Very low air flow

Posted by mapr1 (My Page) on
Mon, Jul 11, 11 at 17:50

I am running my HVAC only in the fan mode to trouble shoot. Very weak air flow coming out of the vents that are even closest to the unit and much worse further out.

Have checked all the filters and returns and they all seem clean. Blower motor seems to be running fine (no funny noises etc). Nothing blocking the ducts too.

Anyone have any ideas to look into before either replacing the blower motor or upgrading the unit completely?


Follow-Up Postings:

 o
RE: Very low air flow

I am running the unit only in fan mode and turned off the a/c. so i am sure frozen coils are not the issue.


 o
RE: Very low air flow

Do you have flexibe ducting? Perhaps one has fallen and has become disconnected.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Heating & Air Conditioning Forum

Instructions

  • You must be a registered member and logged in to post messages on our forums.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review the contents and make changes.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • It is illegal to post copyrighted material without the owner's consent.
  • HTML codes are allowed in the message field only.
  • No advertising is allowed in any of the forums.
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.



 
Click here to learn more about in-text links on this page.