Condensation/Drip from Air Handler in Attic

lpennington
11 years ago

I replaced both A/C units in our 16 yr old house within the past year: one handler in attic and one in basement as well as both outdoor units. Today we had a high of 84 (not much compared to the rest of July) and when we went to give our kids their bedtime baths, the ceiling in the bathroom had a water spot and the wall was water damaged. I went into the attic and looked at the large pan under the unit. It was not overflowing, but there was moisture underneath it.

I do not have the model information on hand, but I am fairly certain that our HVAC company recommended a system with more capacity. We rarely have the attic unit on all day, even during the weekends (shouldn't matter imo) but today it was on from approx. 3:00 pm until we noticed the water damage at approx. 8:00pm, however, it was off from 11:00am thru 3:00pm...

I took the below video which may or may not help provide any insights into this:

http://www.youtube.com/watch?v=4LLD59U0brU

Is this just a "sh** happens" kind of thing? Or we have planned better with our HVAC installers for this? This has never happened before with our old unit. Thanks in advance.

Comments (12)

  • brickeyee
    11 years ago

    Any unit in an attic should have an emergency backup drain pan.

    If there is water in the backup pan it means the main pan (inside the air handler) has a clogged drain.

  • mike_home
    11 years ago

    How can a one year old installation already have a clogged drain line? This is unaccepetable in my opinion.

    This may have been leaking since the day it was installed. It now has gotten to the point that you are noticing the water damage. Your installer needs to fix this and install a back up drain pan. I would want a cut off there is any type of overflow problem.

  • lpennington
    Original Author
    11 years ago

    Mike_home, I was also thinking, "how can something be wrong already?" Now I know that (1) water should not be in the pan, and (2) the pan is not holding the water that does find it's way in there (the pan was not overflowed yet water still escaped).

    Presumably this is a warranty issue?

  • mike_home
    11 years ago

    This is a bad installation issue. I assume your contractor will cover the labor and materials for the first year. The contractor needs to correct the problem and install a back up in case this happens again.

  • ionized_gw
    11 years ago

    Are "back up" drain pans in attic units required by building codes?

  • lpennington
    Original Author
    11 years ago

    Well, the tech just left and he said the condensation drain/piping was installed backwards and the water backed up from that point. No charge for the visit.

    We'll see what they say for the 1 foot wide spot on the bathroom ceiling or the wall I'll have to repaint. But at least the big number is out of the way.

    Thx so much for responding to my post. Just having someone respond really provides some peace of mind during the hours between discovery and when the pro's arrive.

  • juliekcmo
    11 years ago

    If you got a new roof or attic insulation, that can sometimes allow debris to get into the drain.

  • energy_rater_la
    11 years ago

    what did the company say about the water
    on the plywood service area?

    did you show them or mention to them the
    water stain on the ceiling?

  • lpennington
    Original Author
    11 years ago

    energy_rater. They haven't said anything yet. The tech who came out simply mentioned that there's paint to cover that sort of stuff! I am writing a letter to be mailed with a request that (a) we are compensated for the damage or (b) be given the next year's service maintenance plan for free ($350 value).

  • energy_rater_la
    11 years ago

    please let us know about the type of paint
    the tech refers to.

  • mike_home
    11 years ago

    Zinsser cover stain primer works well. I have used the alkyd version and not the latex. One coat usually covers a water stain. You then need to coat it with the ceiling paint.

  • brickeyee
    11 years ago

    "Are "back up" drain pans in attic units required by building codes?"

    At least by some.