2 stage A/C questions

Posted by attofarad (My Page) on
Thu, Sep 29, 11 at 15:49

My most likely installer has quoted a Carrier system with options for either a 5 ton 24ABB compressor or a 5 ton 2-stage 24ANB760A003 compressor (for $950 more). In either case, I would be combining with a 120kBTU Carrier Infinity ICS 58MVC120F120, or maybe the 100kBTU version, Infinity controllers, etc.

How do 2-stage compressors work? Are they sorta like the furnaces, where they run a lower amps, BTUs and lower blower speed? I can't find specs in the A/C for output on low on the Carrier site, like that I can find for the furnace, or any description of system operation.

The system will be zoned, so I'm hoping to be able to cool only 1-2 zones while running on low A/C, and have the blower running at low speed to match.

I've lived in this house 22 years with no A/C and no huge need, but my new wife runs hot, and likes to work out. Since I'm doing a total furnace/duct tear out and relocate, it is now or never. Also, an extra 0.5% in overall house price to have A/C will maybe make it easier to sell, and cost be recouped.


Follow-Up Postings:

 o
RE: 2 stage A/C questions

Okay, I found the info in the installation manual. The 2-stage scroll compressor has solenoid control of valves. When the valves are open, some of the gas which would be compressed is dumped from the first compression pocket back to the low side of the compressor, thereby decreasing the displacement and capacity.

Which brings me to a related question. When the A/C compressor is on Low, the expansion coil is effectively quite oversized. The Infinity controller should slow down the blower to match the load. Generally speaking, what is the disadvantage of having a coil larger than necessary?


 o
RE: 2 stage A/C questions

An oversized evap coil (such as 3 ton with a 2.5 ton condenser) will have a lower temperature than the smaller coil. This favors sensible cooling (temperature) at the expense of latent (humidity) removal.

In your case, when the staging is low, the airflow should be adjusted to provide the same (approx) sensible heat ratio (in effect, adjusting the coil temperature).

Intentionally using an oversized coil to increase SEER without considering the sensible and latent cooling needs (by way of a heat calc) seems amateurish. Consult the mfg's product specifications.

V


 o
RE: 2 stage A/C questions

It is very common for Carrier legal combinations to allow an oversized coil. I have this in my house. I have a 2 ton condenser with a 3 ton coil, and a 3 ton condenser with a 4 ton coil.

If you choose a Carrier Infinity 2-stage condenser you will still have good humidity control with an oversized coil.


 o
RE: 2 stage A/C questions

Mike, do you know if your blower speed is set up for 350 CFM per ton, rather than 400? I had an Infinity quote which was specified with an oversized coil and contractor noted that speed was 350/ton.

It sounded counterproductive to me. Can any PROs respond?

V


 o
RE: 2 stage A/C questions

According to the Carrier product data sheet for my condenser (24ana7) the blower speed in the high stage is 350CFM per ton in the high stage, and about 235CFM for the low stage. The bulk of the dehumifying will be done in the low stage.

The Infinity furnace or air handler has a variable speed electronically controlled motor. I don't think the installer sets any speed. The controller sets the air flow based on the equipment connected to the system. In addition the fan will increase the RPMs in order to reach the correct CFMs for high or low stage.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Heating & Air Conditioning Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Please review our Rules of Play before posting.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here