HVAC Plenum and Duct Design

Posted by db4570 (My Page) on
Wed, Sep 26, 12 at 11:11

I'm making some improvements to my noisy and undersized ductwork, and seeing big improvements to the areas I have done so far.

The next step is to install a correct plenum and ducts to a family room that is over a crawl space, which has a very inadequate system. My plan is to used insulated flex duct, connected directly to the furnace plenum, starting at 10" diameter, and running it through this space, wyeing off 6" ducts for individual registers along the way, and reducing the diameter of the main plenum along the way. Similar to the attached picture. The rest of the house is supplied by a traditional rectangular main trunk off the opposite side of the furnace plenum.

I'm trying to follow good duct design practice as I've learned by reading, but something mystifies me. In a rectangular trunk installation, we are told never to install a branch duct off the very end of the trunk, but when I see diagrams of reducing trunk systems, there is a takeoff off the end.

What exactly is the reason for not taking a branch duct off the end of an extended plenum? And why does this rule not seem to apply to a reducing trunk layout? I want to do this right, assuring the best airflow and least noise.

Any opinions?

Thanks!

David


Follow-Up Postings:

 o
RE: HVAC Plenum and Duct Design

no pic attached.
you don't tap off the end of the supply plenum
because it reduces static pressure.
as the air enters the plenum it hits the end cap
if a duct is taken off the end cap the total pressure
is reduced.

also you don't tap off the plenum within 18" of the coil
not sure why...but just one of the things I was taught
in class.

10" to tri box then 6"? you sure about those sizes?
6" is usually a bathroom. do you have a ductalator to
know how many cfm of air each size duct can move?
this along with room size determines how much cmf
to provide. then you can divide it between two ducts.

that pic would help.

make sure you mastic seal all duct take offs, where
flex connects to supply boxes, where supply boxes
penetrate floor & plenum to equipment connections.
duct leakage in a crawl space creates a lot of problems.

best of luck.


 o
RE: HVAC Plenum and Duct Design

" don't tap off the plenum within 18" of the coil
not sure why"

You do not want to increase flow velocity over the coil.

It reduces effectiveness and efficiency.


 o
reRE: HVAC Plenum and Duct Design

Uniformity of flow can also be disturbed.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Heating & Air Conditioning Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Please review our Rules of Play before posting.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here