Your Opinion on this Recommended System

Posted by twlkp76 (My Page) on
Sat, Aug 11, 12 at 12:09

I need to replace my 20 year-old, 4-ton heat pump. My local utility did a heat loss calculation for my home and says that I need a 3.5 ton heat pump with 12.5 kw heat strips.

This is the system suggested by a contractor.

Is this setup good, or should I ask for something else?

18 SEER
York Affinity series - Model # YZH04811C (4 ton)
Indoor unit Air handler - Model #MV20DN21C
Variable speed ECM motor 5 ton
Coil: Model # FC64D3XN1 - Full coil, 5 ton
TXV kit, electric heat kit (13kW)
Programmable Thermostat (York - YTHX9421R5051)
Honeywell RedLink Internet Gateway


Follow-Up Postings:

 o
RE: Your Opinion on this Recommended System

Location?

What size heat strip do you have now? 13 KW is a little light for a 4 ton especially during a defrost cycle to temper the air.

Looks like AHRI matching number #3540158.
Excellent performance/efficiency numbers across the board.

Has demand defrost which is great!

IMO


 o
RE: Your Opinion on this Recommended System

Pacific coast. Fairly mild climate, temps running averaging between 37-76 through the year. Some years it does snow (occasionally over a foot). Temps have gotten to 0, but actually rarely get as low 10, and at the other end not very often are they over 90.

I wondered the same thing on the heat strips. I believe that I was told the power available for old strips was 20kw.

Is the thermostat one you are familiar with?

Thanks!


 o
RE: Your Opinion on this Recommended System

I would want a 15 KW at the minimum staged in 5 KW increments or perhaps 2 7.5 KW strips. Discuss with dealer.

Thermostat mdl number looks like a HW VP IAQ model which is one of the best. Verify with dealer.

IMO


 o
RE: Your Opinion on this Recommended System

Thank you very much for your help.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Heating & Air Conditioning Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here