To figure out the right size a/c unit...try this method

Posted by robar (My Page) on
Thu, Sep 13, 12 at 19:17

I saw this on the internet. Take the square footage of your home and multiply it by 25, then divide this amount by 12,000. This will tell you the size (ton) you will need for your central a/c. Example....2000 sq ft. home multiply by 25 equals 50,000 divided by 12,000 equals 4.16. You would need a 4 ton unit.


Follow-Up Postings:

 o
RE: To figure out the right size a/c unit...try this method

I don't think so.

I've got a 2000 square foot home and it has a 3 Ton unit that is sized properly.


 o
RE: To figure out the right size a/c unit...try this method

Loads are a factor of many many things, and doing the math is the only way to know that the load is correct.

Using square footage doesn't account even for 8 foot or 10 foot ceilings. That alone would alter the volume of air by 20-25%.

Not to mention, R value of insulation, east and west windows. skylights, and building materials.


 o
RE: To figure out the right size a/c unit...try this method

Robar...that exactly what every installer in my area uses to quickly determine the equipment people need.

This is completely wrong and you end up with the wrong equipment about 80% of the time.

This is the lazy way of doing it to make a quick sale.

Take a look at this free online Manual J calculator to get an idea of all the factors that go into calculating loads: http://loadcalc.net

I'm not affiliated with the site...I just found it and learned to use it. It took me a few days, but it really helps you understand what's the appropriate BTUs for your house for cooling and heating.


 o
RE: To figure out the right size a/c unit...try this method

This is also called the 500 sq. ft. per ton calculation. This is wrong and leads to oversized equipment.


 o
RE: To figure out the right size a/c unit...try this method

there is a reason you spend the money for the
software to correctly do a load calc.
rule of thumb sizing causes a LOT of problems.
for homeowners.
hvac companies make more money by selling
larger equipment..with shortened lives due to
excessive stop & starts..utility companies
profit in that it causes more to start up the
unit than to run it for long lengths of time.

its bs OP.

a bit more classy than standing across the
street and holding up fingers to cover house
and using that as guide for sizing..but bs none
the less.

do a search for load calcs, manual j, s, d....

best of luck


 o
RE: To figure out the right size a/c unit...try this method

+1, the 500sqft per ton is obsolete. Newer homes can do 1,000sqft per ton in southern climates.


 o
RE: To figure out the right size a/c unit...try this method

If two twin 2000 sqft houses in said southern climate are built next to each other by the same builder using the same materials, but one house was built with no insulation in the walls, no insulation in the attic, and no insulation on the floor and the other had R38 in the attic, R15 in the walls, and R11 in the floor, then their cooling and heating needs would be different.

So, we are trying to raise awareness that using sqft per ton is obsolete regardless if you use 300 sqft/ton or 400 sqft/ton or 1000/sqft per ton. They are all obsolete...do the load calculation.


 o
RE: To figure out the right size a/c unit...try this method

SO how do you know whats right?? I have 2 estimates for central a/c. Both for RHeem units. I have a 2 floor colonial with 35 windows. 1st fl - 2300 sq ft 2nd fl 1700 sq ft. I have 2 pretty different estimates. #1- says I need a 3 ton and 4 ton. #2- says I need a 4 ton and either another 4 or 5 ton. He is going to do more calc and get back to me. I have oil baseboard heat. no ducts yet.


 o
RE: To figure out the right size a/c unit...try this method

The load calculation (Manual J) takes into account a lot of factors like insulation, windows on east/west facing walls, sqft, doors, type of floor, climate, volume of house, doors, appliances, people in house, and so on.

So, a Manual J calculation will spit out your cooling and heating needs in BTUs and this calculation is far more useful than the 400 sqft/ton lazy way of estimating. This is how you know you have the right sized equipment.


 o
RE: To figure out the right size a/c unit...try this method

I'm sorry I don't mean to b a PIA but if I live on Long Island with a family of 5. 15 windows west 20 windows east. Avg insulation. Im worried b/c I know the size of unit is very important and I got 2 different opinions. All bedrooms (4) and 2 baths upstairs. I like to sleep in cold a/c my DH makes fun of me I'm trying to freeze him like Walt Disney. LOL


 o
RE: To figure out the right size a/c unit...try this method

Both estimates could be wrong. You are getting estimates of 7 - 9 tons for a 4000 sq ft house. This seems oversized unless you have poor insulation and windows.

In general contractors will tend to oversize in order to play it safe when there is no existing AC.


 o
RE: To figure out the right size a/c unit...try this method

OK I don't have existing a/c so I guess that could be why. I gues I'm worried because everyone on the forum seems to say getting the correct size unit is very important.


 o
RE: To figure out the right size a/c unit...try this method

Getting the correct size is very important. This is why you need to ask a lot of questions of the contractor.

You have a big old house, so it is easy to make a lot of incorrect assumptions. I suggest you have the contractor show you the load calculation print out. Make sure he has accurately entered the dimensions of all rooms and windows. Ask what assumptions have been used for insulation and air infiltration. Find out what software he is using. If he can't answer these questions or won't show you the results, then a load calculation was not done.

When you have some data start your own thead with an appropriate title.


 o
RE: To figure out the right size a/c unit...try this method

Thanks for the great input. I will certainly post results.


 o
RE: To figure out the right size a/c unit...try this method

I keep reading on forums that a load calc is needed. I have talked to 2 HVAC places that said they would not do a load calc. Finally the 3rd place I called the boss told me he would do one for $450. Maybe in middle Tennessee HVAC people
feel like it's a waste of time. I will keep trying but I understand why people don't get a load calc.


 o
RE: To figure out the right size a/c unit...try this method

Here I had to get a Load calc in order to get the permit. There was no separate charge for it.

YMMV

This post was edited by saltidawg on Tue, Aug 20, 13 at 17:10


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Heating & Air Conditioning Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here