| HELP... SOMEONE MUST KNOW HOW ZONES SHOULD BE SIZED!!
We obtained two quotes to install a new zoned system. Both quoted the same equipment: AC: Carrier 24ACB7 (2 Ton 2 Stage)
Although we considered an Infinity system we can't afford the nearly 40% premium this added to the pricing. Both firms used Elite's RHVAC for sizing which calculated gains & losses as follows: ________Area___-____Loss____-____Gain___-_Heat_CFM_-_Cool_CFM_-_Design
_CFM
**** Option #1 ****** The first firm sized the ducts as calculated by the software (Elite's RHVAC) with no oversizing. They explaned that the software takes everything into account and sizes the ducts correctly without needing to adjust the cfm for the zones. Any excess airflow is handled by a bypass connecting the supply to the return which opens when the pressure in the ducts gets to be too high. They are proposing installing the following trunks for each zone: __________CFM____-_Duct_Size_-_Notes
Bypass 8x16 - Loop between Supply and Return **** Option #2 ****** The other company claims that the software treats the entire system as if it wasn't zoned and that it is necessary to increase the size of the ducts in order to get the system to work properly. He explained that zoned systems should be designed such that bypassing isn't necessary and to achieve this goal each zone must be designed to handle 60% of 1st stage blower capacity less an allowance for closed damper leakage. He explained that this is calculated as follows: 1st Stage = 670 cfm
Which results in the following zone sizing requirement: ________Zone_CFM_-_Duct_Size_-_Notes
He explained that although a bypass technically would not be required with this design that his preference is still to install one simply to protect the equipment should a damper fail leading to a condition where the furnace is running but all zones are closed. Since the bypass is akin to a pressure relief valve on a boiler he indicated that his preference is to just dump the excess air into the room the furnace is in rather than looping it back to the return air. ***** Option #2 - Upgrade #1 ***** He then explained that although the above sizing which he said was 'by the book' would work, considering the huge peak solar gain in the sunroom he would prefer to increase the size of this zone further such that it is sized to handle the full 600 cfm of the 1st stage to avoid the system getting noisy when only the oone zone was calling. However, this would slightly increase the cost of installation for the larger duct. ***** Option #2 - Upgrade #2 ***** He has suggested that we may wish to consider rather than doing this by adding the additional two registers required off a single resized trunk that instead a second damper be used. His reasoning is that he feels that if sized for 600 cfm that in winter (when only 200 cfm is required by the room) that the velocity at the registers would be too low to ensure proper mixing (the room is 25x25 with 11' cathederal ceiling). The downside (and reason he is leaving the decision to us) is that this would add a significant additonal cost to the system. Who is right with regards to sizing ducts within a zone? Do either of the 'options' presented by the 2nd contractor make sense? THANKS!! |
Follow-Up Postings:
|
- Posted by david_cary (My Page) on Mon, Aug 8, 11 at 19:25
| I couldn't read all that. You definitely want to go bigger with zoning. I have an Infinity and despite its controls, I am having to add extra ducts/vents in because of noise. I always think you want to go big on these things so you have the ability to damp down some areas. |
|
| What is 2nd stage cfm delivery? 800 cfm for 2 tons. what happens when any one zone goes high stage. with no damper bypass the velocity will be extreme.Ive done it both ways. oversize duct by 60% is great for 2 zone application but never tryied it on 4 zone. Im all about efficiency and hate bypass for this reason however you must accept bypass rather then problems with noise and velocity.that 8x16 bypass is wayy to big and I would go 8" round ( 400cfm) The smallest zone 350 cfm +byass of 400 = 750 . carrier moves air at 350 per ton so 700 cfm wil be ok. I would check to see what 2nd stage heat cfm is gonna deliver as well. |
Please Note: Only registered members are able to post messages to this forum. If you are a member, please log in. If you aren't yet a member, join now!
Return to the Heating & Air Conditioning Forum
Instructions
- You must be a registered member and logged in to post messages on our forums.
- Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review the contents and make changes.
- After posting your message, you may need to refresh the forum page in order to see it.
- It is illegal to post copyrighted material without the owner's consent.
- HTML codes are allowed in the message field only.
- No advertising is allowed in any of the forums.
- If you would like to practice posting or uploading photos, please visit our Test forum.
- If you need assistance, please Contact Us and we will be happy to help.