| I am replacing a split HVAC system that handles the main floor + a 15x19 room and bathroom in the basement for a total of approximately 2000 square feet. The entry and family room are vaulted ceilings. The old unit was a 3 ton 19 year old Carrier system that had always seems at least adequate in performance when working properly. I typically shut the exhaust vents in the basement during the summer since it was usually cool enough without them open. The estimates I received were mostly all 3 ton replacements of various brands based on my satisfaction with the old unit. However, two companies did load assessments and the weird part is that one told me it should be a 2 ton and the other said it should be a 3.5 ton! I tend to think the 2 ton is grossly undersized and wonder if the 3.5 ton might be too large? Anyway, here's the suggested unit based on the 3.5 ton load:
Trane XL16i 4 Ton 2 Stage, Trane XV-80 80K 4 Ton 2 stage variable speed 2 stage furnace. Does this sound like a reasonable sizing and solution? The home is in the Atlanta area and windows are all single pane except for a french door to the deck. There is another 3 ton unit handling the upstairs but also 19 years old.
|
Follow-Up Postings:
|
- Posted by tigerdunes (My Page) on Wed, Sep 7, 11 at 18:06
| Cw I don't like that sizing at all for heating and cooling. Basement finished areas at or partially below grade normally have low heating and cooling loads depending on insulation properties. Heating a main floor beneath a second floor is not as great either. Of course, you have vaulted ceilings in one area of the main floor. I agree a two ton is probably too small but the idea of a 4 ton seems oversized. Back up and thoroughly review carefully before making a decision. IMO |
|
| Thanks for your input but I wanted to clarify a bit more. The figures from their load assessment indicated: 96920 Btu Heating 44010 Btu Cooling Based on that, the suggested 4 ton unit makes sense doesn't it? I mean there isn't a 3.5 ton unit so if a 3 ton AC is 36,000 Btu then it would be 8,000 Btu short and the 4 ton at 48,000 Btu would be the only choice although 4,000 Btu overkill. |
Please Note: Only registered members are able to post messages to this forum. If you are a member, please log in. If you aren't yet a member, join now!
Return to the Heating & Air Conditioning Forum
Instructions
- You must be a registered member and logged in to post messages on our forums.
- Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review the contents and make changes.
- After posting your message, you may need to refresh the forum page in order to see it.
- It is illegal to post copyrighted material without the owner's consent.
- HTML codes are allowed in the message field only.
- No advertising is allowed in any of the forums.
- If you would like to practice posting or uploading photos, please visit our Test forum.
- If you need assistance, please Contact Us and we will be happy to help.