Heat pump question: compressor or defrost control?

Posted by wannabeDIYer (My Page) on
Sat, Oct 8, 11 at 0:23

Hello,

Parents have an American Standard Heritage 10 heat pump, which they've used pretty sparingly over the last three years (last homeowner installed it around 1998??).

It recently stopped cooling and heating. The first contractor who came by thinks the compressor kicked the bucket. The second contractor who came by thinks the compressor is A-ok and the defrost control board is shot.

Don't know anything about heat pumps but it seems to me that these are pretty different diagnoses!! Is there anyone who might tell me how to figure out who is right?

Many thanks in advance.


Follow-Up Postings:

 o
RE: Heat pump question: compressor or defrost control?

Find someone who can at least put some gauges on the thing.

A failed compressor is easy to find.


 o
RE: Heat pump question: compressor or defrost control?

agree

Need another opinion from an experienced HVAC pro/dealer who knows HPs preferably a Trane or AmStd dealer.

IMO


 o
RE: Heat pump question: compressor or defrost control?

Thanks for the very prompt advice.

What's confusing is that both contractors put gauges on the thing--and both were licensed HVAC servicemen, although neither were American Standard dealers.

I guess I'll go to the horse's mouth and call out the local dealer for Am. Std., although that company has a mixed reputation and charges for a service call.

Thanks again.


 o
RE: Heat pump question: compressor or defrost control?

Trane is the same product if you have a good Trane dealer.

What's "kicked the bucket" about the compressor? Locked up? Not pumping? Shorted? This isn't rocket science. All the defrost board does is pass the "turn on" signal to the compressor. Really easy to tell if that is keeping the system off.

Last year I went on a call that one of 2 compressors in a high end Trane was locked up. It was til I put a high voltage wire back on the terminal it was supposed to be on. Popped right up. Thieves.


 o
RE: Heat pump question: compressor or defrost control?

Thanks for info.

"Kicked the bucket" = the compressor just isn't starting up.

Contractor who initially thought the problem was just the defrost board now thinks the problem is both the defrost board AND the compressor and wants to replace the whole heat pump.

Getting third opinion tomorrow; hope I find someone like y'all!


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Heating & Air Conditioning Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here