Change over valve setting

Posted by langle1033 (My Page) on
Mon, Aug 17, 09 at 10:55

In Honeywell Vision Pro 8000 (TH8320U1008) setting menu, I have to select either cool (=0) or heat (=1) for the change over valve.

I have a heat pump with electric backup (upstair) and a heat pump with gas back up (downstair).

Please tell me how to setting this parameter for each unit.

Thank you


Follow-Up Postings:

 o
RE: Change over valve setting

It differs by manufacturor. Who makes your two units?


 o
RE: Change over valve setting

Both of my heat pump units are Goodman.

Thank you


 o
RE: Change over valve setting

You should select 0. The reversing valve needs to be energized in cooling.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Heating & Air Conditioning Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here