| About 2 years ago I improved my ducting by tying it down, tightening joints then sealing with mastic and metallic tape.
Last week, a duct test revealed ~14% leakage (just under our Code/Reqs). The local vendor can install new ducting that targets 9% or the top-line at 6%. They are going to run numbers for me on costs/benefits. 1) Would you consider 14% a poor/adequate/good job for a DIYer? I'm wondering if there are points of leakage out of my control, such as within the gas-pack or the sheet metal interfaces between the roof. 2) If I slightly increase tonnage (+0.5) on new HVAC, I may replace it all anyway (vs. just increasing return and a few new supply lines). Outside of that decision, would you think it's worth upgrading ducting to gain a 6% improvement just on its own? It's probably going to run a couple/few thousand. Opinions? As always, thank you for volunteering your time.
|
Follow-Up Postings:
|
- Posted by veesubotee (My Page) on Mon, Sep 5, 11 at 17:03
| Hmmmmm. I would be a little suspicious if the tester wants to sell you the ductwork job. Ask yourself, "what makes type A ductwork better than type B"? Or, is the difference in the quality of his workmanship. No duct should grossly leak if one takes the time and trouble to do a quality job. You need to do some of your own testing. Go to a hobby store and buy a thin wooden dowel (about a yard long). Take a facial tissue and cut a strip (longwise) about an inch wide and tape the end to the end of the dowel. Turn your blower on high and with the 'telltale', probe around every accessible joint and along seams. Don't forget the tops of trunks and also the returns and filter housings. Supply leaks will cause the flag to blow; return leaks will suck in the flag. Maybe your leak rate isn't as bad as was reported. You would have to have a lot of holes to rack up that leak rate. Is your current unit a 4 ton unit? Don't know if there are any 4.5 ton units. Why do you want to increase tonnage? Has a documented heat calculation been done? If your current ducts can't deliver the air, you will make matters worse. Good Luck. V P.S., disclaimer: I am not a PRO. |
|
| Thanks for the suggestion, I'm always suspicious of the test/sell approach. But my original ducting is supposedly horrible compared to the newer stuff (I think the minimum code is R6). I researched tight ducts before hand and do believe they are as good as they claim and I do trust the company that tested would install correctly. About testing myself: I did that when I originally sealed it myself. There were no detectable leaks (which are EXTREMELY obvious in a still, dusty, 130F, attic when I'm all sweaty) at any joint and all the outer grey plastic was undisturbed. More than half the joints I sealed and taped are now buried in lots of cellulose insulation, so not an easy thing to get at now. I watched them take the readings and do the math to obtain the 14%. >>> You would have to have a lot of holes to rack up that leak rate. That's the part I'm looking for guidance on. That would SEEM true, but I'm pondering there must be a large acceptable threashold for "non-leaking" ducts if new ones are only 9% and the top-lines are 6. |
|
- Posted by SkyHeating (My Page) on Wed, Sep 7, 11 at 11:28
| 14% is not bad, its just not good either. There are naturally going to be places that you just can not seal and being a DIY project you may have missed areas that you did not know how to access or that you should seal them. What I am VERY curious about is why are they upsizing your system? It is common practice to downsize after sealing but if your system is working well now, why make it larger? this will just cause more problems. |
|
| The instrumentation device can easily be 10% in error. 14% of total air flow. Two areas to check, but difficult. Under the ceiling grills. And inside the return air intake. Have a HERS Rater give your house duct leakage test. You can us a smoke test also. Pressurize your duct system with stage-smoke [ u can rent these at the rental store and a leaf blower [electric] ..blank off all the vents with 3 in painters tape, the beige color professional, Sherwin Williams ..blue is too expensive. blow it into the return vent...will need some cardboard and duct tape to attach. Good Luck...oh bty, if you have floor vents, inside, under the floor grill ..will need mastic or mastic butter. |
|
- Posted by energy_rater_la (My Page) on Wed, Sep 7, 11 at 14:04
| 14% leakage is not bad. average new construction leakags minimums often start at 30%. diy ductwork is not rocket science. concentrate on return, and supply boxes. make sure your paint on mastic is water based |
|
| Chuckfh: >>> The instrumentation device can easily be 10% in error. >> HERS Rater give your house duct leakage test. >>> floor vents, inside, under the floor grill ... need mastic Thanks for sharing! |
|
| Energy_Rater_LA: >>> average new construction leakags minimums often start at 30%. >>> it is just the degree of difficulty to get to them. So I made sure duct was secure & used plastic/metal ties as needed. I spread ~1/4" thick grey mastic on *every single* connection where flex duct attaches to a boot, reducer, or the plenum. Two boots were difficult as two sides touched framing and ceiling sheet-rock, so my application was messy and lacking on just those two. The only exception: A 20' chase holds the 14" flex duct travels through the living room (raised plant shelf). I packed insulation around both of the attic-side openings and also cut out a 1'x1' hole so I could examine the ducting from the interior (of course I put a hinge on the removed sheet rock & applied weather stripping to make a tiny sealed door). >>> remove supply grills use mastic tape to seal Thanks for the answer and tips. |
|
| Skyheating: Thanks for the reply. A man J was done 18 months ago (when I knew nothing of home heating/cooling) that recommended I go with 4ton, but they said "maybe 3.5ton". Come to find out that particular vendor is shady and was trying to oversell me on a $10k unit (without upgrades to the ducting). So I can't trust the man-J results either. If I increase from existing 2.5 to 3 ton it would be for additional supply vent to a walk-in closet and to increase maybe an inch on duct into a particularly hot bedroom and increase it in the living room with cathedral ceilings. These are my opinions at this time but I'm not installing anything until I get my home audit done, then work with an hvac company I can trust that will advise me correctly on the sizing, ducting, and I'll pay for another man-J to confirm it. By then, I'll have actual duct and home leakage numbers to plug into the software. |
|
- Posted by energy_rater_la (My Page) on Fri, Sep 9, 11 at 10:02
| Already done, except I used spray foam to fill gaps between the boot and the sheet-rock. Why not foam and what should I do now? why not foam..because it isn't an approved hvac product. you can't easily remove the foam now but you can I do a lot of ductsealing. after so long I can achieve the 5% that my state's efficiency program requires. look for hardcast brand #1402 mastic tape best of luck |
|
| Just so I know I'm explaining this correctly, here is what I'm referring to. This is a bedroom vent above the door next to the drop ceiling hallway. If you click to see the detail, the foam is visible on the bottom gap. I only did a tiny strip of foam from the interior. I did NOT apply mastic on the Boot to Sheetrock from the attic side. Is that where my mistake was? Or can I just go around on the interior and apply the mastic tape? |
|
- Posted by energy_rater_la (My Page) on Fri, Sep 9, 11 at 20:08
| I'd go from the interior with the mastic tape and cover the foam. but make sure the tape will be covered by the grill..it is next to impossible to get off once it sticks. you did a neat job, I just worry with foam looks like they blew the drywall finish with best of luck |
|
| energy_rater_la: OK will do. That won't take me more than a few minutes per vent. >>> looks like they blew the drywall finish with the supply boxes uncovered..huh >>> your boxes must be insulated on the exterior? Thanks for all the contributions folks. Very helpful in a few different ways. |
|
- Posted by countryboymo (My Page) on Tue, Sep 20, 11 at 23:44
| I had places on my boot to floor areas that had over an inch of gap and the only thing I could think of at the start of sealing before I knew about mastic was foam. I later went over the foam which had shrank away but only had 1/8" gap or less and gave everything a double coat of brush on mastic. It is a lot of work to seal each individual connection you can get to but a small leak here and there adds up quick. I had like 400 register cfm of return air at the start of my ductwork rebuild on a @1200 cfm 3.5 ton system. The rest was being sucked out of the attic and basement. I don't remember my supply numbers but they were stupid low also. |
|
| My house was built in 1950. The duct system leaked badly until we got after it with mastic and tape. My HVAC contractor buddy mentioned my old rigid ducting He went on to say the 'new' flexible ducting is MUCH easier to install so all the HVAC companies say it is 'better' because it is a faster install. Here in California the regulations require that a different company test the duct system for leaks (it can not be the outfit which installed the heating/cooling system) Thoughts? |
|
- Posted by energy_rater_la (My Page) on Sat, Apr 21, 12 at 12:59
| Here in California the regulations require that a different company test the duct system for leaks (it can not be the outfit which installed the heating/cooling system) this is a good practice imo. wish we had those standards in place here. flex people diss hard pipe here is my experience. most hard pipe that is unwrapped has dust marks hard pipe is more expensive, and is wrapped flex does have more resistance to air flow, pros and cons for both. try to avoid the companies I test both types, unsealed hard pipe leaks both can be well sealed. just takes the want to do so. best of luck |
|
- Posted by energy_rater_la (My Page) on Sat, Apr 21, 12 at 13:07
| "I had places on my boot to floor areas that had over an inch of gap..." always remove ceiling/floor/wall registers and seal you'd be amazed at how much leakage there are at these |
|
- Posted by countryboymo (My Page) on Sun, Apr 22, 12 at 13:17
| There are also some new caulks that will expand and contract huge amounts and will stick to about anything which in this application would be awesome. |
|
| I just replaced the unit and was able to investigate the transition area in the roof. The new unit is a Coleman 2stage 16/14(s)eer DBYX-F036D110 (ecm/scroll), and I upgraded my return vent from 14" to 18" and added a new supply vent -- everything is still in balance. So before, my duct leak rate was 14%. But the 3rd party test (who said he "calibrated yesterday") shows it's now only 6%! And BTW I still haven't gotten around to putting tape on any of the registers! I did notice quite a few gaps up inside the transition area/adapter when the old unit was pulled off. Just what I had suspected in the OP -- the majority of the leaks were probably in that area, which I couldn't get into. Before they dropped down the new unit, they applied reflective/sealant tape everywhere indicating they made more effort to seal it up well. Of course I was standing over his shoulder and talking the whole time about how much effort I put into sealing everything ;-) Thanks for all your replies |
|
| >just takes the want to do so. < Les Miles influences us all, eh energy_rater_la? :) What is this mastic tape you speak of, and what exactly does it attach to? I guess it must stick to the drywall to get a seal, and I guess it would be the surface drywall within the area covered by the register? I used caulk around a few ceiling penetrations with really bad gaps in my house, but I haven't done the supplies. I've also thought about using the soft DAP foam-in-a-can. Any thoughts on that? Any problems with condensation around these sealed supply boxes? |
|
| >>> I guess it must stick to the drywall to get a seal, and I guess it would be the surface drywall within the area covered by the register? Yes, that was the idea. As far as mastic tape, I don't know the brand names but even the bigbox stores carried a couple types: the plain alumin foil w/adhesive, and the foil tape with a thin film of what looks like mastic (dark grey stuff that will conform into smaller spaces and remain somewhat flexible). Not sure what he'll say about condensation, but very little worry in my area. However for whatever condensation already develops between the boot/attic layer, I doubt sealing up the small gap between the register boot and the drywall would make matters any worse. If so, there are bigger issues or other implementations for tackle that problem. |
|
- Posted by energy_rater_la (My Page) on Sun, Jun 24, 12 at 14:37
| this is how I seal supply boxes. hardcast brand mastic 1402 tape. foil tape fails, hardcast with black condensation on grills was how this don't use foams. they exacerbate rather best of luck |
|
| Thanks for the picture and tape recommendation. I asked about the condensation because someone said somewhere it could be a problem because without the attic air infiltration, the register got too cold. I was kinda doubtful about that. |
|
- Posted by energy_rater_la (My Page) on Mon, Jun 25, 12 at 7:07
| I have to admit..had to google Les Miles... |
Please Note: Only registered members are able to post messages to this forum. If you are a member, please log in. If you aren't yet a member, join now!
Return to the Heating & Air Conditioning Forum
Instructions
- You must be a registered member and logged in to post messages on our forums.
- Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review the contents and make changes.
- After posting your message, you may need to refresh the forum page in order to see it.
- It is illegal to post copyrighted material without the owner's consent.
- HTML codes are allowed in the message field only.
- No advertising is allowed in any of the forums.
- If you would like to practice posting or uploading photos, please visit our Test forum.
- If you need assistance, please Contact Us and we will be happy to help.