Northern Virginia area, electrical costs work out to be about 10 cents a kilowatt hour after you figure in taxes and other associated charges. Not great, but not terrible. I have a Trane XL1200. After some initial problems with the unit it's been very good for me. I have an all electric house. I keep the temperature fairly low (66 to 68) in the winter and spot heat with ceramic heaters if I need to. In the 14 years I've been in the house I've never had an electric bill in the winter over $130, and most are well below that. The newer air exchange heat pumps are much more efficient in border areas like Virginia. To be 100% honest I'd rather have baseboard hot water, but I don't. |
RE: new heat pumps for cold temperatures
| | |
| "I am in VA and our electricity at this time is an average of 6.36 cents, with it being 5.92 in winter." - Those are probably generating costs only and do not include transmission and distribution. I pay about 13 cents/kw-hour total delivery cost in Baltimore. Our electricity went up 65% thanks to de-regulation and no competition. I have looked into the Hallowell unit. There big advancement is the booster compressor and subcooling economizer. They still use a 5 kw electric heat strip in conjunction with the 2 stage heat pump compressor and additional booster compressor at 10 degrees outside air temp. An EER of 12.3, SEER of 14, and HSPF of 9.6 for the 36C35H is not much better than my new 3 ton Goodman GSH14 heat pump (12 EER, 14 SEER, 9 HSPF). With your fairly decent electric rates coupled with your Virginia climate, I'm not sure why you are looking at this Arctic system. What is the price tag on this system? |
RE: new heat pumps for cold temperatures
| | |
I have now spoken with Hallowell, and the additional heta strip is in place but is not engaged until the outside temperature is down to 20 belwo or so. We never have that so in essence it will never kick in. As i have ead more on my own and now spoken to the company, I am even more interested. Our electricity really is not as expensive as gargyg's, even after figuring all other costs, so this would be extremely economical to operate. They are suplying many units to all sors of commerical and residential applications but have just started the residential marketing in ernest. It is an idea whose time has come witht he way energy costs are going , and when you factor in the whole carbon footprint thing, it is even more advantageous. I will be getting a quote once we have established a connection between them and someone where I live. So evryone check out www.gotohallowell.com. It is NOT Halloween! |
RE: new heat pumps for cold temperatures
| | |
| After doing some digging on Hallowell International I have to be honest and say that I am very skeptical and I’m being kind. This company started two years ago and only has 25 employees. They are manufacturing out of an inexpensive metal building facility and it’s definitely not state of the art. For a company to claim the title "International" and then you see their operation, well let’s just say then name alone is misleading. For a startup company in this industry where your competition has billions of dollars, not thousands of dollars, it would be a fair bet to say they are highly undercapitalized. If they don’t have the money to grow much faster in this industry, the odds are they are going to fail. As a homeowner, I won’t take a chance on a new company not being around in a few years. As a homeowner, I won’t take a chance on a new company whose equipment might not work as promised and also might now be around in a few years. They are growing but if Hallowell International truly had the equipment that delivered what is being said about it such as, "Acadia outperforms conventional heating systems by 200 percent, and has already lowered home energy bills by up to 70 percent -- even when outside temperatures reach well below zero." If these statements are true, every major manufacturer around the world would be on their doorsteps in a bidding war for that patent. If this patent were that good, a very small company such as Hallowell International probably couldn’t refuse the offers they would be getting. I could be wrong but even if the equipment does perform as stated, you’re taking a big chance on the company. |
RE: new heat pumps for cold temperatures
| | |
| "I have now spoken with Hallowell, and the additional heta strip is in place but is not engaged until the outside temperature is down to 20 belwo or so." - You need to read the tech info on their website. It is energized at +10 on a call for second stage heating. "Our electricity really is not as expensive as gargyg's, even after figuring all other costs, so this would be extremely economical to operate." - So why are you going to pay 2x the cost when a regular air source heat pump will work with your low electric prices and moderate climate. You don't live in Alaska or Canada. This is overkill for Virginia (why do I feel like I'm talking to my wife and she isn't listeming). PS. Tell Al Gore I said hello. |
RE: new heat pumps for cold temperatures
| | |
| "seems sound from testamonials " NEVER rely on this. Real equipment is tested and certified by labs, not Joe Blow saying "It worked real good". ""I am in VA and our electricity at this time is an average of 6.36 cents, with it being 5.92 in winter." - Those are probably generating costs only and do not include transmission and distribution. I pay about 13 cents/kw-hour total delivery cost in Baltimore. Our electricity went up 65% thanks to de-regulation and no competition." No, Virgina electricity is still very reasonably priced. Dominion Virginia Power still owns generating and distribution assets. The Peoples Democratic Republic of Maryland legislature screwed up the electric regulation big time. You get what you voted for. |
RE: new heat pumps for cold temperatures
| | |
| Re: mepop While it was never my intention to conceal the cost of GSHPs, I agree that it should be clear at the outset. However, there really is no concealing the cost. It’s going to come up and pretty fast. The cost factor of geothermal is ALWAYS the 600-pound gorilla in the room; no matter how you tap dance around it – it’s still there! The biggest improvements to performance have been 2 stage scroll compressors and ECM variable speed blower motors. I too am a skeptic. I believe progress will be made incrementally, not with dramatic breakthroughs. There’s no free lunch. Even GSHPs with higher (5) COPs there is a cost involved and that cost is a larger earth loop. More drilling, more pipe, more antifreeze, more pumping power. Does it work? Yes. Is the claim legitimate? Yes. Is it worth it? Yes. But it’s not free! The incremental cost increase will be recovered through reduced operating and maintenance costs. Geothermal will really pay off in areas that have serious heating or cooling load requirements, preferably both. Extreme temperatures +large building envelopes = faster payback. 1.) Regarding published energy use. It is published in the technical manuals of virtually every GSHP manufacturer as a downloadable pdf. The WaterFurnace link in my above post is but one such example. You will need some knowledge and experience to fully extract and interpret the data – but it’s all there. It HAS to be; otherwise we CANNOT design systems (with any predictability)! Download and expand the WaterFurnace pdf. Look at pages 37 & 38. This is a 2-speed nominal 3-1/2 ton HP. The specs are all there, but don’t neglect the info on pages 19 & 20 – very important! Back to your question again, published energy use. Where does all this published data leave you? Well guess what -you’re STILL back at the starting gate. Why? Because unlike an air-source HP that you slap on the foundation wall and drill only about 8 inches or so, with geothermal, you have to take this information and then CUSTOM design a ground loop! How many feet (hundreds!) of borehole, open loop or closed-loop, how many feet of HDPE pipe, what diameter, parallel or series connection, what kind of antifreeze, what concentration of antifreeze, what viscosity is this antifreeze, how many feet of head, how many circulating pumps, whose pumps, series or parallel connected pumps, what header design (parallel installation only), how many GPM, what kind of joints (butt or socket fusion), total resistance of all joints (different for each size & type), and on and on and on! These are but a FEW of the factors that go into designing a GSHP system. Who ever you hire had better understand it all if the ‘as built’ system is to look (operate) anything like the ‘as designed’ system. It HAS to be done right the first time out. Mistakes can be costly to correct – especially if they’re at the bottom of a 600ft. borehole! That’s why a good designer is worth their weight in gold. The bottom line to your question is that each and every GSHP installation should have its own ‘as built’ book listing FULL specs for that specific installation. Why? Because it’s every system owners’ RIGHT to own such a document, it’s ethically required of the installer, because every system is different and custom designed - even if the same HP is used, and most importantly so that there is a base line to go back to if something/anything goes wrong. I would also like to add, with some sense of pride, that Canada now has the highest standard in the world to have a residential GSHP installation certified. It’s enough to make most (every) installers want to hang themselves, but is very good for the consumer. 2.) "The WaterFurnace Envision, with a COP of 5 (30 EER) sounds very impressive but that COP does not calculate the electricity required for the circulation pump." The 5-COP does include the power consumption of the circulating pump, as this configuration is a closed loop system. A closed loop system is a balanced system much like an elevator with compensating counter balance weights. Extreme heavy lifting is only done residentially in open loop systems, particularly those with deep wells. A 3 ton system, as in the above mentioned example will only require 1 circulating pump rated at a nominal 1/6 hp. Furthermore, this pump is located in the mechanical room next to the GSHP so any heat generated by the circulating pump is a net gain in the heating mode. It only really becomes a net minus in the A/C mode. The reference you are seeking regarding this matter of pumping power is in the above-mentioned pdf section 1, page 8, titled ‘Performance Standard ARI/ISO/ASHRAE 13256-1’. N.B. ‘Pump Power Correction Calculation’ & ‘ISO Capacity and Efficiency Calculations’. 3.) Regarding this residential homeowner’s system, there is obviously a problem. I have heard of these problems but it is difficult to comment without knowing all the facts. One thing is certain; it is not because of ‘unbalanced usage lowering the loop field temperatures’. Not likely in a residential application anyway. Nothing can be more unbalanced than the heating and cooling loads of large commercial buildings and those with properly designed geothermal systems work just fine. The problem is more likely due to an insufficiently sized ground loop, or flow rate. It’s really much more complicated than that but we don’t have all the facts. Is it a pond loop? Is it a vertical or horizontal loop? How many feet of borehole if it’s vertical? How many feet of trench if it’s horizontal? How many pipes per trench if it’s horizontal, buried at what depth? And on and on and on etc. The bottom line is the installer didn’t do his homework. More than likely, it’s a flow rate problem. Someone who knows what they’re doing has to measure flow rate in GPM and feet of head as well as EWT (entering water temperature) & LWT (leaving water temperature), then reference this to the manufacturer’s specifications for that HP as in our pdf mentioned above. This is precisely why an ‘as built book’ is vitally important. It’s the road map of what was done, how it was done and a baseline of performance so that any competent tech can walk in there and be able to say ‘ah ha, this is what’s wrong’. I’ve heard of cases where they’ve had to pump out all the loop fluid into barrels with compressed air and measure the volume of fluid just to approximate how many feet of pipe they had down hole because nobody really knew. Talk about a nightmare! As for your neighbors at church who converted from natural gas to geothermal? Well praise the Lord; they’ve seen the light! In terms of CO2 emissions, it’s about the equivalent of getting 3 cars off the road. You should thank them. Amen! Steve |
Here is a link that might be useful: WaterFurnace
Re: Hallowell Heat Pumps
| | |
| Re: greengirl I think you should reread all of garyg’s posts. I give them a 2 thumbs up. Except for saying ‘hello’ to Al Gore – he’s a Warm Monger! SR |
RE: new heat pumps for cold temperatures
| | |
"The Peoples Democratic Republic of Maryland legislature screwed up the electric regulation big time. You get what you voted for." - And now the newly elected Maryland Governer is trying to raise taxes big time to balance the State budget. He was against slots as mayor but now realizes the need for the slots revenue as Governer. I smell a recession: high energy prices, high gas prices, high taxes, large personal credit card debt, shrinking dollar, high national debt, etc. |
RE: new heat pumps for cold temperatures
| | |
You guys do get a bit consecending at times, but it is being ignored, not being missed. The units are as the website says, no new technology at all, just a new configuration and application of well respected and available parts, making it installable and servicible by any qualified hvac person. The patents are for the application, not the parts. Cost is more than a standard heat pump by the 20-30 percent that they stated (NOT 2 times) but cannot be determined until an installer would do an estimate, just as in any regular installation. The material warranties are for 5 years, with an aditinal 5 years available for $300 dollars or so. They are just now (few months) beginning their residential advertising, having been doing commercial and government housing applications mostly. They are more widely sold in hte west at this time but are spreading as people see the worth in the application. Apparently the government thinks highly of the units! Maybe there are big companies on the doorstep to try to buy them out, ever think of that? Maybe they are not interested because they do have the next best thing.Right now I am exploring, but if everyhting tht was new got dismissed outright then the world would be turnign pretty slowly by now! On to acquisiton---If there are no dealers in an area, a potential customer is asked to supply several companies that they respect and Haliowell will make contact and set up someone to be the dealer in this case. I will be continuing down the line to see what the actual costs would be. Whether we do it now or not. While it might be overkill for my climate, no energy source will be getting cheaper and if saves more than a standard heat pumpo year after year, then any higher price will pay for itself. To know that you were using so little electricity to do all your heating and cooiling would be great. Not everyoe can or would do geothermal, ever. I imagine that while this is a new product, all products that are highly respected now started out as new products that developed that respect. Do keep up the dialogue but leave out the petty references. |
RE: new heat pumps for cold temperatures
| | |
| "You guys do get a bit consecending at times, but it is being ignored, not being missed." "Do keep up the dialogue but leave out the petty references." Hmmm. I detect arrogance. |
RE: new heat pumps for cold temperatures
| | |
| I've got no dog in this fight, other than the fact that I live in Virginia, too. I have to second, third, whatever, many of the comments that have been made here about being very skeptical about the kind of claims that Hallowell is making about its equipment, and to NEVER EVER base your decision on testimonials. That said, there are a couple of reasons why I'm skeptical. 1. The concept that this is just a new configuration of old parts. While that can certainly gain advances, such efforts are usually measured in single digit percentage points. What Hallowell is claiming is, in some ways, taking a 30 MPG car, reconfiguring what is already there, and coming up with a 120 MPG car. In both cases there's a certain amount of physics that are involve that simply can't be ignored, and as often as not it's physics that are the limiting factors. In a car, it's physics that about 97% of the energy created by burning gasoline or other fuel is expended as waste heat energy. In the case of a heat pump, it's the fact that the air, at any given temperature, retains only so much available latent heat. In the case of some vehicle designs the waste heat is harnessed to do other kinds of work, and that brings about greater efficiencies. In heat pumps, reconfiguring the design of the coils and the speed at which the fans operate allows recoving more of the latent heat in the air. But, at some point, you run out of heat. And when the temperature drops into negative digits, there's really not enough latent heat in the air to be captured by anything other than a monumental shift in technology, not a simple redesign of the existing system. 2. I agree with the above poster who has said that if someone actually did come up with such a design, first I'd bet on one of the major R&D programs being run by one of the biggies -- Trane, Carrier, Lennox, etc. -- who are capitalized out the wazoo. Granted, that's not a given. Small timers have made MONUMENTAL discoveries that big research labs have missed, but almost always those leaps are in totally new directions, not in tweaking existing stuff. 3. I also agree that it's kind of odd that someone who developed such a leap in design didn't offer his expertise/patents to one of the major players. Again, though, not a given, others have done that -- the people who founded Gore-Tex fibers (family members) are a perfect example of that. OK, those are just a few of the major reasons why I'm dubious about the claims made by Hallowell and their product. Unfortunately, there are a lot of companies out there right now who make similar claims about leaps in technology offering big savings. Two of the most prominent are HydroSil and EdenPure. Those products LOOK good, and the companies seem to have a lot of backing in the terms of facts and figures and chart and graphs and data strings, etc., but once you start digging, you realize that their "tests" are absolute BEST case, most favorable conditions, their numbers just don't quite add up, and in reality, what they are claiming, comes very close to breaking the laws of thermodynamics. The problem is, while it may seem as if we're pissing on your parade and going out of our way to be condescending, it's the fact that a lot of us have seen stuff like this before, and about 99 times out of 100, it's not what it's claimed to be. By all means, keep investigating, and keep letting us know what you find out. |
RE: new heat pumps for cold temperatures
| | |
| Quote "In a car, it's physics that about 97% of the energy created by burning gasoline or other fuel is expended as waste heat energy." Rubbish. It's closer to 60% - if only 3% of the energy in the fuel was available for moving the car then the internal combustion engine would not be a feasible means of transport. Quote: "And when the temperature drops into negative digits, there's really not enough latent heat in the air to be captured by anything other than a monumental shift in technology, not a simple redesign of the existing system". To be pedantic, latent heat is the energy in the water vapour in the air that's recovered when it condenses. As for available energy in the air, there's lots left when the temperature is in the negative digits. We're nowhere close to the theoretic maximum efficiency of a heatpump (dictated by the Carnot cycle) which is somewhere around a COP of 7 for the temperatures we're talking about here. So there's plenty of scope for bring about much greater efficiencies for heatpumps that are optimized for heating. Previously heatpumps were more usual in a climate that requires efficient cooling and so different trade-offs were made. Just to prove it can be done, there are ground source heatpumps that are used in the arctic to extract heat from the frozen tundra - so it can certainly be done. Paul in Montreal. |
RE: new heat pumps for cold temperatures
| | |
| Yes, you're right, my figure for the energy heat loss in an internal combustion engine was off. The salient point remains, however, that it's very unlikely that massive increases in efficiency are attainable by simply reconfiguring the design. As for latent heat, it's actually the heat involved in a change of state such as when water goes to ice (or vice versa). I used the term imprecisely simply to give name to the heat energy available for capture in an air exchange heat pump. As for extracting usable heat from frozen tundra, I don't doubt it for a moment. Remember, frozen tundra is still FAR warmer than than the air above ground in arctic conditions, so I don't think that's a good example at all. We're not talking about ground source heat pumps, though. We're talking about air exchange heat pumps, which have to work in a FAR wider range of exchange temperatures. Remember, dig down a few feet just about anywhere on earth and the temperature is pretty much constant. Once again, though, I remain dubious that simply reconfiguring some existing parts can bring about the kind of jumps in efficiency that the company is claiming. And if it were possible, I find it even harder to believe that one of the major manufacturers wouldn't have been doing so already in an effort to gain serious traction into markets that are traditionally closed to air exchange heat pumps -- New England, the Dakotas, Minnesota, etc. Once again, though, I'm not totally discounting this company's claims. I'm just skeptical. |
RE: new heat pumps for cold temperatures
| | |
| New England, due to high electricity rates, has not been a traditional market for heatpumps (nor air conditioners for that matter). Most heatpump manufacturers are primarily in the AC business where there is a much larger market. This is partly why GSHPs are more popular in heating climates than cooling (even though they're efficient in both) since the heating output is relatively constant. The biggest challenge with ASHPs is that the output capacity drops with decrease in temperature so that if you size it for heating, it becomes way oversized for cooling. If an ASHP was sized just for heating, then it can be designed to have a reasonably large COP even at very low air temperatures (of course, choice of refrigerant makes difference too). There are companies in Northern Europe that make heating-only ASHPs so it can certainly be done. But to make a system work well for heating in very cold conditions and also work well for cooling in warm and humid conditions is a challenge - though "multi-speed" compressors help here. Of course, the Asians are far ahead of North America with their DC (or inverter driven) compressors that give continously variable capacity. There are still large gains in efficiency possible from the 3-4 COP at the moment to around 6-7 (or even higher for GSHPs - > 10 should be possible). Paul in Montreal |
RE: new heat pumps for cold temperatures
| | |
| Back to the Hallowell HP. Perhaps their high COP at low temps comes from the fact that they’re combining the COPs of the heat strips, back-up, aux, ?-stage or whatever you want to call it with the HP which is STILL running – even when the rest of the world agrees that it shouldn’t. That heat strip will always have a COP of 1, so combining it with an inefficient HP will still raise the COP of the HP making it look better than it really is. It gets worse than that. If those IDIOTS are still running that HP to death at 0ºF, -18ºC and below, what about the wear and tear of all the mode reversals and defrost cycles? If you’re still hell-bent on buying this Frankenstein, may I suggest having it installed by a company that is likely to be around for a while, perhaps even after Halloween goes bust and DEFINITLY purchasing the longest extended warranty offered. One other thing. If the temp ever dips to anything near 0ºF, -18ºC, that ‘4.8kW’ ain’t anywhere NEAR enough! I haven’t seen anywhere in their literature any mention of ARI/ISO/ASHRAE/ACCA/CSA – doesn’t that tell you that this is a junk science, Cold Fusion HP? Just a thought. Caveat Emptor SR |
RE: new heat pumps for cold temperatures redux
| | |
| SR, you normally post good info. There's no way they'd include a COP=1 of the heatstrips. A regular ASHP will still have a COP>1 down to -18C. Once the temperature gets way below freezing, there's less need for defrost cycles as the air is dry at that point - most defrosting is required somewhat above freezing as the air still has a lot of moisture in it. As for wear and tear, there's no difference between -18C and 0C as far as the reversing valve is concerned so long as it's properly lubricated and within tolerance. It's not difficult to make mechanicals work well down to -40C and below - if it was, much of life in Canada would be next to impossible. As for the output capacity, yes, that is the issue at very low temperatures - hence my comment about sizing for heating-only. This is the biggest challenge with a conventional "single-speed" heatpump. But with inverter driven DC compressors that are continuously variable in capacity, it's not difficult to overcome. The Asians have been doing it for years with their mini-splits. What they're doing is certainly not junk science - it's not that different from what the low-temperature GSHP guys are doing (such as Ice Kube Systems) - so long as there's a phase change in the refrigerant, heat can be extracted down to any arbitrarily low temperature. No rocket science required. Sheesh. Paul. |
RE: new heat pumps for cold temperatures
| | |
| Will everyone please go to both the Hallowell web site and the uswesco web site and read ALL of the links. The whole system is explained in detail in the various papers and articles. Do Goggle it as well and read the pages of comments, studies and papers from various energy conservation bodies. I am not a hvac technician but the whole thing that is patented is outlined in detail, down to the white apper detailing the technical spec for boosted air souce heat pumps. It doesn't appear to be Frankenstein science at all and is in use many places The fact that Shaw licensed the technology out to Nyle and then tookk it back when it wasn't being used the best and has joined ith Hallowell to market it is confimation of faith in the product. We are all supposed to be seeking new positive things,especially in light of enegy costs. I asked for feedback from people who had one or had worked with one, not anyone who wanted to dis the thing without first hand knowledge. The arrogance someone alluded to was most certainly not coming from me, but I was most cetainly not happy about some of the references in some of the answers. Lets all learn whatever the truth is, once we discover what it really is. Wouldn't it be great if by being wrong you could be better? Higher initial outlay for this might not be so bad if one is paying even higher prices for fossil fuels. Thanks to ALL. |
RE: new heat pumps for cold temperatures
| | |
| greengirl: I’m not being a smart ass but if every website delivered what they promised; everyone would be slim, live to a 100, have a full head of hair, be wrinkle free, happy as a clam and wealthy as Bill Gates. Many who have strong beliefs in saving the planet are similar to those with religious beliefs. There is no conclusive proof for either but if you have faith and it makes you feel better, go for it. I hope Hallowell does have a better mouse trap so please let us know how your investment goes? If their claims of energy savings are true, we will be seeing it in every technical journal, newspaper, magazine, evening news and Michael Moore movie well before you get your results. Good luck and I hope it works. |
RE: new heat pumps for cold temperatures
| | |
| The whitepaper that's on the Hallowell site at least explains how the mousetrap works. It's all pretty basic refrigeration mechanics really and is certainly not rocket science. The largest market for heatpumps in the US is dominated by the cooling climatic zones which don't need below-freezing performance so it's no wonder that not many companies have attempted to address this market. It's no surprise, to me, that Hallowell are located in Maine - a state that, by rights, should be part of Canada ;) Any initiative that attempts to get closer to the theoretical maximum efficiency dictated by the Carnot laws is to be applauded. And in case anyone is confused by the term "theoretical" I mean a hypothesis that has been proved correct and can now be used as a predictor (hence Carnot Law). Paul in Montreal p.s. I have no affiliation with Hallowell but am interested in technology that reduces the requirement for fossil fuel usage |
Here is a link that might be useful: All Climate Heat Pump technical whitepaper
RE: new heat pumps for cold temperatures
| | |
Paul: Even Ice Kube, which is most likely the heat pump operating in the frozen tundra that you eluded to in a previous post, has a low temperature limit of -10ºF. I have doubts as to Hallowell’s claim of a COP of almost 2 at -30ºF. I’m not sure how they’re rating the COP of their units, they don’t specify, but 1.95 COP at -30ºF? That makes me wonder; perhaps you can enlighten me? I agree that Hallowell is not that different from Ice Kube (which represents the other (high) end of spectrum of heat pump technology, and in many ways is virtually in a class of it’s own) in that there is a phase change in the refrigerant. Keep in mind that Ice Kube, as all geothermal HPs, operate within the envelope they are heating (or cooling). There’s a big difference between equipment operating in an environment of about 68ºF and equipment operating at 0ºF and below as Hallowell claims theirs does; that can be a difference of about 100ºF. Machinery operating in temperature extremes will likely require more maintenance than equipment operating at relatively stable room temperatures. As for life here in Canada, when does CAA get most of their calls for cars that won’t start? Steve |
RE: new heat pumps for cold temperatures
| | |
| The car analogy is not a fair one as the reason cars won't start is because lead-acid batteries lose most of their effectiveness below about -10C. Mineral oil also greatly increases in viscosity below a certain temperature (hence 5W40 oil is preferred in winter). As for a heatpump operating at cold temperatures, so long as there is sufficient lubrication in the compressor (and I'm sure the PEG type synthetic lubricants used can be designed to have the required viscosity at such a low temperature) there shouldn't be a problem. The only question I have at those low temperatures if how the defrost operation works. Perhaps it's not required below a certain temperature due to the dryness of the air. In which case, the reversing valve doesn't have to operate so there is no extra wear and tear. There's plenty of equipment that works happily at extremes of temperature - it's not difficult to design - it's more in the specification of the correct lubricants. Machines can't "feel" the cold anyway. As for a COP of 2 at -30F, this is still way less than the Carnot limit of around 5.4. If you read their literature, they did use ARI test procedures to rate their units. By the way, all refrigeration systems work with a phase change in the refrigerant - the boiling point of R410a is -52C so there's no problem at -30F (-34.4C). As their whitepaper points out, it's the mass-flow of the refrigerant that's an issue a low temperature and it appears that their secondary "booster" compressor addresses that issue. There's certainly no difficulty in running a refrigeration circuit at that temperature with conventional refrigerants. Paul. |
RE: new heat pumps for cold temperatures
| | |
The problem with having any portion of the system fall below 32 F is that frost forms and the coil starts to ice up. A system can be designed to operate and just about any temperature if you can avoid icing on the coil. It will take power to run a defrost cycle to clear the ice, hammering the efficiency of the equipment. Evaporators at very cold temperatures are used in high vacuum systems to remove residual gases. Look up 'cryopumps'. The gases freeze onto the evaporator. Large systems that must run for long periods provide a way to isolate the condensing surface from the system, then boil off the trapped gas. A second pump is operated while the first is out of the system. This is not a very practical option for a heat pump sitting in ambient outside air though. |
RE: new heat pumps for cold temperatures
| | |
| The tech info on the 36C35H Hallowell has some inpressive heating numbers: 17 F outside air: 2.45 COP, 111 indoor air temp 10 F outside air: 2.35 COP, 108 indoor air temp 0 F outside air: 2.21 COP, 102 indoor air temp -15F outside air: 2.06 COP, 99 indoor air temp. The above temps are without the 5 kw heat strip which adds another 15 degrees according to their literature. I have a phone call into Hallowell for pricing. |
RE: new heat pumps for cold temperatures
| | |
| I think it is excellent to see his discussion going on. I am a converted skeptic. I originally followed Hallowell and then did some research. Talked to some clients with Hallowell. Visited Hallowell and now we are the Canadian Distributor. The technology scares the crap out of most Geo Thermal guys but the ones that grasp it actually start promoting Hallowell in areas where they cannot put a loop or the price is too high. Leeds for Homes are all over the Hallowell in Canada. It is real easy to sit here and knock the COP of 5 that is being stated for Geo Thermal, but why bother. We have Hallowell's installed in Newfoundland, New Brunswick and Ontario so far. First units are going into Quebec, Manitoba and BC now. We are having a great time. Check it out, you will be pleasantly surprised. You will see Canadian utilities offering rebates next year. Jim |
RE: new heat pumps for cold temperatures
| | |
| Re: jchaters "The technology scares the crap out of most Geo Thermal guys…" Dream on! SR |
RE: new heat pumps for cold temperatures
| | |
| I am not in the trade. But I do have some college credits in physics, as well as some other courses. From long ago, of course. If the Hallowell does so well from the air, the same technology would do even better with the higher temperature of ground-source water, or an equivalent. That part of physics has not changed. Latent heat has already been mentioned. I do hope the Hallowell proves to be all that it claims. We need all the help we can get, energy-wise. |
RE: new heat pumps for cold temperatures
| | |
| I called Hallowell the other day and spoke to a Rep. He couldn't give a firm price for Maryland but estimates $13,000 for a 3-ton drop-in system (no major ductwork or major labor). They are coming out with new models for 2008 that meet the criteria for the US Federal Tax Credit for air source heat pumps of 15 SEER, 13 EER, and 9 HSPF. Currently, the 3 ton unit is 14 SEER, 12.3 EER, and 9.6 HSPF. I thought the 5-year parts warranty on the Hallowell was a little weak. I can see this for Canada or for a climate where there are long bitter winters. This technology, along with Nordyne's variable speed IQ drives, should be the next leap in technology. Until then, I'll stick with my new Goodman heat pump. I could buy and install 3 of my current heat pumps for the price of a Hallowell. |
RE: new heat pumps for cold temperatures
| | |
| So let’s see if I have this right, $13,000.00 (estimated price for a ‘drop-in’!) – 3 times the price of a standard air-source HP, for 12.3 EER vs. (let’s just say) a WaterFurnace GSHP with a 30 EER that can also heat DHW. Canadian Federal grant for air-source HP = $400.00 vs. $3500.00 for GSHP (possible max. total of grants in Quebec for GSHP = $6800.00). Personally, and I’ve been there before, once I’m anywhere NEAR $13k – I’m going the rest of the way and installing geothermal – even without grants! I don’t want ANY noisy, unsightly electro-mechanical boxes outside exposed to the extremes of the weather. But that’s just me. SR |
RE: new heat pumps for cold temperatures
| | |
| And the payback period for this equipment over more conventional equipment is??? You can buy a lot of electricity for the extra $$ the are charging. |
RE: new heat pumps for cold temperatures
| | |
| Here in the heating dominated Great White North, it’s not uncommon for homeowners to be paying $4000.00, and even more, at last year’s prices, just for heating alone. So if your savings with geothermal are in the order of 60% or greater over conventional equipment, it makes sense when looking at what your costs are going to be over the next 20 years in both energy and maintenance, as geothermal has both the lowest maintenance costs and longest life cycle of any mechanical HVAC system. Then of course there are the issues of the environment and national security, not to mention resale value of a home with geothermal. Regarding resale value, we’ve had an independent, professional energy audit done on our home that indicates it’s one of the most energy efficient in the country. I’m betting that verifiable energy efficiency pays back a premium when it’s time to cash out. SR |
RE: new heat pumps for cold temperatures
| | |
I really don't have an opinion regarding this new technology. However, I did want to comment that there are other ways to decease your carbon footprint and decrease your energy costs, if Greengirl is interested. We built a new house last year, sealed it tight, insulated it, and used very high efficient windows. We placed a wood stove on the main level and dual heat units both up and down. We rarely ever used the furnace last year and pretty much heated the house mostly with the woodstove (very high efficient, minimal pollutants). Our electricity for the heat pumps is from credits of windpower that we pay for. Maybe a little more, but worth it for us. For a small cost of electricity for wind credits, and high efficiency Trane Units, we still have spent less up front and are spending less monthly than Geothermal or the new technology units being considered here. There are other ways to be energy conscious and save money. |
RE: new heat pumps for cold temperatures
| | |
| DING, DING, DING, DING, DING, DING. I believe we are finally on to something with the post of homeowner2007. Building the home properly comes first and foremost to the heating and cooling system. It amazes me how poorly our country builds our commercial buildings and homes. As far as energy efficiency goes, we build like crap. Building the home as tight as possible, by using the most efficient windows and doors, and not having a thermal bridge in your exterior walls will go much further to saving energy and money then any other efforts. I frequently look at high end, custom built homes and it’s amazing how much these builders don’t know, (or don’t care). Last month I saw a multimillion dollar home being built with the most expensive and most energy efficient natural gas fired heating and cooling systems. The walls were all 2x6 wood construction with a hand made brick exterior. The windows were the most expensive true divided light windows on the market but those true divided light windows are far less energy efficient. These windows were chosen for the appearance and not energy efficiency. You can spend all you want on the walls and insulation but putting a huge hole in those walls and placing inefficient windows and doors in those holes is defeating the purpose. I saw were the plans called for batt insulation, but these homeowners could have easily afforded closed cell, open cell, or spider insulation. The house wrap was also poorly done and the building envelope was not tied into the roof envelope properly. Even when using, 2x6 wood framing and insulating those cavities, the wood acts as a thermal bridge to the outside and greatly reducing the energy efficiently. Not to mention every window in the house, (about 80) was being wired for window candles and the exterior will have elaborate landscape lighting. We all like these bells and whistles but come on? This home will be far more energy efficient then homes built decades ago but it’s not good enough. If the home was designed properly, they could have reduced the tonnage needed to heat and cool the home by as much as 20% in my estimation. They also would have probably saved 40%-50% on their heating and cooling bills. Geeeesh, it’s not like they didn’t have to money to do it the right way. Worry about the building envelope first then the rest is downhill. Properly designed window treatments also go a long way. |
RE: new heat pumps for cold temperatures
| | |
| Perhaps through the appropriate levels of government, a minimum (high) standard of energy efficiency needs to be imposed on all new construction. Not meeting the standard (such as LEED) will result in a high annual energy inefficiency surcharge tax. That, coupled with energy efficiency rebates or tax credits for retrofits on existing buildings may be a good place to start. It has to be made very painful to build commercially, industrially, institutionally, or residentially in a fashion or manner that does not incorporate current best practices of energy efficiency in construction and design. Energy efficiency is a crucial environmental as well as national and international security issue. Besides, it can be beneficial to everyone’s financial bottom line. Immediate energy savings will ultimately more than make up for any incremental increase in first costs by building to the highest standard. SR |
RE: new heat pumps for cold temperatures
| | |
| GreenGirl, I called them but they still had no dealers in Virginia. Did you have any luck finding a dealer that will install it? I'm not normally an early adopter, but the technology seems straight forward. But the real attraction is the discharge air temperature in the heat mode. Larry |
RE: new heat pumps for cold temperatures
| | |
| I have now spoken with their guy at the factory who asked me to send him the names of several hvac people here. I did and he contacted the one who had done our house when it was built. He was waiting to hear back from another and told me to go ahead and call any in which I might be interested to have them call him. he is apparently being inundated with people inquiring of late and can't keep up with all the calls he has to do to pursue dealers. Supposedly ANY qualified hvac people can do this installation since there is no new science in it at all. The catch is getting people who are used to the normal mousetrap into researching the thing in order to understand it and believe that it isn't smoke and mirrors. I then called our guy here and he did indeed do just what the Hallowell guy said he would do, that is try to steer me to standard equipment. He also apparently thought, as so many do, that I am 1) a stupid woman, 2) an uneducated stupid woman 3) haven't done any homework or research on the thing BEFORE calling Hallowell and was therefore being duped by the snakeoil salesman at Hallowell. It took a long conversation before I could convince him to proceed to look at the stuff that I have found copious volumes on the internet from all kinds of sources beyond Hallowell and to come and take a look at our house to see our system and see what new tubing etc woud be necessary to change over to any new refrigerant system. Theoretically the duct work should be fine since they were the ones that installed it. More on that later. I will see what he says and then procees to call a couple of others to get three to see how they vary. According to the Hallowell guy, the cost of the unit to the dealers would be the same, so any variance in cost would be whatever any respective contractor charges as their "price" and that can vary at lot, even thoug you wouldn't think so unless, as we all know, some people are just out to make a killing. I'll post as I find out more. The obviuos thing is that, presuming the unit works as stated and all test seem to bear that out, it would be of more benefit to those in colder climates than Virginia. However, with our situation with the cost and volume of the propane for our hydronic heat, the relative cheapness of electricity here, the age of our AC and heating system and water heater, any of which could go at any time, coupled with the cost savings of ANY modern day heat pumps which is way above even modern AC's, it seems like a really viable possibilty that must be explored. It just irks me so that people have tunnel vision and don't want to explore new things. I know I would pay more, but how much more and how long to recoup in OUR situation is the key.Then we get into the going greener thing, which is valid these days too. So I would suggest that you contact several people where you are and talk to them and have them call Hallowell and talk to Randy and see what you can uncover. When the thing goes public big time for residential soon, it will be a different story. |
RE: new heat pumps for cold temperatures
| | |
| "However, with our situation with the cost and volume of the propane for our hydronic heat, the relative cheapness of electricity here, the age of our AC and heating system..." - This is the first time that I read that you had propane heat. Propane moves with the price of natural gas and, to some extent, fuel oil. I don't have to tell you that propane is the most expensive fuel for heat. "I know I would pay more, but how much more and how long to recoup in OUR situation is the key." - The balance point (the outside temperature at which an air source heat pump can no longer supply enough heat and supplimental heat is needed) depends on house construction, insulation, heat pump capacity, compressor age, etc. Assuming a balance point of 32 degrees, any savings in electric costs from using the Hallowell versus an typical air source heat pump with back-up has to be computed for the number of heating hours below the balance point of 32 degrees. How many heating hours below 32 degrees are in the Virginia winter? Not many as compared to the Northeast or Canada. I am trying to be realistic here, not a pessimist. With your moderate Virginia winters, you will not, in your lifetime, save enough money in electricity to cover the additional costs of the Hallowell. The Hallowell may be great for the next owner of your home (I say the same for Geo - sorry, Steve), but it won't save you any operating $$ that a typical air source heat pump won't save you. |
RE: new heat pumps for cold temperatures
| | |
| The new Hallowell web site is up and very inclusive and good looking. Much good info there now. Check it out. |
RE: new heat pumps for cold temperatures
| | |
| As a homeowner who has recently installed a Hallowell 36C/35H heat pump, I feel compelled to contribute my 2 cents worth to this thread. We have lived with a "conventional" heat pump since 1978, so I am familiar both with HP technology and have the basis for a comparison between the older HP system and the Hallowell all climate HP (yes, I know it has since been re-branded). Our home was designed to include an air-to-air solar system where the HP was intended as a backup system; in reality, the solar system augmented the HP. The home is approx 1700 sq ft with 6" of cellulose insulation and energy efficient windows. We are located in climatic zone 5 and since 1978, the average yearly HDD has been 7200, with a range from 5858-8065. Our annual kWH electrical consumption has averaged 18,928 kWH with a range from 14380 to 26318 kWH. The local utility currently charges $0.10/kWH; this has increased markedly since 1978 and is unlikely to go down. As our home was designed to be total electric, migrating to natural gas (the predominant heat source in our town) was not a particularly viable option. I came across a link to the Hallowell system nearly 9 months ago and immediately sent an email describing much of what I said above. I was soon contacted by Duane Hallowell (CEO) with whom I spent over an hour on the phone! Over the next few months I was markedly unsuccessful in convincing local HVAC contractors to undertake the installation of the Hallowell system, but I eventually found someone toward the end of summer. The system was delivered at the beginning of November and operational shortly thereafter. Due to the integration of the previous HP with the solar system, it was not a "plug and play" installation, however it did go relatively smoothly. The indoor air handling unit is manufactured by York; the outdoor unit contains proprietary circuitry and control algorithms for operation of the system. The hardware cost was significantly less than the numbers I have seen quoted on this site; I do not yet know the installation charges as I am currently on travel. My experience thus far indicates that the system performs "as advertised" and while I have not yet been able to compare consumption data with previous years, stay tuned. In scanning the various posts, I did not see where anyone identified David Shaw (who holds the patent for the ACHP) as a retired Carrier engineer who started working with Nyle prior to moving the patent to Hallowell for reasons noted elsewhere (see http://www.construction.com/NewsCenter/TechnologyCenter/Headlines/archive/2006/AR_0306.asp). I would also note that trials of the technology have (and are) being carried out by a College in eastern WA (see http://www.chelanpud.org/all-climate-heat-pump.html). I would note that David Shaw has thought about the short comings of the conventional HP (email for material). The paper was presented in 1984, possibly prior to his tenure at Carrier. Finally, I note that the Bonneville Power Administration has also evaluated the system for use in the northwest (see www.aceee.org/conf/06et/TP1-1_HadleyHallowell.pdf ). |
RE: new heat pumps for cold temperatures
| | |
| "The hardware cost was significantly less than the numbers I have seen quoted on this site; I do not yet know the installation charges as I am currently on travel." - I would be interested in your installed price. What was the split between equipment and installation? What kind of heat pump did you have before the Hallowell? What state (Zone 5) do you live in? You have had the unit for less than a month - installed November? 10 cents/kw-hr is not that bad. Maryland is 13 cents delivered. Our houses are the same size. You have 2x the number of heating degree days than I have in Baltimore. I'm thinking that your electric bills can get pretty steep. No wood stove or pellet stove? Great info on this post. |
RE: new heat pumps for cold temperatures
| | |
| The original HP was an Armstrong AirEase; the compressor in the outdoor unit failed in Feb 2004 and a 3.5t Concord outdoor unit was brought in as a replacement. Due to incompatibility in efficiencies (indoor/outdoor) and the cost of running on electricity for several months of the year, I made the decision to go with the ACHP. We live in northern UT at an elevation of 4500 feet. Had a Jøtul woodstove until Feb 2007; my wife was not fond of the frequent chimney fires we experienced. Installed a pellet stove instead. We have seen -20F but not for a long time; last winter we got down to -5F on several occasions. Final cost not yet available and yes, it was installed earlier this month. |
RE: new heat pumps for cold temperatures
| | |
| Nout: Best of luck with the new unit. Keep us updated please. Take care. |
RE: new heat pumps for cold temperatures
| | |
Nout, Thanks so very much for writing as someone who actually has the unit! I am so looking forward to hearing every detail of as much as you are willling to share. I am particularly interested in the costs for both the unit and installation and how you finally got someone to believe and do it. Operating costs will be interesting too, but as I'm sure garyg will point out, you are in a completely different zone than we are, and I realize that completely. You can compare to yourself though. The people at Hallowell have been just wonderful to help a lowly homeowner! I have done so much research into this and have been so smitten with it only to have so many here disagree...... You might want to post your original response on the hvac-talk.com site too, under residential because there are as many or more people, both pros and homeowners such as myself who are writing about it there. Just look for the title all climate heat pumps and join the fray! Thanks again and waiting eagerly for a new chapter. greengirl |
RE: new heat pumps for cold temperatures
| | |
| greengirl_va, Be happy to go into more detail but would prefer to do so "offline." If that works for you, pls send email to: ftb (@) cc (dot) usu (dot) edu NoUT |
RE: new heat pumps for cold temperatures
| | |
| This is a follow-up to the note I previously posted regarding the Hallowell All Climate Heat Pump (now re-branded as the Acadia). Our unit was installed in November and has been operational since November 13. Over the next 30 days our average daily consumption has been 47.8 kWH; this is 20% lower than our lowest historical consumption for this time of year (averaged over the lowest 9 years) and 43% lower than the highest historical consumption (averaged over the 8 highest years). I estimate that our non-heat load is 508 kWH/month or 16.9 kWH/day (again based on 25+ years of data), so the heat load reported here was about 31 kWH/day (106,000 BTU/day). The number of Heating Degree Days (HDD) is (unofficially) 1024 as derived from http://www.climaton.com/forecast/UT/Logan.php As the HDD data is tabulated on a calendar month basis and our electric meter is read in the middle of each month, I have not attempted to correlate the HDD and consumption data. Our largest consumption rate occurred during a month when HDD=1476 and the lowest when HDD=973. Thus far, the results are encouraging relative to the heat pump that had been running since 1978. I have no connection to Hallowell and their system was the optimal solution to my particular situation. The lowest temperature during the 30 days referenced here was 7°F. NoUT |
RE: new heat pumps for cold temperatures
| | |
| NoUT: What was the installed price of the Acadia? Was it a "drop-in" install? How much ductwork was involved with the install? Best to you. |
RE: new heat pumps for cold temperatures
| | |
| "Thus far, the results are encouraging relative to the heat pump that had been running since 1978." Almost anything new should beat the pants off a 30 year old unit. |
RE: new heat pumps for cold temperatures
| | |
| garyg: I don't yet have installation charges, but the total cost will be north of $7500. No, it was not a "plug & play" installation as the Hallowell AHU was taller than the original AHU. There was no heating duct work required; however, it was necessary to add a piece of sheet metal to accommodate the return air but this was trivial. brickeye: I would remind you of the nature of this thread (new heat pumps for cold temperatures) and suggest that most homeowners do not update their HVAC systems until a failure requires doing so. In point of fact I had a SEER 13 outdoor unit running for 3 years and the consumption rate I quoted is 50% of the average consumption during those 3 years. This speaks to your "beat the pants off" theory. |
RE: new heat pumps for cold temperatures
| | |
| I am impressed with the generally high quality of the comments posted. Here are some observations of my own: I live west of Boston, and my cost of electricity is $.118 per kWhr, or $0.0328 per MJ (megajoule; one kilowatt-hour is 3.6 MJ). By contrast, my cost for natural gas is $1.59 per therm, where a therm is 100,000 BTU and a BTU is 1055.9 joules. So the cost of gas is $0.0151 per MJ, or $0.0188 per MJ at 80% efficiency. The ratio of the cost of electric resistive heat to the cost of gas heat is thus 1.74:1.00, which means that a heat pump with a seasonal coefficient of performance greater than 1.74 will cost me less to operate than a gas furnace, neglecting (for the moment) capital costs. The Hallowell heat pumps achieve this by a wide margin. It seems to me that three questions remain: (1) How well do the Hallowell heat pumps handle frost build-up on the outside evaporator coil? This is critical in a wet climate, and can have a big effect on seasonal COP. (2) How stable is Hallowell? Evidently they are not a publicly traded company, and rapid growth can be hard on a small company with inadequate capital. (3) How reliable are their heat pumps in the long (10-year plus) run. As for capital costs, they appear to be not all that far from the conventional combination of a gas furnace and a central air conditioner. In any case I will give them serious consideration when my current heating/cooling system dies. And, if they were publicly traded, I’d consider buying their stock. |
RE: new heat pumps for cold temperatures
| | |
| Peteroff: "The ratio of the cost of electric resistive heat to the cost of gas heat is thus 1.74:1.00, which means that a heat pump with a seasonal coefficient of performance greater than 1.74 will cost me less to operate than a gas furnace" - I'm not sure how a "seasonal COP" is calculated. My new 3 ton Goodman has a COP of 1.84 at 0F outside, but I'll still need aux electric heat in addition to the heat pump as the balance point of my home is about 20F or so. The question for you in regards to the Acadia is "what is the balance point of the house and how many hours are the outdoor temps below that balance point?" This is where the Acadia will save a homeowner money by being able to run a heat pump below the balance point without aux electric or gas. The balance point is based on many variables including house design, insulation, ductwork, outdoor temp, indoor setpoint temp, heat pump btu capacity at cold temps, etc. Using your numbers to calculate the cost of 1 million btus: Gas at $1.59 per therm and 80% efficient: (1,000,000 btu / 103,000 btu per therm)($1.59 per therm)/.8 = $19.30 for 1 million btu. Straight electric at $.118 per kw-hr total delivered price: (1,000,000 btu / 3413 btu per kw-hr)($.118 per kw-hr)/1 = $34.57 for 1 million btu. Heat pump at $.118 kw-hr, COP = 2.82 at 25F (COP at 25F is from my Goodman tech info) (1,000,000 btu / 3413 btu per kw-hr)($.118 per kw-hr)/2.82 = $12.26 for 1 million btu. Although cheaper to run, the heat pump will see a lot of wear and tear because it will be operating often. It may have to be replaced every 10 years while a gas furnace may get 20+ years. Take care. |
RE: new heat pumps for cold temperatures
| | |
| EER ("Energy Efficiency Ratio") is measured in watt-hours per BTU, and is simply COP multiplied by 3.41. Thus, an air conditioner with an EER of 13 has a COP of 3.81, that is, 3.81 units of heat energy are removed from indoors for each unit of electrical energy consumed. In heating, EER is highly dependent upon the outside temperature. "Seasonal" EER (SEER) is an attempt to average EER over climate variability. For example, if the average January-February temperature in Boston is zero Celsius, the normal range might be -5 to +5 and the extreme range -15 to +15. The SEER is the EER averaged over these conditions. This isn't easy to do unless you have a database of typical hourly winter temperatures. And, in any case, manufacturers' SEER values are based on steady-state EER values, and do not correct for start-up/shut-down losses in real-life operation, nor for the effects of ice build-up on the outside heat exchanger. This is why I wouldn't take manufacturers' data too seriously, and would prefer to hear from actual users in climates similar to those here in the Boston area. |
RE: new heat pumps for cold temperatures
| | |
Greengirl - I went to the site and had a look. Read some of the links as well. Here's what I think: 1. In "heatpump-friendly" weather, it's more efficient than conventional heatpumps. The question then becomes - "how does that jive with your location?" 2. The concept is a variation of existing technology. said technology has been in use awhile. 3. The website is... a "commercial" designed to sell a product. As such it will always frame the product in the best light possible. 4. If you find an installer and have to convince him that this is the system that would best suit your needs, think twice. Find an installer that is on board with this unit and it's application. If you can't - consider why that might be. Perhaps he's unsure of its benefit to you. Perhaps he's unsure of his abilities relative to the install. Perhaps he doesn't want to be part of an install that you will ultimately regret. In my own business occasionally someone will want us to produce a product that we by nature of experience know will not satisfy the client. If the client will not listen to us because they believe they're right; this can be problematic. Often we can educate the client before they spend a great deal of money on a bad venture. Your local HVAC guys may be trying to do exactly that. I understand your enthusiasm for this but realize that when people in trades get excited about a product and its use; then you as a consumer can generally have a higher confidence level in the outcome. Clearly you're not stupid, uneducated, etc. But that being said; don't let yourself be found as "unwise". -br |
RE: new heat pumps for cold temperatures
| | |
| "Clearly you're not stupid, uneducated, etc. But that being said; don't let yourself be found as "unwise". " - Outstanding advice. |
RE: new heat pumps for cold temperatures
| | |
| Heatpumps are heatpumps are heatpumps. Nothing changes except the brand. Efficiencys are basically the same. They are goverened by the outdoor temperature. There is nothing that is really much better efficiently. Only better mechanically. But they use the same components. |
RE: new heat pumps for cold temperatures
| | |
| Alas, the comment above by bob brown is simply not true. The Hallowell heat pumps do represent a better-performing design, and the comment above has no factual basis. The writer should know better. |
RE: new heat pumps for cold temperatures
| | |
This is an update on the Hallowell "Acadia" installed last November. For reference I will list the consumption for the same periods a year earlier and the heating degree days ( ) corresponding to the months in question: 2006/2007------------------2007/2008 Nov/Dec 2845 (1162)-----1417 (1230) Dec/Jan 5036 (1483)-----2464 (1363) Jan/Feb 3627 (965)-------2661 (1221) Feb/Mar 2522 (787)------1811 (990) At a nominal rate of $0.11/kWh, this represents a reduction of more than $500 over the previous year (which was not as cold as the current winter). Note that the HDD data are for a calendar month while the consumption data refer to readings made monthly, but in the middle of each month. In response to Peteroff, I can make the following observations: frost buildup on the coils is a non-issue; that said, my problem has been the by-product of the defrost cycle. Most of the winter I had a 6" block of ice under and around the outdoor unit. The installer ignored the manufacturer recommendations regarding installation height above the slab and I fought with reducing the ice most of the winter. This will be rectified by increasing the height of the supports and installing self-regulating heating cable. Note that the labor costs were roughly 1/3 of the total cost. I did experience a failure of one or more of the temperature sensors in the outdoor unit. Hallowell sent replacement sensors (new design) and a new control board, which upgraded the system with their latest control algorithms (yes, there is a CPU on the control board). The parts were sent from Bangor via next day air and I was able to get assistance on the weekend (from the CEO no less) in addressing a minor restart issue. My previous posts discuss our climatic regime - dry, high altitude - and house configuration. Based on data acquired since 1978, the current winter has been one of the colder winters over the past 3 decades. With the exception of the sensor failure noted previously, the Hallowell Acadia has performed spectacularly and I can highly recommend the technology that Hallowell have developed. I hope this helps others that are considering the Hallowell systems and I would be interested in learning of the experiences of other consumers using the Acadia or addressing other aspects of operation/performance. |
RE: new heat pumps for cold temperatures
| | |
| nout, the data you posted are very useful. It's clear that your new heat pump is outperforming the old one by nearly 2:1; you've gone from about 3.2 kWhr/DD to 1.7. I'm looking forward to the results after a full year. I'm also glad to hear that frost build-up on the outside coil is no problem, but your difficulties with freezing drip suggest this would be even worse in a wetter climate. Still, I'm pleased to see that performance is not adversely affected by freezing, at least in your dry region. |
RE: new heat pumps for cold temperatures
| | |
| Nout, What do you pay for electricity during the winter vs. summer months? |
RE: new heat pumps for cold temperatures
| | |
Hello Nout, You also green girl_va--or anyone else--please chime in!! I saw some of your posts about the Acadia ACHP--I must say--I know nothing about heat pumps period!! That said, we are building a new home (very tight envelope) in SW New Mexico--@ 5600 ft. el. It does get cold here--and lows can get down to 7 or 8 degrees, but usually bounce back during the day as we do get around 320 day of sunshine here--or so they say in the retirement books--LOL Also, we get some humid days in the monsoon season--and the wife hates to be (hot) Like this AM, we had a low of 27, just before sunrise, but are headed for the 70's--so we have lots of 40 degree (swings) in our temps here. We are retired, and on a fixed income, this will be our last home, most in this area are from the (old school)--me to kinda--and HP's of old, are rumored to not work well here!! I have labored on how to heat and cool this home--as most in this area use forced air (propane fired) with wood or pellet stove as a main source of heat--we hate the thought of chasing firewood, or pellets--and the scariest part is propane is at $3.00 a gal. with elec @ ,10 cents a kwh.??? I would love any thoughts at all on how you like your system--and do you also have a back-up--we could use our ( propane-fired, radiant heater) the kind that's called a blue flame??--un-vented--hangs on wall--or stand--gets around 99 percent efficient?? thanks again, Rocky |
RE: new heat pumps for cold temperatures
| | |
| Re satester2: Have you considered a geothermal HP? Up front cost would be high but so would long term satisfaction, operating costs and resale value. SR |
RE: new heat pumps for cold temperatures
| | |
Go to HVAC-Talk.com and read the lengthy number of posts there from the thread I started. As my last one stated, pay particular attention to the ones from Stormman, jchaters,a nd nout (who you already know to see). I am waiting till the end of the month when the 2008 model is supposed to be out. It will have even better numbers and since we were not having to do it in the fall since our water heater graciously held on all winter, we decided to wait for the new one. It will be the same cost and better numbers, so why not. I got very tired to trying to get input and having guys just refuse to admit that this was viable. You can read for yourself. Nout has an extensive post recently about his unit. He has been emailing me for several months, being very kind to discuss his install. I would imagine that he would visit with you about it as well. Look for his email in one of these threads.... I am still, or even more encouraged, by everything that I (we) have read since I started this. If you have gone to the Hallowell web site and seen their news section, the government contracts are enough to give give one confidence.I can share more once we actually have it, but then we will be using it first in summer, not winter so I won't have cold comparisons until next year. |
RE: new heat pumps for cold temperatures
| | |
thank you so much greengirl, I have read everything you and nout have written. I did try to contact him via his e-mai--and it did not work--could you forward ours--I would love to talk to him--and you, also--email is rockyvicki(@)gmail(dot)com I did get a quote from the USWest--just the other day on the 36c/36h--I would like to compare notes with you--and see if this is the new one or not--write please |
RE: new heat pumps for cold temperatures
| | |
| How much is the quote? Is there a lot of labor involved in the install? |
RE: new heat pumps for cold temperatures
| | |
| Nout, I live in the Pocatello ID area and am looking into the Acadia heat pump as well. I would like the opportunity to discuss your experience with the equipment and the installer you used. I know winters in Logan can be quite treacherous from my time there in college and believe if you are happy with your equipment it would work well here too. Would you please send me an email at kmecham@gmail.com so I can ask you some more specific questions? Thanks! |
RE: new heat pumps for cold temperatures
| | |
| I do not know if quotes are allowed in the open forum, but if you would like to email me--my email address is in the april 15th area. |
RE: new heat pumps for cold temperatures
| | |
| Greengirl_va: I looked for you on HVAC-Talk.Com but couldn't find you (or nout). In which thread did you post? |
RE: new heat pumps for cold temperatures
| | |
| My fumble fingers typed my name wrong when I signed up, so it says greengril.... Look on page 4- info on new allclimate heat pumps......Happy reading! |
RE: new heat pumps for cold temperatures
| | |
| Hi All, Let me first say that this thread has been an excellent read! It's great to see some friendly differences between folks who like different technologies. I'm building a house in southern NH and will be moving in late May. The house originally came with a high efficiency propane FHA furnace. Well, my current house (also in southern NH) also has a high efficency FHA furnace and it costs a fortune to run. I currently heat 3,100 sq' (2 zones) @ $2.96/gallon of propane. I calculated 2 heating seasons ago that I used 1,100 gallons of propane. This past season has been a bit less painful as I supplemented our heat with a pellet stove. I ended up saving about $500 for the season in fuel costs, but I have to say lugging those bags of pellets up and down my cellar steps and dealing with the maintenance of cleaning the stove has not been fun. So back to the new house. I decided I didn't want to deal with propane for heating, nor another pellet stove, again so I had our builder look into geothermal for me. The quote for that (which would include a cut for the builder) came back at just under $40k for a system where they dig trenches in the yard and bury loops. I believe it was called a closed loop system. The builder then suggested the Hallowell Acadia. After digging around on the internet to get some information, I decided to go with it for the cost of $13,000 over the high efficiency FHA propane system. The unit I was quoted on is the 46C unit and includes the installation, air handler and additional supplemental electric heat. I was OK with that cost since it will also provide central A/C, which I was going to install after we moved in. I'm very excited to experience the Acadia and looking forward to cheaper heating costs. Also, I met the VP of Hallowell sales at a local housing convention in Boston last month and got to see the unit in person. I was even more excited after that! |
RE: new heat pumps for cold temperatures
| | |
| "I decided to go with it for the cost of $13,000 over the high efficiency FHA propane system." If you dont mind me asking, what was the total cost of the Acadia if it was $13k more than the propane furnace? I think you should do well with this unit in your NH winter climate. Keeping the outdoor unit free from deep snow is a must. Good luck. |
RE: new heat pumps for cold temperatures
| | |
| Hi garyg, I'm not sure what the total cost comes to since the propane furnace system was included in the overall house price. I should say that the Hallowell unit is the 42C, not 46C. Typo on my part. We just got through a brutal winter here (2nd most snow ever on record), but I'm looking forward to next winter to see how the unit performs. We're scheduled to close on the house on May 16, so the unit should be going in any day now. The duct work is being installed in the basement now. I'll plan on taking photos and posting them here if folks are interested? I should also say that the folks at Hallowell have been great. They volunteered to have one of their engineers come down from Bangor, ME to supervise the unit install for free since there haven't been many installed in my area. |
RE: new heat pumps for cold temperatures
| | |
Hi dsilvest, I think you got a great price on that system. I am building a 2500 sq ft cape in Southern Maine. I was quoted $22,000 and $16,200 to install the Acadia with ductwork. Hallowell sent a sales rep to talk to me about the system but he was not much help. I was able to speak with someone in Bangor, Maine that has had the Acadia in his 2400 sq ft cape for 2 years. His electric bill is $100.00 in the summer and around 350.00 in the winter. He figured he spends around $1,500 to heat his house per year. Please keep us posted. Also, if you don’t mind saying, who is installing your system? |
RE: new heat pumps for cold temperatures
| | |
| Hi bobo1756, I figure the propane system costs about $5-6k or so. That would make my actual cost for the Acadia about $18-19k. Based on the quotes you received, I'm happy with that. I'll be curious to see what it costs to heat my home next winter. Our house is going to be energy star, so hopefully that will help with the utility costs as well. My long term plan is to have some PV panels installed on the roof so I can "get off the grid" entirely. Unfortunately NH doesn't have the best rebate programs for solar panels at this time :-( The house is being built by Adamyk Homes. I'm not sure who the HVAC contractor is. Although he has installed several systems in the area according to the builder. |
RE: new heat pumps for cold temperatures
| | |
| Hi everyone, We're building a house in Fairfield County, CT, where costs are extremely high. We have actually stopped the progress on our construction to figure out what to do for HVAC, because the 93k cost of geothermal was too much given some cost over-runs we've had (that subject is for another post!). We are seriously considering the Hallowell Acadia but no one around here has it or has installed it that we know of. We have 3 installers willing to do it and we have gotten one quote in for 53k which includes an ERV unit. It is a 4630 sq ft space with another 1200 sq ft heated and cooled in an attic studio. The quote is for a 9 ton system. We should get the other quotes soon. Dsilvest, what is the size of your house you are building? Does this cost sound high (everything is here, but sometimes contractors just throw high numbers at you to see if they'll stick! It is tiring...). We were going to do blown in foam insulation, but the 37k quote for that was not going to work; we are looking at a combination of cellulose applications which initially quoted at 26k, but after protests, he changed and removed some of the "extras" and now it's 16k or so. We are planning on this being an Energy Star house as well. I have learned a lot from reading this post, and would appreciate any advice that could be shared about the Hallowell system, costs for our situation, etc., recommendations for install since it will be someone who hasn't done one, etc. Nout, I tried to email you today as well, and hopefully you will get it. Greengirl, I know how you feel - I'm primarily in charge of our construction (with our project manager) and found out about Hallowell by my own research. I have some interesting reactions with all the contractors I have dealt with - mostly respectful up front, but clearly assuming I know nothing, and definitely ignoring my upfront mention of severe budget issues with most of the quotes that come in. If anyone is in CT with this system I would love to hear from you. We have not had good communication with Hallowell yet; they didn't answer my husband's email, but project manager has talked to them a bit. They won't reveal any pricing, but one HVAC guy said the cost to him is 11k per unit - does anyone know if this is correct? Thanks for your assistance/advice! |
RE: new heat pumps for cold temperatures
| | |
The new units ar eout and ours is in town, due to be instaled next week. We will be the first here, of course. Our contract is for $11,600 and it was about that for the other estiamet we got as well. Both from HVAC companies wh had never heard of it. You have read my whole saga here, I'm sure.... Ours is a 3.5 ton, so therefore is not as large as what you are dealing with, so numbers are probably not comparable. If you call Hallowell and ask for Randy or email him at rmargraf@gotohallowell.com, he will either answer your questions or put you in contact with who can. He was very helpful on the phone with me over the course of several months as we awaited the 2008 updated one, with the inproved SEER etc. Once I got into emails with him, as time went on, he got shorter with his answers but I know they are in high gear now. He will answer but not use extra words beyond the necessary.... He would never give me pricing either but clearly it isn't as high a cost as whoever led you to believe because companies don't install for free.Their units are only 3.5 or 4 ton, so you clealy will have two. If that's the 11,00 cost to which you refer, then that would be about right probably. Nout should answer, especially if you email him, He doesn't read the thread all that regularly... Our company here is extremely intrigued! They were to put it in this week but wanted more time ot study the new beast, they were so interested... I surley did not intend to stir up the waters as I did when I started this thread but it has been quite an eye opener seeing the responses from the guys.... People are so afraid of new things and I am so intrigued! You can check out the HVAC-talk.com thread too. |
RE: new heat pumps for cold temperatures
| | |
Thanks, greengirl, I will contact Randy at Hallowell. Did you already have all the ductwork in place? I'll be interested to hear how it goes with your system. Is Nout's email correct as written much earlier in the thread? We have 3 companies here who are eager to install. One is well known by my project manager but he usually only installs the best hydro aire systems; one is new to us and usually installs the Bryant Evolution heat pump sytem (which needs propane back-up), but they've installed one Hallowell but it hasn't been turned on yet; and then there is a guy who was familiar with Hallowell but hasn't installed one yet, and he does some geothermal. They are probably all competent and a lot of it will come down to cost. I'll let you know how it goes here in CT. |
RE: new heat pumps for cold temperatures
| | |
It was the original email through which I contacted him. He then gave me another. I will inquire of him whether the first is still active, since I know he is between states and residences.... Yes, we had ductwork from our first set up, so our cost is just for change out. But tht does inculde some electrical as well. I know that nout bought his himself somehow and then had to hire a company to put it in, so he knows what he was charged for the unit, but that was retail, not wholesale as a company would pay...What is you remail, so I can tell him to watch for it? |
RE: new heat pumps for cold temperatures
| | |
Hi greengirl, Tell nout it has reidhigham before the @ . It's interesting that he got it himself; my project manager said Hallowell says they will only sell to licensed HVAC contractors. Thanks for your help again, and keep us posted on how you like your system! |
RE: new heat pumps for cold temperatures
| | |
| Hi ggrose, Our house is an approximately 3,600 sq' 2-story colonial with 3 heating/cooling zones. We'll have the 4-ton unit, which was $13,500 ABOVE the standard 90%+ efficiency propane furnace that we upgraded. Also, we're going with a Blown-In-Blanket (BIBS) insulation system that cost $7,000 ABOVE the standard fiberglass batts. Based on your sq', it sounds like you're probably looking at 3 units, which would put your quote in line with what I'm paying for one (the $13,500 + whatever the standard propane unit costs). I'm not familiar with the cost of the spray foam insulation, but from what I understand it's better and more expensive than BIBS. My costs were hard to swallow at first, but when you're not only saving on monthly utility bills, but also helping the environment, it's a little easier to swallow. We're closing on our new house in the next 2-3 weeks. The Acadia is not installed yet, but should be any day now. I'm looking forward to it! |
RE: new heat pumps for cold temperatures
| | |
Hi dsilvest and all, We finally decided on an HVAC contractor and we are going with a Hallowell Acadia system. It is a 3 unit system - 4,3, and 3, with separate zones. Considering what the cost of a typical hydro-air system was going to cost, and the extremely high cost of the geothermal (seemingly going up daily because of demand and climbing well prices), we think the 46k cost of the Hallowell (installed) is okay. This does not include the humidfiers, air cleaners, or ERV unit which are add-ons. We're paying about twice the cost of fiberglass for upgraded cellulose insulation, but approx. half of what foam would have been. We are still to price solar hot water and hoping it is a possibility. Good luck with yours, and let us know how it is, as will I. |
RE: new heat pumps for cold temperatures
| | |
| "...we think the 46k cost of the Hallowell (installed) is okay. This does not include the humidfiers, air cleaners, or ERV unit which are add-ons." Wow. That's $15k per unit without the add-ons. I'd get a 10 year parts and labor warranty for that amount of $$. Good kuck. |
RE: new heat pumps for cold temperatures
| | |
| Hello everyone, After starting this well- lived thread, I can report that our Hallowell Acadia is IN now and cooling like a charm with 100 degree heat that hit just as it was finished! We did wait, as those who have kept up have read, for the 2008 model upgrade with the new logic board and the different compressors. (They were a result of Bristol discontinuing the ones that Hallowell was using and Hallowell choosing to use differnt ones before being forced to.) Of course the main issue from the beginning was the heating side, but it will be months before we know that answer. Right now I'm just grateful to have cool and it be as good at it as the AC we had. Comparison costs for that part will take a month to determine but it is a given that a new unit of whatever willbe more cost effective than a 16 year old one..... Ours wound up at the quoted $11, 600. It was a replacement but with just a bit of new wiring and duct modification where the air handler sat. It was and is only one zone, even though with a two story house we could have benefittedf rom two, that's not the set up we had and couldn't go that far with costs to convert! It was a very staight forward replacement but there were two issues that I found online that I had to insist on and actually call Hallowell and have them tell the conrtactor that it HAD to be done the way stated. One was that the unit has to be up on legs of some height- not any higher than one might have for 3-4 inches of snow- even if there is not much snow in your area. The unit has ventilation holes in the bottom that must both drain AND ventilate. The other issue is that the filter dryer MUST be inside be next to the air handler and insulated, NOT outside like they do them everywhere here.That one took a while to get across and finally the phone call to Hallowell. Contractors know what they are used to and see no reason for changes unless forced to. It worked out fine in the end but if I hadn't been vigilant and insisted, they would not have done it! So, at this point everything has worked according to Hoyle. We are glad we did it and I will report honestly how it does once we have winter. And of course every winter will not be the same..... I will watch for others to report their reactions to their units as more people acquire them! Please ask any questions that you might have and I will try to answer them! Green girl |
RE: new heat pumps for cold temperatures
| | |
| Hi Greengirl, I am also looking into the Hallowell sysem. Can you share what ton/model system was installed in your house, and did the install include any ductwork modifications? Did it include removal of the old equipment? It would be good to know what work was included in the price you paid, so I have an idea where my estimate falls in relation to your job. Thanks! - Chris |
RE: new heat pumps for cold temperatures
| | |
| Dear GGROSE, We live in Oxford CT and are considering the Hallowell system. We have a 3200 square foot well-insulated house and are considering a 4 ton unit. What HVAC contractor did you use and were you satisfied with their work? If anyone else knows of any reputable contractors in Southern CT please join in. Thank you. |
RE: new heat pumps for cold temperatures
| | |
| Hi Everyone, Just wanted to let folks know that we closed on our new house and the Hallowell unit has been running like a charm. We have the 36C and 3 zones to cover a total of ~3,500 sq'. It cools quite nicely and is actually very quiet compared to our old Rheem central A/C unit. I'm looking forward to seeing how it performs this winter! |
RE: new heat pumps for cold temperatures
| | |
Hello; Thanks for all the info from everyone, this is a great thread! I am about to purchase the 4 ton Acadia to replace the oil breathing dragon in the basement ofmy 100+ yr old home in nw PA. Greengirl stated that Hallowell introduced an updated model early this year with new compressors and circutry. Could any one tell me how to identify the new unit? Is there a specific date of mfg to look for? What are the new compressors? The local rural electric coop distributes the units and quoted me $8500 for the 4 ton unit, the installer wants another $3500 for the drop in replacement. The coop stated they would sell the unit directly to me but wasn't sure how that would affect warranty. I am hoping to purchase the acadia within the next 2 weeks and schedule install within the month. Thanks for your help everyone!! |
RE: new heat pumps for cold temperatures
| | |
Our Hallowell has been in running fine since early June. There was one problem with a relay that was causing some issues of running stage one and two when it should not have, but the folks at Hallowell sent replacement parts PDQ and all has been well since! We have saved about $30 or so a month on the cooling side so far. Of course the main claim to fame has always been on the heating side, so that will have to wait to be reported. We are happy with the cooling savings but anticipate remarkable heating ones.... Our propane usage has plummeted with the new high efficiency water heater and with the Hallowell to cover the heating this winter, we will be saving so much over what our old system was costing as to be incredible. I know that we do not have extreme winters in VA but compared to what we had it will be great. I will update everyone as time goes by. The new units are all that are being manufactured since May. Whether your coop has old ones in stock and that's what they are selling, I couldn't say. If you had the specific unit number, you could call Hallowell and ask to speak to one of the techs and inquire. They are all very nice people and very much interested in customer support. The total cost of yoru deal is just a pinch above what we wound up paying and ours was a 3 ton, so I don;t think it is out of line. As far the compressors, the reason they brought out the new model was because Bristol was discontinuing the model compressor that was being used in the Hallowells. Hallowell didn't want to be caught in a squeeze play as they ran low on stock of them, and so elected to go ahead and change the particular compressor they put in their units. I can't imagine the waranty being affected by any of that. The warranty on the unit would have to be administered though who installs it, like all untis.... |
RE: new heat pumps for cold temperatures
| | |
| Thought an update on my last post would be in order.... we just received a new electric bill and the savings for this last month are are more on the order of $50 over last year. I also should add that our rates have inches up ever so slightly over last year and I did not mention that in the last post. |
RE: new heat pumps for cold temperatures
| | |
| Dear Oxford CT poster, we are HVAC contactors in Weston, CT, have spoken to Hallowell about becoming a dealer. If intersted, please contact us @ bbbn33@aol.com. |
RE: new heat pumps for cold temperatures
| | |
| My 4 ton Acadia is installed and running! So far so good... |
RE: new heat pumps for cold temperatures
| | |
| I am interested to know what the actual vent temp is going to be when its 0 outside with NO heat strips. |
RE: new heat pumps for cold temperatures
| | |
| We've fired up the Acadia a couple of times so far here in NH. We had a couple of nights where the temps dropped below 40 outside. The Acadia heated the house up no problem, but I did notice the vent temps were cool compared to the propane FHA system in our old house. I know this is to be expected. I have to say there was much less of a swing in temps between on/off cycles than what we had with the propane system. The big test will be coming shortly when the temps drop consistently below freezing outside. We have yet to receive our first electric bill, but I'll post the #s as soon as we get it for this past month. |
RE: new heat pumps for cold temperatures
| | |
How do you know when the electric heat comes on? The Acadia controls the first stage via w1, it comes on with defrost and below 15. The second stage is controlled by the thermostat via w2. If both w1 and w2 are on you get 3rd stage electic heat. However I don't think there is any indicator on the thermostat for this. Also, how does the thermostat decide to energize w1? If I select emergency heat the thermostat energizes we to the acadia. This shuts off the compressors and I guess acadia energizes w1 but this only gives first stage electric. Does any one know anything about this? So far we've only gotten down to 42. When the first stage is on I see about 82 at the first register. When the second stage is on I see about 125! Nice and toasty! We haven't seen the booster yet. |
RE: new heat pumps for cold temperatures
| | |
| Re: cpeters99 I’ll venture a guess that when your vent temp reaches 125°F, your backup heat strips are ‘on’; if so, kiss your savings good-bye! You can verify this, failing T-stat indication, by watching the rotational spin on your utility meter disk when 2nd stage is demanded. Please (someone/anyone) correct me if I’m wrong. SR |
RE: new heat pumps for cold temperatures
| | |
| I emailed my questions to Hallowell and got this reply promptly: There are no indicators for the W1 call for resistance heat. It is a 2nd stage call below 10 deg and used during defrost and emergency shut downs. The W2 is indicated by a 3rd stage call shown by the "+2" blinking. "+2" solid is a 2nd stage from the thermostat. 3rd stage is energized when the temperature falls 3 degrees away from the set point. W1 and W2 calls are completely separate during normal operation. They are 1st and 2nd stage respectively in emergency mode. When power is lost, there is a potential of the refrigerant mixing with the oil and allowing excessive wear to the compressor. After a power loss, we recommend the thermostat be put into emergency mode to allow the crankcase heaters to warm the oil and remove liquid refrigerant. If the homeowner is not present, the unit can be operated without concern. We have done multiple tests in an attempt to have compressor failure and it did not occur. This is a recommendation to insure a long life of the equipment. There is not an automatic function as the power is off and our control de-energized not allowing a timer to run. We are confident that this will not be an issue for you. Once again, this is a recommendation to insure a long life of the equipment. Please feel free to contact us with any further questions/concerns you may have. Mark C. Risinger Technical Support Specialist Hallowell International LLC 110 Hildreth St. Bangor, ME 04401 (207)990-5600 or 1-877-322-2342 Fax(207)990-5602 I'm sure when I saw 120 degrees I was in m2: second stage compressor with no resistance heat. It makes a little more sense now! |
Just asking a question...
| | |
| Just asking a question here. Has any HVAC tech reading this thread ever measured a temp of 125°F, out of a register no less, with a HP system - without the backup being on? SR |
RE: new heat pumps for cold temperatures
| | |
| Hello, One item I forgot to mention. Our local power supplier (PSNH) offers what they call a HeatSmart program. It works like this - if you have electric heat (which the Acadia is) and have an approved backup heat source (like a wood or pellet stove), you qualify for a reduced electricity rate to run your heating system (includes the Acadia unit, the blower and the resistance heat). In exchange for the reduced rate (which they say is about a 24% savings), they can shut off your electricity to your system during peak usage for a period of 4 hours. This has only happened a couple dozen times over the last several years. The bonus is that the Acadia also acts as central A/C in the summer, so that usage is discounted as well. Here's a link with more info: http://www.psnh.com/Energy/Home_Efficiency/HEATSMART.asp |
RE: new heat pumps for cold temperatures
| | |
| "Just asking a question here. Has any HVAC tech reading this thread ever measured a temp of 125°F, out of a register no less, with a HP system - without the backup being on?" - Not a tech. My air source heat pump puts out 101F air at 50F ambient, which drops to 91F air at 25F ambient. With the 15kw aux strips energized, I get >125F from the registers. Take care. |
RE: new heat pumps for cold temperatures
| | |
| Re: garyg Thanks Gary, that’s about what I expected. Re: cpeters99 If I may impose on you, for the sake of experimentation, to please turn off the breaker for the backup and to repeat the temperature measurement again at the plenum and at the register furthest away from the HP. Thanks, SR |
RE: new heat pumps for cold temperatures
| | |
| Does anyone have experience with contractors in Northern NJ for this system? |
RE: new heat pumps for cold temperatures
| | |
| Hello GreenGirl! We need to replace our heat pump in the not too distant future as it is getting some age on it. I would love to have geothermal because of the low "noise" factor (our unit is right outside our bedroom window) but am looking into the lower cost alternatives first! :) Your posts on the Hallowell products have me intrigued. How do you find the noise level compared to older model heat pumps. Mine is about 9 years old now and it's so loud it wakes me up every time it cycles on and off. BTW, we also live in Virginia. We are in the Blue Ridge mountains at about 2700 feet so it is about 15 degrees cooler than the Piedmont sections of Virginia. Thanks for any comments you may have. I would be interested in hearing from anyone who has installed one of these. Nita |
RE: new heat pumps for cold temperatures
| | |
NIta, I almost can't give you a definitive answer to your question since our unit is on the opposite side of the house from our bedroom. Except for when we are in our great room watching TV etc., we never have heard our air "conditioners". I can say that it does not seem as loud as our previous compressor for the AC either in the great room or outside right next to it. The air handler inside is DEFINITELY quieter than our old one. Standing right next to it, you almost can't hear it all. Do you have a two story house? If so, then the issue would be not so much in any case. We are in the Shenandoah Valley so it isn't bad at all. So far we are tremendously pleased both with the unit and with the Hallowell people. They have gone way above and beyond what any big company would do with questions, problems and after the sale help. They are real human beings, which is rare these days! If you want more info, you can email me at chckandco@aol.com. You can probably email or call Hallowell and get some sone ratings for the unit and then compare to the sone ratings of your present unit.....Have you visited their web site? greengirl |
RE: new heat pumps for cold temperatures
| | |
| Hi Nita, I would liken the outdoor compressor sound to that of a refrigerator in the house. There's a slightly louder noise when the compressor kicks on, but then it quiets down after a couple of seconds. Our unit is outside the back of the house and I can hear it when we're inside on the 1st floor. It's not loud enough to wake me up, though. I can barely hear it on the 2nd floor. I live in NH, so we've had some cold weather lately. I can tell you the unit heats the house nicely. Greengirl is right - the air handler is almost silent. I had to look at the system lights to verify it was on! |
RE: new heat pumps for cold temperatures
| | |
| Hi All, I just got my November electricity bill and thought I would share the change I've seen. My November 2007 bill, which was when I had a traditional propane FHA furnace for heat, was $102. My November 2008 bill, using the Acadia, was $184. Our non-HVAC electricity usage has remained the same. Therefore, I can assume it basically cost me $82 to heat my 3,500 sq' home using the Acadia from late October through late November. My propane cost was zero :-) |
RE: new heat pumps for cold temperatures
| | |
| Re: dsilvest Still sounds like a lot to me. Where are you located, what do you pay per kWh? SR |
RE: new heat pumps for cold temperatures
| | |
I installed a geothermal heat pump 2 years ago in the Shenandoah Valley, Virginia (1,700 ft el.) and love it. I had air source heat pumps in North Carolina and the noise drove me crazy when I was inside and outside the house, even with a new Trane unit. The air source units basically run continuously in the winter. My wife always complained about the cold air coming out of the registers, but not with the geo unit. The silence inside and outside is golden. Electric is 8 cents/KW with all fees included, heating and cooling is $350/yr during two full seasons. I installed a 2 1/2 ton closed loop ground source geo unit for my 2,100 sg ft house with lots of windows and a winter thermostat setting of 71 degrees. I sized it for 85% worst weather and it costs $3,000 more than a similar air source heat pump. The bids for the geo unit varied by $9,000 so get several bids. I ended up with a basic commercial WaterFurnace unit w/o bells & whistles. The geothermal units are suppose to last 20 years vs. an air source units about 10 years. Make certain to seal the duct work with mastic. I disconnect the heat strips until the weather gets really cold, then I keep a constant temp to keep the strips from coming on. The geo keeps producing heat regardless of the temp, My geo unit needs a bit of boost when the temps are about 22 degrees since I right-sized the unit to work that way. It was another $3,000 to get a larger unit which is a lot of heat strip usage compared to a total use of $350 for the entire year. A colleague has been installing commercial units for schools and hospitals for 30 years. My neighbor installed an air source heat pump and propane gas furnace unit for $10,000 more than a regular air source heat pump. I don't understand the logic. Hope this helps. |
RE: new heat pumps for cold temperatures
| | |
Hi all, My Acadia heat pump was installed in our new home in southern Maine this summer. We heat about 1300 sq ft of the house as the 2nd floor is unfinished. We have gas appliances and gas hot water. We pay .16 per Kwh for electricity, which I feel is a lot. $89.00 for Sept - October 21. $119.00 for October - Nov 21. I am not looking forward to the colder months to come but so far we are doing alright. We keep the heat set at 66. I don’t think the heat pump is the cheapest way to heat but sure looked good when oil was over $4.00 per gallon |
RE: new heat pumps for cold temperatures
| | |
| Hi SR, I'm not sure of our exact electricity rate - I'll need to check my bill tonight. We live in southern NH and actually had some snow flurries yesterday :-( In our last house, which was built in 2004 and is in the same town we are now, we had propane FHA heat. In one season I calculated that we used 1,100 gallons of propane. At minimum $3/gallon, that's $3,300 for the heating season. Take away a bit for hot water and dryer use and I figured we spent about $450-$500/month (Oct through March) for home heating. I'm still curious to see how the Acadia performs in the deep winter, but so far so good. |
RE: new heat pumps for cold temperatures
| | |
| Is your Acadia the 4 ton unit? Do you have 2 zones? I had installed in September, and received my electric bill from 10/15 - 11/15. House is 1400+ sq ft 1st floor and 450+ in second floor. Results not very good, it was 2nd highest kilowatt usage for year. The installer is coming back tomorrow to replace one of the thermostats. I've been working with Hallowell the last 2+ weeks on this. I live in Salem, NH. I'd like to get in touch with you. |
RE: new heat pumps for cold temperatures
| | |
The is a simplistic solution but make certain that in step one of the installer configuration that the thermostats are set at HP2 so that they make use of the technology that the Acadia brings to bear. Ours got mistakenly set wronglya nd for a little over a week, we had a similar experience till I reread the manual and discovered it and changed it to the correct setting (upon corroboration from Norm at Hallowell). It has been flying great ever since, with our kwh usage about the same as a normal hot day here in the summer, which is good since the naysayers were saying it would be more. I will post a more extensive explaination later. |
RE: new heat pumps for cold temperatures
| | |
| Yes I checked both when 1st installed, they were set at HP2. However one of my thermostats is a white rogers with hallowell logo and other because of shortage has the white rogers without logo. I'm told that the one without logo needs to be replaced. Installer is coming to replace. Not sure I understand why this will be solution. I keep bringing up the fact that the EWC zone panel for zone 1 does not have COM wire attached but zone 2 does. I've not received a explanation on whether this is okay or not. As you can tell by the tone of this I'm not very confident. I've been back on oil for over two weeks which I can run separately. Any help you can provide would be appreciated. |
RE: new heat pumps for cold temperatures
| | |
| Hi jimscanlon, Our house has 3 zones and we have the smaller Acadia unit (36C I believe). I think our first zone is about 1700 sq', 2nd zone is 1300 and 3rd zone is 500. Our HVAC guy just came here yesterday actually to adjust the thermostats. We found that when all 3 zones were on, the thermostats would get confused and the "Call for Service" indicator would light up on all 3. Then the system would run on just the resistance heat ($$) until all 3 zones hit their temp setting and shut off. Then the Call for Service indicator would turn off. After speaking with Hallowell, the problem is with the model of the White Rodgers thermostats we have. The HVAC guy had to come back and reconfigure them to HP1 and swap a couple of leads. So far, the issue has not come back. |
RE: new heat pumps for cold temperatures
| | |
| I strongly suggest a call to Norm or one of the other techs at Hallowell for a solution from the horse's mouth. Norm is beyond tremendous and very helpful and will know instantly what the problem is that an inexperienced person cannot. Norm, please forgive me for suggesting this but this is where you soar and can make a difference in sales! |
RE: new heat pumps for cold temperatures
| | |
Hi greengirl and dsilvest, Well my replacement thermostat got replaced yesterday, hopefully I will see an improvement. The HVAC guy and I did talk to tech support (Norm) just to make sure the install was in order. He confirmed this to be. Just so you all know I was in constant contact with Hallowell for over two weeks on my issue. If it was as simple as replacing the thermosat then I say why did I have to wait for over two weeks? This could of cost a small fortune waiting for the solution. Of course I still had not deinstalled my 3yr old oil burner since I've not found a reasonable cost solution for hot water. Does anyone know what the display indicators are on the thermostat and what they mean. The documenation and Hallowell web site does not provide this information. Such as "Stage 1". Just as a side note I see that dsilvest mentioned he had problem with thermostat. But I was wondering what the HP1 setting is. I'm only aware of HP2. |
RE: new heat pumps for cold temperatures
| | |
| Hi jimscanlon, My hallowell documentation had an insert that describes what each of the thermostat settings mean. I believe HP1 was for a single stage heat pump and HP2 is for multi-stage. Our HVAC guy had to set our thermostats to HP1 (per direction of Norm from Hallowell) and swap some leads. So far the issue has not returned. Re: hot water - take a look at Rinnai tankless units. We've used one for 4 years now and are very happy. |
RE: new heat pumps for cold temperatures
| | |
| I have mountains of stuff that I printed out when researching, which I will dig up. I know there is a chart that may have been somewhere on the Hallowell web site that show exactly what is engaged at each stage of operation. I'll post later. I wanted to find it again for myself to see how it factored in to what was going on here. I'll post later once I find it. How can a multistage heat pump work at HP 1??? Although I would imagine if Norm says so, it is. Did you talk to HIM at first,or someone else, and that might be why it took so long to resolve??? |
RE: new heat pumps for cold temperatures
| | |
| Hi greengirl, The multi-stage HP works at HP1 because of the lead-swap that was done. All the changes were at Norm's direction. He said White Rodgers had done something incorrectly based on Hallowell's requirements and that this switch corrects the issue. Norm really does know his stuff. For the thermostat settings, see page 21 on the below link: http://www.loraxec.com/media/Acadia_-_Install_Manual_-_May_12_2008.pdf |
RE: new heat pumps for cold temperatures
| | |
| I am having a 4 ton acadia unit installed in 2 weeks. my house is air tight, super efficient gold medallion home. I chose to go with the acadia over a geo thermal unit. (8k price difference). house is 3300sq ft up and 3300 sq ft down. every wall is insulated in the house and the basement has no heat at all and it stays at 53 degrees in the winter. Am i making the right decision. I am nervous and second guessing I still dont see much feedback on this unit. I am in northern ohio. thanks everyone jp |
RE: new heat pumps for cold temperatures
| | |
| Hi jp, I think you're making a great decision. I've had good luck with the unit so far. I don't think their marketing efforts have been very strong, and that's probably why you haven't heard much about them. I do think their stepping it up a bit as I've seen references to Hallowell in my last 2 This Old House magazines. -Dave |
RE: new heat pumps for cold temperatures
| | |
| Re: jp For $8k difference I think your decision not to go geothermal is seriously flawed. First of all the geothermal HP will easily last twice as long, the ground loop will last virtually forever. Secondly, when it comes time to cash out and sell you’ll get a premium for your property with a geothermal installation. Who will have heard of or care about a (then) old Acadia conventional air-source HP? IMO SR |
RE: new heat pumps for cold temperatures
| | |
| Such a hate on for the Acadia! Can you point me to the source of the life expectancy and resale value of an Acadia please? |
RE: new heat pumps for cold temperatures
| | |
| thanks for the replies, I hope im making the right decision. as far as the geothermal goes. I have heard, more horror stories than good ones about geo. the deciding factor for me was when my friend who owns a major electric company in the area, installed a geo unit. he paid more than what I was going to pay and his house is only 2800sq ft and no finished basement. he brought in the "best" and biggest geo guy who does more than anyone. the result is, he is putting in a pellet stove this year. his electric bill went up to budget 300 bucks a month. last year before geo he paid 270 a month to heat. he said it is OK. and wishes he didnt do it. the ony good thing he has to say about it is that his house is an icebox in the summer. He renovated this entire property, new windows doors insulation etc...... this is the second person i know that has invested in geothermal and doesnt care for it. the other person is my uncle, he had a problem with the loop, then a problem with his waterfurnace, it broke 2 times the first year. he wishes he put in 2 smaller units instead of one big one, for when it breaks down, and once again he said it is OK... I am looking for a realistic ROI of 8 years, on the ACADIA. if the geo hypothetically is 50 dollars cheaper a month to run, my ROI on that extra 8k I invested on geo is 13 years. the ductwork is costing as much as the acadia unit alone, so that extra 8k is a big stretch considering... thanks everyone jp |
RE: new heat pumps for cold temperatures
| | |
| Re:kvan "A recent study by the U.S. Environmental Protection Agency showed that geoexchange systems generally have the lowest life-cycle cost of all systems available today. The study also shows that geoexchange systems have the lowest impact on our environment. And consumers rank their comfort and satisfaction with geoexchange systems higher than all others. While a higher initial investment is required, the investment is paid back through low energy bills (enhancing resale value), excellent family safety, and real comfort." Source: 2003 GeoExchange Heat Pump Consortium http://www.geoexchange.org/about/compare.htm The correct link today would be: http://www.geoexchange.org/geothermal/publications/cat_view/62-fact-sheets.html Then download ‘Comparing Heating Systems’ & ‘GeoExchange Fascinating Facts’ "Geothermal heat pump systems, also known as "geoexchange," are the most energy-efficient, environmentally clean, and cost-effective space conditioning systems available, according to the Environmental Protection Agency."1 1Environmental Protection Agency, ‘Space Conditioning: The Next Frontier’, Office of Air and Radiation, 430-R-93-004 (4/93) (If you want chapter & verse) BTW: Where did you see hate? Any dissenting opinion is ‘hate’? (Typical liberal thinking!) SR |
RE: new heat pumps for cold temperatures
| | |
| I'm glad you dug up 5 year old information. Very informative. I think I'll goto a cigarette company to ask whether smoking is good for me or not. I'm sure they have a study there too. I still don't see anything specific comparing geo to cold climate heat pumps, nor do I see actual numbers. Sure it could be "the most energy-efficient", but it's not saying whether it's 100% better or .1% better. |
RE: new heat pumps for cold temperatures
| | |
| Take a trip to Europe the answer will soon become apparent. Ductless Split Systems will be the real deal sooner or later. several companies have a wall mount that looks like a wall picture mounted on the wall. Check it out. (1)No temperature loss in ducts. (2)100 percent Zone Control (3)No to little Noise (4)requires little or no additional Electrical. (5)If one breaks down you are covered by other zones. (6)Buy one per year to avoid major cash lay out. (7) Install yourself and save. (8)Remote Control (9)Very reliable (10)only requires a two inch hole in the wall. (11)No I dont sell them I am retired from the trade after 40 years in the trade |
RE: new heat pumps for cold temperatures
| | |
| I will have to pay more attention to the Hallowell booth this year at the ASHRAE/AHR show in Chicago at the end of January. Googe, Ductless certainly have the application here in the US however keep in mind in Europe, (been there 5 times), the cooling hours are limited and people are generally more tolerant of temps there because of their energy saving mindset (Electric costs are 2-4X more than ours) The picture looking units (art cool) were originally introduced by the LG group, who are Korean, nowhere near Europe. "Install yourself and save" What consumer today holds EPA certification, has gauges, freon, evacuation pump, brazing torch and recovery machine on hand? Little or no electric? what supplies outdoor unit with 220V? |
RE: new heat pumps for cold temperatures
| | |
| It is -10C(14F) outside and it is 21C(70F) and the wind is blowing off the atlantic ocean here in Nova Scotia Canada. My Hallowell 4.5 ton cold weather heat pump is heating my 3000 sqft home as it has for the past 1 1/2 years at a electricity saving of $2000. per year. Don't tell me that Hallowell cold weather heat pumps don't work because I have proven they do. |
RE: new heat pumps for cold temperatures
| | |
| Re: novascotian2008 Thanks for the update. Everybody’s air-source heat pump can still work at -10°C in Canada. Please give us the update at -25°C (-13°F). Please include whether the backup is on or not. Then I could be impressed… BTW: I’m glad it’s working well, that you’re satisfied, that you’re saving $2k/yr. and have reduced your carbon emissions. |
RE: new heat pumps for cold temperatures
| | |
| I have had my heatpump in operation for 1 1/2 years now so this is the second winter for its operation. I have experienced a number of days at -25C and my house was maintained at 21C. The suplemental heating coils in my heat exchanger are completely disconnected. I am using only the heat pump. |
RE: new heat pumps for cold temperatures
| | |
| Re: novascotian2008 If you can satisfy your stat set point at -25°C - without backup - then I am impressed! SR |
RE: new heat pumps for cold temperatures
| | |
This has been a great thread. Thanks to all for participation. I'll be very interested to get the usage data through this heating season. I worked with a number of clients this last year doing analysis for replacement furnaces. People were getting rid of fossil fuel systems and I was helping them select and size replacement heat pumps. The jobs also included insulation and air sealing as we wanted a whole house solution, so before and after costs would be misleading. In my own house, I have a high efficiency ground source heat pump. However, had the Acadia been available when I installed mine, I would have gone with it. More on why later. In working with my clients, we wanted to look at the cost/benefits of the systems being compared. These included ground source, two stage air source, Acadia, and oil furnace. The houses were modest, about 2000SF and moderately tight and insulated. Nothing extreme but not too bad after being sealed up. For the analysis, we used the bin temperature data for our region (Eastern PA) and I computed operational times/cost for each bin. For those interested, the bin data tells how many hours each season the temperature is in a narrow temperature range, typically 5 degrees. In this way, if you know the heat load of the house, and the performance curve of the heat source, you can compute the approximate operational costs and predict when backup heat is needed etc. I've verified the calculations with actual performance where the data have been available, so this is a reality-based evaluation. One of the huge problems we've had in our climate with heat pumps is convincing the HVAC contractors to actually size the systems correctly for the heating load, rather than the cooling load. Here, we need about twice the heat as cooling, so if you follow convention and size for cooling, you vastly undersize the heating system. This was done historically for single speed heat pumps so that they could properly satisfy the air conditioning requirements. Nowadays, with multi-speed heat pumps, you should size for heating, at least in our climate. That works out very well, as it allows the cooling load to be efficiently dealt with using the first stage compressor, then the heating load can be handled by the first or second stages as required. For our climate, I've been designing to get as low a balance point as reasonable for the conventional heat pumps. As noted, most HPs were undersized and so they had a balance point of about 40F. At that temperature, most of the winter around here requires the backup heating to be on, making them cost ineffective. This has been the case even with good two stage HPs. So, by pushing the balance point down below 30F, I can get their systems to heat their homes without backup heat for the majority of the heating season. To further increase efficiency, I've promoted staged electric backup. Most HVAC installers just install a 15-20kw heat strip. In fact, if you size right, you can start with 5kw down through the low 20's, then kick on the full heat strip only as needed for cold temperatures. This optimizes the HP energy use considerably. Doing everything rigorously like this is really key to achieving high efficiency out of a heat pump. The devil's in the details as they say. All that said, the attractive thing about the Hallowell is that it's designed for the heating load of colder climates. Its first stage cooling is actually half the output of the second stage. This lets you get near optimal output for the cooling season. A conventional, two-stage heat pump has about 30% less cooling than heating, so for cooler climates, you tend to be a bit oversized on the cooling side if you really push the heating output. The Acadia goes one further with the booster compressor, jacking up the heating output further, so getting the details exactly right, like with a conventional 2-stage HP, isn't quite as critical. The unit itself does the switchover as needed and the compressors are capable of handling the heat load to cold temperatures before turning on the electric backup. To me, this is a big advantage of the Acadia vs. a conventional 2-stage HP AND vs. a ground source system. More on this, as the ground source people will likely holler. In moderate and cold climates, the cooling output from a ground source system (single or two-stage) will VASTLY exceed the cooling load of the house, leading to really poor quality cooling. A single stage ground source system is even worse. If you look at the performance curves, you can verify this. Even stage one of a ground source system, when used at typical ground temperatures, outputs nearly the full output capacity of the ground source system. In a heating dominated zone, even one as mild/hot as the mid Atlantic states, you will find that a ground source system will provide sub-optimal cooling if sized appropriately for the heating loads. Even if you size conservatively, like I did, for a heating load down to about 20F, the ground source system will still blast out too much cold air for all but the hottest temperatures, assuming that you have a well-insulated home. The Acadia, on the other hand, will provide a much better air conditioning capacity, and a conventional HP will provide decent AC. The other issue with a ground source system is that even the best installers have to balance operational efficiency with installed cost. In our region, very few go open loop, which is the most efficient configuration, due to maintenance issues. Instead, they go closed loop, vertical boreholes. I've had a half dozen clients get quoted on this configuration in the last 6 months. For a ground source system, 3-5 tons, the bore drilling cost was in the $12k-$15k range and the ground source system itself cost about the same, depending on model. So the installed cost was typically $25k-$30k for a retrofit application (existing ducts, new variable speed air handler, compressor, and drilling). For these homes, winter projected operational costs were very low, in the $350-$500 range under optimal conditions. Keep in mind that these are approximate costs in the expensive mid-atlantic region. But I've talked to numerous people and this is a very typical installed cost around here. Now, getting back to my previous comment about balancing install cost with efficiency. Because well drilling has gotten so expensive, they're teaching ground source installers to install less bore hole depth. I attended a ground source workshop recently, given by the leading ground source consultant and college in the region and they were endorsing quite short boreholes, but noting that the seasonal ground temperatures would suffer. For example, while ground source systems are spec'd at about 50F loop temperature, as the season progresses, the ground temperature drops or rises, due to a variety of parameters (water table movement, ground conductivity, system run time etc.) As such, with these shorter ground loops, you have to actually plan for ground temperature of around 32F during the winter and 80F during the summer (again, this is very dependent on the exact system operational parameters). But these are very typical parameters. For some real-life numbers, I installed temperature probes on all the boreholes in my ground source system, and within the first month of hard winter operation, the ground temperatures dropped below freezing and stayed there for the rest of winter. So, in REAL LIFE operation, many ground source systems are operating at temperatures that are at or below the outside air temperature, so their COPs drop considerably. Instead of 5 you might get 3 or lower. The one positive thing is the there's no defrost cycle. That's the big win for these systems. You never have to deal with the cold blast every hour when the system goes to defrost like you do with an air source system. These are the things that ground source advocates either don't want you to know or don't know enough to know themselves. But keep that in mind. If you install a closed loop ground source system with typical loop configurations, your performance will be vastly lower than the numbers may indicate. So back to air source systems. In this climate, our winter air temperature may vary from 25-40 in Nov-Dec and drop to 15-30 for Jan and feb. Again, you look at the bin temperature data and it tells the temperature distributions through the year. Comparing a top of the line two stage HP with the Acadia, you find that the conventional air source systems are really efficient! They maintain a high COP. Take a four-ton system running at 30F. The system runs at a COP of almost 3.5! Even at 20F, including defrost cycle derating, the COP is above 3.1. So a modern, two-stage air source heat pump really performs. This is actually much better than the COP of the Acadia, so when I've done my cost analysis, these systems, which around here cost about $10k installed, have operational costs of maybe $750-$850/winter. This includes backup electric heat strip requirements. As it turns out, in this climate, the Acadia is about the same operational cost, with a quoted install cost of $14k-$16k. As noted, the Acadia has some benefits however. You don't have to be as rigorous about the sizing because it has more stages and is able to pump out the heat without the electric backup. The delivered air temperature is higher than the conventional HP. And the summertime load match is better than any other system. So, in this climate, when you run the numbers, you find that the air source heat pumps cost $300-$500 more to run per year than a properly installed ground source system for an installed cost of $10-$15k less. The ground source might last 20 years, while the air source is typically rated at 15 years (not 10 like was earlier mentioned). So, if you're looking at pure financial figures and a 10 year time scale, you get: Ground source, closed loop: ~$30k Two speed air source: ~$18k Acadia: ~$22k Again, this is for a typical mid-Atlantic state. The colder the climate, the more the balance can shift to ground source and Acadia. It also doesn't take into account the comfort issue. Ground source - no defrost, more even heating, oversized cooling. Conventional air source - defrost cycle cold blast, heating drops more with temperature, moderately good cooling. Acadia - not sure about defrost cycle, heating increases with decreased temperature due to booster compressor, excellent cooling. Sorry to overwhelm with all this information. But this is a topic that I've been analyzing/studying for some time now and I wanted to get it out there for others to share. |
RE: new heat pumps for cold temperatures
| | |
| Can anyone out there explain to me what the following reading on my Acadia thermostat is. STAGE 1+2 (+2 is blinking) I'm seeing it a lot when the temperature drops. It is about 18 degrees farenheit right now. Thanks, |
RE: new heat pumps for cold temperatures
| | |
tedsan, thanks for that post. This has been a most informative thread. |
RE: new heat pumps for cold temperatures
| | |
| Hi jimscanlon, I believe your thermostat is saying your 2nd stage compressor is operation. It sounds like you have a slightly different thermostat than I do, but mine blinks "System On +2" when the 2nd stage is on. Also a note - I had noticed the system was running almost all day over the last couple of days. The set temperature was maintained, but I found it odd. I called Hallowell and they said this was normal and actually preferred since a constant run is less wear and tear on the compressors than a frequent start/stop. |
RE: new heat pumps for cold temperatures
| | |
| Hi dsilvest, Do you have total kilowatts usage on your last bill? Yes your thermostat readings are different. You may want to check about the blinking. When mine blinks on the +2 it is using resistance heat. Also, I have my email address posted. If you would send me email, I can send you all the correspondance I've had with Hallowell. Since you are in New Hampshire we would have lot in common due to same weather temperatures. Merry Christmas, Jim |
RE: new heat pumps for cold temperatures
| | |
| I signed up just to post on this thread. I have a lot to say about this. I try to buy American i.e. USA manufactured but I went for Fujitsu ductless heat pump for central Calif. Why can't Americans make this great product, works down to 0 F which we never see here, very efficient, quiet, makes it's own three-phase to be efficient, 19 SEER, makes it's own variable frequency drive AC for it's motors, silent, inexpensive, a dummy like me can install and charge it, remote control does it ALL. A FABULOUS product. max size 30KBTU. Never need to revert to resistive strip heating. Appears bullet proof like a 1987 Fujitsu DMP printer I've used for decades. come on America! |
RE: new heat pumps for cold temperatures
| | |
"Ground source, closed loop: ~$30k Two speed air source: ~$18k Acadia: ~$22k" Wow. My 3-ton 14 SEER, 9 HSPF, Goodman heat pump was installed last summer for less than $4k. Single speed Copeland scroll compressor. 10 year all-parts warranty on the system. I could get 4 to 7 systems for the prices quoted above. To each his own. Take care. |
RE: new heat pumps for cold temperatures
| | |
| Hi, I've been sitting back waiting a couple months before I say anything about my new Acadia. I got my electric bill today and since the system was installed on 10/10/08 I have used approximately 3,000 kwh to heat my home. November and December have been quite cold with a week of temps in the teens before xmas, dropping as low as 0. I live in Erie, Pa in an old 2100 sq ft home. I was running the full system, with 3 auxillary resistance heaters, but the middle of december I shut them off, running totally on the heat pump through the coldest weather. The system had no problem heating my home to 65 at night and 68 to 70 (usually 70) during the day. The only real problem when it gets that cold is the defrost cycles become more frequent and blows quite cold without the resistance heaters. Anyway, my electric is relatively cheap here at 9 cents per kwh so it looks like I've spent about $270 to heat my home so far this season!!! This is a great improvement over fuel oil, even at todays abnormally low prices!! |
RE: new heat pumps for cold temperatures
| | |
I live in southern maine, heat 1300 sq feet of new constuction with the acadia. Electric bill for Nov - Dec $220.00 Not bad, but the heat pump started blowing cold air when the temps warmed up to 45-50. Had to shut the power off at the breaker to reset the system. The unit started heating again. I have found the acadia to be very tempermental which worrys me when five year warrenty runs out. |
RE: new heat pumps for cold temperatures
| | |
| Does anyone with an acadia have a problem with icing on the outdoor unit coils in extended cold temps? It's been 20 and below for the last 2 weeks and my acadia shut down because the coils were iced solid about 10" up. I'd noticed the performance decreasing lately but didn't realize why. It seems to defrost properly but can't melt the thick ice that refreezes immediately. It works good after I defrosted it with a torpedo heater, but I wouldn't think I should have to do this. My dealer said it may be necessary in cold temps!?!?? |
RE: new heat pumps for cold temperatures
| | |
Contact Hallowell directly. They've got some incompetent installers, so I'd only trust what Hallowell tells me directly. Clearly the guy who you're working with doesn't know what he's talking about. Hallowell extols the virtues of the unit for working in frigid temperatures. Chances are, the installer didn't properly charge the system (fill it with "refrigerant"). If under-charged, it will freeze up too quickly. If they service it, tell them that you want to keep a log of the "superheat" and "subcooling" numbers. Any time the system is serviced, insist on these numbers for your log. When you call Hallowell, ask them for these numbers. good luck! |
RE: new heat pumps for cold temperatures
| | |
| With a torpedo heater my Tempstar could probably produce good temps down to zero or so. Maybe get two and I could have a two stage! Ok all kidding aside.. I hope they get the bugs out of the Acadia because the design is intriguing. I hope they get your squared away in short order! Best of luck, |
RE: new heat pumps for cold temperatures
| | |
| I asked my installer about the refrigerant charge and this is what he said: The charge is 12 pounds of R410A for the system and 10’ of lines + .6 ounces per foot for additional line lengths. We do not test super heat or sub-cooling on a new Acadia system start-up. We do on any other heat pump or AC system we install. The Acadia system is unique in that it does not come with any refrigerant from the factory, only a nitrogen charge. Per Hallowell instructions (told to me from Duane Hallowell himself), we weigh in the R410A charge according to the manual and start the unit, no further testing is required. Testing super heat and sub-cooling verifies proper charge. We always run these tests on any other system because we do not take for granted that the factory installed the right amount or that some has not leaked out by the time we get the units. With Acadia systems, we would only test sub-cooling afterwards if we suspected a problem with the refrigerant system. Does this sound right because they treat me as if this were my fault! |
RE: new heat pumps for cold temperatures
| | |
| I live in the NE (burlington, MA) and I'm spending close to $600 per month on oil + about $140 per month on electricity for the winter months to heat my home of about 2200 SQ FT. I have forced hot water baseboard heat and I've been thinking about the acadia as well others (freewatt, geothermal, redo current install, electricity only). Are there any websites out there that collect monthly utility charges for customers of various heating technologies? I think that before I make a decision to change out my heating system, the first think I want to look at are facts about monthly heating that a number of people are experiencing using the different technologies. |
|
|
|
|