| In June 2012, I replaced my 10 yr old compressor and handler and always seem to be sweating in my house since the change. I've had the new AC contractor come out 3 times since the install and I just don't understand why I "feel" so hot when all the temp settings are the same as with the old unit. The first two visits, they said the R410 needed to be topped off a little and the 3rd time, they said all refrigerant levels and pressures were right to specs. This is driving me crazy 'cuz I live in FL and even when wearing shorts and a tank top in my house, I'm wiping sweat from my forehead regularly. I keep my 3 zones in the 75-77 range, as I did with my last system. My thermostat reads that the temps are right on, but it just feels like it's not pulling anywhere near the humidity out of the air as the old system did. Here are some specifics:
Old unit: Carrier 5 Ton, 10 SEER, R22, 3-zone, variable speed handler New unit: Amana 5 Ton, 15 SEER, R410, 3-zone, variable speed handler Other possibly pertinent info: The unit I replaced is for my downstairs area, which is about 80% of my total living area. I also have a 2 1/2 Ton Carrier system for my upstairs and the downstairs and upstairs handlers sit side by side. The new AC contractor looked at all my duct work for downstairs and said that my downstairs handler wasn't getting enough air supply and he recommended increasing the air flow. He did this by cutting a hole between the supply cavities between the two handlers. What I'm wondering, though, is if the new 5 Ton unit is now pulling too much air from the supply ducts that used to be just supplying the 2 1/2 Ton upstairs unit, I've definitely noticed that it's a lot more comfortable upstairs since the change, but way less comfortable downstairs. I'm no AC expert, but I'm a pretty intuitive DIY guy and I think this may be the root cause of my humidity issue. The new AC contractor told me these two things: 1) While the industry officially says they're the same, contractors know that R410 systems pull less humidity out of the air than R22 systems; and 2) Just crank the air down an extra 4-5 degrees occasionally to pull out the humidity, then put it back to my normal comfort area. Any thoughts on how to improve my humidity situation? |
Follow-Up Postings:
|
- Posted by veesubotee (My Page) on Thu, Aug 30, 12 at 15:30
| I am not a PRO, but would like to throw out a comment or two. The ability of an a/c system to reduce humidity is dependent on the temperature of the evaporator (inside) coil. With the emphasis on 'higher SEER' (larger coils) these days, a higher SEER coil of the same capacity will have a higher (hotter) temperature, and thus will condense less water. Airflow is also a factor. Most units are run with an airflow of 400 CFM per ton. This will produce an expected degree of performance with respect to sensible (temperature you can feel) and latent (humidity) capacities (removal). Your home's heat gain profile may require more latent capacity than is being delivered. If so, the airflow can be adjusted (approx 350 CFM/T) to increase latent capacity. By the same token, some contractors may adjust the airflow higher (> 400 CFM/T) to achieve a higher SEER. In such a case, humidity removal will suffer. Five ton units have special needs with respect to return air. I will refrain from commenting on your situation. V |
|
- Posted by bus_driver (My Page) on Thu, Aug 30, 12 at 17:23
| HVAC is not my trade. It seems to me that it is not the trade of your new contractor either. But he might be a politician. Moisture in the air does not "recognize" which refrigerant is in the system. |
|
| You house has 7.5 tons of cooling. How large is the downstairs and upstairs in floor area? Have you measured the humidity in the house? If so what are the readings? What is the typical times of the downstairs air handler? How minutes is it on and how many minutes off? The comment about R410 pulls less humidity than R22 systems is nonsense. I have a R410 AC and I can get the humidity down to 38% without too much difficulty. |
|
- Posted by energy_rater_la (My Page) on Thu, Aug 30, 12 at 19:43
| It sounds like high RH inside to me. I have 410 also. can you close off hole between r/a that air leaks in return contribute to high humidity. Mike-home I wondered same thing. how big is your house? best of luck OP. |
Please Note: Only registered members are able to post messages to this forum. If you are a member, please log in. If you aren't yet a member, join now!
Return to the Heating & Air Conditioning Forum
Instructions
- You must be a registered member and logged in to post messages on our forums.
- Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review the contents and make changes.
- After posting your message, you may need to refresh the forum page in order to see it.
- It is illegal to post copyrighted material without the owner's consent.
- HTML codes are allowed in the message field only.
- No advertising is allowed in any of the forums.
- If you would like to practice posting or uploading photos, please visit our Test forum.
- If you need assistance, please Contact Us and we will be happy to help.