blower motor comes on by itself

Posted by elalbino63 (My Page) on
Fri, Oct 14, 11 at 17:52

hi:
strange but it comes on at odd times by itself. I replaced the thermostat it still does it. so i removed the thermostat and with the bare wires sticking out it comes on by itself. stays on for 5 min or so. I had an ac guy look at it but he said he cant do anything unless he is there when it comes on. it comes on sporadically. oddly seems mostly at night. there is a vent by my bed so it blows on me. its a little irritating but its wasting electricity too. first post here and thanks!!!


Follow-Up Postings:

 o
RE: blower motor comes on by itself

I suspect the timer that controls the blower.
Give some more details about the system.


 o
RE: blower motor comes on by itself

its a gmc furnace located in the basement. its prob 30 years old. if I can provide any info let me know. I am including a pic of it if that helps and thanks!!

Here is a link that might be useful: furnace


 o
RE: blower motor comes on by itself

I'm not familiar with that furnace, but the blower function is somewhat generic. The timer runs the fan for a set period after the thermostat is satisfied.
On a unit that old the device may even pre-date solid state and not be part of a circuit board. That may make isolation and testing easier.
A tech replaced my electronic one for ~$50 parts/labor. Like you say, it was a waste of electricity.


 o
RE: blower motor comes on by itself

"On a unit that old the device may even pre-date solid state and not be part of a circuit board. "

Older systes used time delay relays that contained the timer.


 o
RE: blower motor comes on by itself

I guess its not as old as I thought. It has a solid state board and is marked on the decal 1993. its really filthy on the inside. should it be blown out with compressed air? the GMC model number is as best as I can read it GMP100-4 Rev 8 or B. The tech the home warranty sent out replaced a part that made the heater come on but said he couldn't do anything about the fan coming on. he wasn't that great he left the drain tube unhooked, the filter half-way in and cut connections inside the unit instead of throwing them away in the trash can right next to it. I guess Ill call the home warranty people on monday. he did get the heater going though. any thoughts?

I also noticed it has 2 fans a small one above maybe to exhaust CO? It and maybe the big lower one comes on when the door in replace and stays on a few minutes. is this normal? if not it may be a way a tech could check it since he said it had to be on when its not supposed to be before he could fix it.

I took some pics of the inside here is a link to the album.
thanks!!!!

Here is a link that might be useful: furnace pics


 o
RE: blower motor comes on by itself

My thoughts are that if you aren't going to troubleshoot and do this yourself that you should call an HVAC tech and not a generalized individual. A good tech can test the blower circuit live or dead. The fan should run when the unit fires.
Dirt isn't good for components or connections. If you blow it out how will you know you're not forcing dirt where you don't want it? Use a vacuum with a brush. Be gentle around components. Many synthetic materials become brittle after long term exposure to heat.


 o
RE: blower motor comes on by itself

On many older furnaces, the fan control is electromechanical, no electronics, and located in the hot air plenum above or adjacent to the heat exchanger. It is not unusual for such setups to shut off the fan after a heating cycle and then for the residual heat in the heat exchanger to cause the fan to cycle on again for several seconds.
Sometimes the burner high limit control is combined with the fan control.


 o
RE: blower motor comes on by itself

"its really filthy on the inside. should it be blown out with compressed air?"

Using a shop vac (possibly with some smaller extension nozzles) is a lot better than driving the filth further into the equipment.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Heating & Air Conditioning Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here