| We have a good number of posts here that have to do with residential humidity control. We have discussions about blower speed control as a mechanism for that. We have occasional posts about whole house dehumidifiers. So far, I have not seen anything to do with desiccant wheels, but was advised by a manufacturer several years ago that they are not practical for residential scale use.
In commercial and manufacturing situations, overcooling and reheating is done all the time as some of you know. I daresay that it is being done in the building I am sitting in right now. The question is, in residential situations, why can't very conventional existing mechanical cooling systems coupled to existing gas furnaces be used to overcool and then reheat to provide comfortable temperature and humidity? Is because there will be too much heating capacity that can not be effectively throttled, or some other engineering aspect. Is it just that there has not been the demand to develop proper controls? It may not be the most efficient way to do it in a lot of areas where demand for this kind of conditioning is high. In other areas, it might be useful for the limited times where low cooling loads are concurrent with very humid conditions. Of course, a second "condenser" could be added to the indoor air handler for reheat and that would be more energy efficient at the cost of added equipment. |
Follow-Up Postings:
|
| You can do that but other concerns such as proper sub cooling temps remain at coils, compressor slugging, cold weather operation and others. Since you have to generate heat to offset the cooling effects of dehumidification, your much better off using a central ducted dehumidifier.. I have one like this mounted in the attic connected with 14" ducts with an intake and exhaust on open second floor. Mines a desertaire, but same type. http://www.aprilaire.com/index.php?znfAction=ProductsCat&category=dehu mid |
Here is a link that might be useful: Central dehumidifier
|
| "In commercial and manufacturing situations, overcooling and reheating is done all the time as some of you know. " At a large increase in operating costs and maintenance complexity. Large commercial installations have a full time building engineer available to keep things running. Can you really afford that? |
|
| "You can do that but other concerns such as proper sub cooling temps remain at coils, compressor slugging, cold weather operation and others. " Would that be so hard to avoid with the correct electronic controls? "At a large increase in operating costs and maintenance complexity." Already covered, really. How would it be more expensive than a new, separate refrigeration system with both hot and cold coils in the air stream? Cost of operation would be extra gas and electricity on humid days rather than just electricity on a dedicated dehumidifier. We all know that gas is cheap right now. The question is, what is so technically difficult about running both heat and cooling at the same time for short periods? |
|
| "Would that be so hard to avoid with the correct electronic controls? " The typical controls do not measure or take into account the problems you will encounter. "How would it be more expensive than a new, separate refrigeration system with both hot and cold coils in the air stream?" Typical residential cooling systems are not designed to operate below about 50F outside temperature. If liquid coolant returns to the compressor it can be instantly destroyed. An often significant difference between these larger systems is the presence of an accumulator tank for liquid refrigerant, and a separate control loop to keep that tank filled. Industrial air systems are far more complicated than just cascading two separate systems together. |
|
| Thanks for looking. "If liquid coolant returns to the compressor it can be instantly destroyed.
" "The typical controls do not measure or take into account the problems you will encounter. 
Ever seen a residential system with a pressure sender?" What problems? Why would I need a pressure sender? "Typical residential cooling systems are not designed to operate below about 50F outside temperature." Then it can't do what I want below 50F, or maybe 55 so shut it off/lock it out. Won't likely need dehumidification at that temp anyway because that is heating weather. "An often significant ... freeze up. Industrial air systems are far more complicated than just cascading two separate systems together." I'd like to try again. Lets ignore the complexities of industrial and commercial HVAC systems which is irrelevant to the question. I can ask this in two ways. Why can't I run a residential HVAC system, that is conventional beyond some minor control changes, with both the mechanical cooling and the gas furnace running at the same time? I obviously can not do that with a conventional thermostat because they won't heat and cool at the same time. To make the question even simpler, why shouldn't I "hot wire" my furnace to run while the thermostat is in the cooling mode and the cooling part of the system is operating normally? |
|
| ""If liquid coolant returns to the compressor it can be instantly destroyed.
" How are daisy-chained heating and cooling process going to cause liquid to return to the compressor? " If the entering air is not warm enough to evaporate the refrigerant in the evaporator you can 'slug' the compressor. It is your money and your time. It is NOT done the way you describe for the reasons given and plenty more. But you are obviously better than all the HVAC engineers that create these systems. Let us know how it works out after a compete set of seasons. |
|
- Posted by energy_rater_la (My Page) on Thu, Oct 18, 12 at 18:12
| LOL! @ brickeyee ionized might be that deadly combination the heater is physically in the wrong place. this makes my head hurt just to keep pondering ionized! |
|
| Brickeye, I know that there are a lot of people that know more about HVAC design than I do so I ask for help in understanding. Up to now, I have only seen hand-waving and no reasons why it can not be done. Why not explain why it can not or should not be done? "If the entering air is not warm enough to evaporate the refrigerant in the evaporator you can 'slug' the compressor." One reason that I can think of that would make it not practical with existing systems is that I think the air flows through the furnace first and then the cool coils. Although that would preclude slugging, it would make for very inefficient dehumidification. If the system were turned around so the air were cooled first, it should work. Can the return air in a residence be too cool and cause slugging? If so, a simple control addition would prevent that by locking out the compressor if the temp a the return was below desired temperature. |
Please Note: Only registered members are able to post messages to this forum. If you are a member, please log in. If you aren't yet a member, join now!
Return to the Heating & Air Conditioning Forum
Instructions
- You must be a registered member and logged in to post messages on our forums.
- Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review the contents and make changes.
- After posting your message, you may need to refresh the forum page in order to see it.
- It is illegal to post copyrighted material without the owner's consent.
- HTML codes are allowed in the message field only.
- No advertising is allowed in any of the forums.
- If you would like to practice posting or uploading photos, please visit our Test forum.
- If you need assistance, please Contact Us and we will be happy to help.