What's going on with my coils?

Posted by ryanpblyth (My Page) on
Tue, Jul 17, 12 at 17:12

So I obviously have a problem here - parts of my coils are icing up! But why just a few? I have replaced my filter, blown out the drainage line, so I suspect it's low on freon. The thing is - it used to completely ice up, and now it's just parts of it, is there debris in the line maybe? Thanks!


Follow-Up Postings:

 o
RE: What's going on with my coils?

Icing usually starts closest to the refrigerant metering device in the system (orifice or TXV valve) and progresses from there on the vapor line back towards the condenser.

That is the first spot refrigerant boils from liquid to gas and absorbs the most heat (producing the lowest temperature).

A low charge is a very common cause.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Heating & Air Conditioning Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here