Help Needed for a New Gas Pack and Duck Work

orchid1961
11 years ago

My 13 years old Carrier gas pack has just died out. We live in Raleigh NC where heating is generally needed for 3 winter months while cooling is needed over 5-6 summer months. We got quotes from 4 contractors and three proposal calls the Trane XL16c/XL14c unit, one proposal recommends the Carrier Performance Series 48VL-A.

A few years ago, we added in a room of 210 sqft, the load calculation indicates that we need to up the HVAC from 2.5 T to 3T, therefore, the supply and return ducks need to increase from 16" to 18". Since the new room is situated at the far end corner of the house, it is always warmer/cooler than the rest of the house. In the current duck design, there are two supply boxes, the primary box (16" duck delivers air to 1300 sqft) is fed from the gas pack and the second box is fed from the primary box (12" duck delivers air to 600 sqft).To improve the heating and cooling of this room, a couple of proposals call for an additional supply box that gets fed from the gas pack with manual damper to distribute air directly to the two existing supply boxes. I think this design may improve and give the secondary supply box a little more juice and eliminate the delay. Is it worth it the effort? Cost wise, since the primary supply box needs to be replaced to accommodate the 18" feed, it may not be too expensive to go with the new design.

My questions are:

1. Do we really need to increase the supply and return flex ducks to 18" given the fact that the unit may operates in the 1st stage most of the time. It is my understanding that running in the 1st stage, the unit only uses 2T, so there may not be adequate pressure to push the air thru the 18" duck.

2. In the new design, the main duck splits into 14" and 12" branches, again running in 1st stage, there may not be adequate pressure to push the air thru the 2 branches to cool or heat all rooms especially the new room.

3. From the above facts, should I stay with the plain single stage 3T gas pack?

Please help as I'm trying to understand the merits of the proposals in order to make the right decision.

Comments (5)

  • orchid1961
    Original Author
    11 years ago

    I forgot to mention that a couple of proposals stated that we do not need to retrofit the existing duck work since the HVAC will be a 2-stage unit.

  • ryanhughes
    11 years ago

    While the duct modifications add to the total cost, they are necessary. 18" round supply and return would be ideal. 16" round HARD pipe would be minimal for a 3 ton. Flex duct adds some resistance, and it usually isn't run very straight which inhibits flow even further. I'm assuming the ductwork is flexible, which is fine. But it needs to be installed properly and sized correctly. The ductwork should be sized for high stage. Low stage capacity will be around 75% of high, give or take depending on the particular unit you go with. So on low stage, the system will still want to move 900-1000 cfm. This isn't "too little" for 18" ducts. The system will run quieter and more efficiently with properly sized ductwork. Some of the newer variable capacity units have a much larger range of airflows depending on demand. Hope this answers some of your questions.

  • orchid1961
    Original Author
    11 years ago

    ryanhughes, thank you for your help. In your opinion, on low stage, the 18" duct is properly sized for the 3T 2-stage gas pack. Do you recommend going with the new duct design where the main 18" duct is splitted into 14" and 12" branches? Again I'm concerned that these two combined ducts are oversized for the 3T gas pack operating on low stage. I'm more comfortable with the new design operating with a single stage gas pack.

  • ryanhughes
    11 years ago

    In my opinion, the 18" flex duct for supply/return is properly sized for a 3 ton gas-pack system period, 2-stage or not. Again, it is not proper to size the ductwork based on low stage.

    I checked the fan performance table on the 3 ton XL16c. At 400 cfm/ton, on high stage it will move approx. 1200 cfm and on low a bit less than 850 cfm. Heating airflow is a bit different but in the same ballpark. I assume they quoted the model with 75k heat input. I strongly doubt you require the 96k model.

    I'm not sure I'm clean on the duct system setup. So you'll have 18" flex coming off the packaged unit, supplying one primary distribution box which branches off to two other boxes with 12" and 14" flex ducts? I'd rather see properly sized metal, rectangular (matching unit openings and transitioning as/if required) supply and return trunks coming off the unit with appropriately sized branch runs rather than flex duct everywhere, but what you describe is not all that uncommon. I don't see an issue with the 12" and 14" flex duct from a size perspective on either high or low stage. There is no "maximum" or "minimum" airflow a duct can handle, but with 1200 cfm or less, assuming the ducts aren't badly kinked, the static pressure and friction should be within reason.

    Are you certain they did a Manual J load calculation? Have you seen the results? I question a 210 sqft addition adding half a ton to the cooling load, unless it's all glass. Many homes have systems that are already oversized. So 2.5 ton may not be "undersized" even with the addition, but a load calc will tell for sure. Of course, 2-stage systems come in full-ton sizes, but proper sizing of 2-stage systems is still critical. An oversized 2-stage system will spend just about all of its time in low stage, acting as an expensive single stage system.

    I wish I could type more but have to leave. Hope this helps and doesn't add more confusion.

  • orchid1961
    Original Author
    11 years ago

    ryanhughes, again thank you for your help. Black flex ducts everywhere are what I see in the crawl space! I'll try to ask the contractor about the metal rectangular supply and return trunks as part of the new duct design. I did not see the Manual J load calculation, but I was told that the first floor is 1900 sqft, the second supply cube covers about 600 sqft. All the contractor claimed that the first floor needs more than 2.5 T but the builder rounded downn to 2.5T to keep the cost down. They also say that most of the time, the unit operates on low stage and only ramps up to high stage in extreme temperature days. Therefore, I wonder whether I should get a single stage unit like the current system.