No CO, Yet Room Causes Headache/Dizziness

Posted by Sahmmy (My Page) on
Wed, Jul 9, 14 at 19:49

On occasion I sleep in the guest room when hubby is snoring. Perhaps a few times a year. I keep the door closed to keep out our several pets so that I can get a good night's sleep. Recently I slept there, and woke with a headache and dizziness. When I left the room, the headache and dizziness disappeared. This has never happened before. I thought maybe there is a CO problem, but there is a Kidde Nighthawk CO alarm in that room, that showed "0". Just to be sure, I bought a brand new Kidde Nighthawk CO alarm for the room, and it too showed "0". I slept there again just to see if it would happen, and again I woke dizzy.

Nothing has been changed in the room in the way of new paint or fabrics or anything. The only thing I can think of is that it's summer so we run the A/C with the fan on the "On" setting rather than "Auto" to keep the cool air circulating around the 3-story house. The last time I slept in that bedroom, we were still on heat which we leave on the "Auto" setting. Could the constant blowing air have something to do with the headache/dizziness? There is a return register in that room. I am stumped, and wondering if you guys might have some advice.

This post was edited by Sahmmy on Fri, Jul 11, 14 at 21:56


Follow-Up Postings:

 o
RE: No CO, Yet Room Causes Headache/Dizziness

Put your husband in the room for several nights and see if he suffers any ill effects.

IMO


 o
RE: No CO, Yet Room Causes Headache/Dizziness

I suggest setting the thermostat to auto for a couple of days and then sleeping in the room. If you have no headache or dizziness you will know running the fan constantly is causing the problem. If that is the case, then whatever is affecting you is being pulled into the room through the duct work from another part of the house.

Does the duct work go through the garage or any other part of the house that may have fumes? It may not be CO but something else that does not agree with you.

This post was edited by mike_home on Thu, Jul 10, 14 at 11:34


 o
RE: No CO, Yet Room Causes Headache/Dizziness

Just a guess, the door closed might be creating a negative pressure in the room. Whether that would cause headaches or dizziness I couldn't say but you could try sleeping there with the door open as a test.


 o
RE: No CO, Yet Room Causes Headache/Dizziness

Mold?


 o
RE: No CO, Yet Room Causes Headache/Dizziness

Thanks everyone for your suggestions! I will try them all.


 o
RE: No CO, Yet Room Causes Headache/Dizziness

mrjasondude,

I had lots of experience in being in an environment with a vacuum and also with a pressure. Neither condition caused headaches or dizziness.


 o
RE: No CO, Yet Room Causes Headache/Dizziness

First you are confusing correlation with cause and effect. It is a common problem. If your observations are reproducible, you might start looking for environmental causes. There are way too many uncontrolled variables in your situation to fly off the handle and start buying CO detectors and other equipment, or blaming the HVAC system.

That considered, A partial vacuum in the sleeping room (induced by the HVAC system for more than one reason) can cause air to be sucked in through leaks from other areas, rooms or outside. You can draw in allergens, fumes and whatnot from the attic, outside or a crawlspace.

I agree with sleeping with the door open as a test. In addition, with the fan on, and the door cracked open just a little, which way does the air blow, in or out of the room? Is the door undercut significantly? Where are your supplies and returns? These are all things that will indicate and influence pressure differentials.


 o
RE: No CO, Yet Room Causes Headache/Dizziness

Where is the hot water heater? Where is its vent?


 o
RE: No CO, Yet Room Causes Headache/Dizziness

May be something as easy as changing the linen or the pillow and blanket......


 o
RE: No CO, Yet Room Causes Headache/Dizziness

Coulda been an upper respiratory or ear infection that had a brief hold, but the OP managed to kick quickly.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Heating & Air Conditioning Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here