Trane 16xli + Oil Boiler Control

Posted by RaminVA (My Page) on
Fri, Sep 7, 12 at 22:39

Hi all,

I live in a 80-year old 2-story single family home about 1900 sq ft in central VA. The entire house is heated by an oil-fired boiler + baseboards. We currently have 2 15-yr old a/c units -- one in each floor to cool in the Summers.

I am replacing the two a/c's with heat pumps. Trane 16xli for the 1st floor and Trane 15xli for the 2nd floor. The idea is to use them in Fall and Spring when it is milder outside (is that a good idea?). The plan is to activate the boiler and baseboards on colder days.

I would appreciate any advice on how I can integrate the a/c units (or at least one on the 1st floor) with the oil fired boiler into one thermostat. The Trane dealer tells me that any thermostat that is not Trane will void the warranty. His recommended Thermostat the TCONT803 according to him can be wired with the 1st floor a/c unit so I can switch to boiler manually but the fan on the air handler will have to run at 50%. Does anybody have a work around? OR can you a recommend a thermostat that can do this seamlessly?

Thank you and appreciate the responses.


Follow-Up Postings:

 o
RE: Trane 16xli + Oil Boiler Control

I am not an expert for your setup, but I will offer some comments.

I have never heard the Trane warranty will be voided if you don't use their thermostat. The Honeywell Vision Pro thermostats are used frequently with Trane equipment. Call Trane if you want to get an answer on this.

I assume you have a thermostat for the boiler? Then my suggestions is to lock out the two heat pumps and the boiler at a set temperature. For example if you determine you want the set point to be 35 degrees, the two heat pumps would be locked below this temparature, and the boiler would be locked out above this temperature. You would need thermostats which have an outside temperature senser. I am not sure if the Trane TCONT803 has this feature. Others on this forum can comment on this.


 o
RE: Trane 16xli + Oil Boiler Control

Right now, my downstairs thermostat (Honeywell 7-day programmable) controls the down stairs a/c and the boiler. Sometime in the Fall, I switch over to heat and just use it for the boiler. Works fine.

I want to do something along the lines mike_home suggests -- depending on the outside temperature, the system chooses he heat pump or the boiler. When in boiler mode, I want the HP/air handler "off" -- presumably the newer Honeywell thermostats can do that?


 o
RE: Trane 16xli + Oil Boiler Control

The Honeywell Visionpro IQA thermostat with an outside temperature sensor should be able to accomplish want you want to do. It would lock out the heat pump and enable the boiler at a specific outdoor temperature. You should also lock out the upstairs heat pump at the same temperature.

It sounds like this contractor only wants to work with Trane thermostats. Trane may have an equivalent theromstat, but I am not aware of it. I also don't understand the comment that the air handler needs to run at 50% if you switch it manually. Do you have confidence in this contractor?


 o
RE: Trane 16xli + Oil Boiler Control

The contractor is highly rated (on Angies list). They were very professional; did a detailed Manual J; looked through my electric/fuel bills to see what sort of system fits, etc. I assumed Trane was imposing such constraints.

Trane has a t-stat the Comfort Link II which I believe can do what you suggest --but is pricey and charges $8.99/ month for Wifi enabling it. Something like the Honeywell Prestige series does everything it does so perhaps that is the route to take...


 o
RE: Trane 16xli + Oil Boiler Control

RaminVA,

You do not have to use a Trane t-stat. The use of any other t-stat in no way voids any warranty from Trane.

The 50% fan thing he is talking about however is correct. Trane xl16i requires a variable speed air handler that will only run at 50% with a call for continuous fan. There are easy ways to work around it though if you know what you are doing.


 o
RE: Trane 16xli + Oil Boiler Control

Thanks, harlemhvacguy. The systems are going to be installed next week. I might as well install a t-stat that integrates well. Any recommendations on the t-stat? Or is the workaround something I can do (via the operating system) after installation?


 o
RE: Trane 16xli + Oil Boiler Control

It can be done in the setup of the thermostat. They will have to set it up as a dual fuel with back up heat as gas with furnace( boiler in your case) controlling the fan. in this case no fan. The tcont803 and tcont402(non programmable ) will both do this as well as many other honeywell t-stats.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Heating & Air Conditioning Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Please review our Rules of Play before posting.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here