Flex vs. Galv Duct

Posted by caseyj (My Page) on
Thu, Jul 26, 12 at 10:19

Is it best to use insulated flexible duct vs. going with the standard galvanized duct? Seems like there are a lot of problems with sweating and air leakage with galvanized. Is this a code issue?


Follow-Up Postings:

 o
RE: Flex vs. Galv Duct

either will work if they are mastic sealed.

flex has only two areas that leak..where they
connect to take offs at plenum (take offs leak too)
and where the flex connects to supply boxes.
if you mastic seal these connections (and duct
take offs at the plenum) the will not leak and
condensate.

hard pipe ducts leak at every seam and joint.
if you take the time to mastic seal all of these
areas prior to insulating then hard pipe is a good
duct system. problem is..folks don't mastic seal.

hard pipe ducting is more expensive than flex.

I like flex..seal it up, strap it up and its a good
duct system.

hard pipe is also good, just more leakage areas.

hvac folks either love flex or hate it
same with hard pipe ducts. usually they install
the brand they love..LOL!

and remember the mastic sealing is in the
details. use paint mastic and/or hardcast brand
1402 mastic tape.
to have a properly sized & designed duct system
is a wonderful thing. pair it with a properly
sized hvac system & you are golden.

best of luck.


 o
RE: Flex vs. Galv Duct

I've used both but since most of the installations or additions I was working in were in existing construction, flex was the only way possible to reach some areas. Just remember to use a lot of hangers or other support so it doesn't sag over time and cut down on air flow.


 o
RE: Flex vs. Galv Duct

You want the lowest mass possible fort ductwork in unconditioned space.

When the system is not running, the ducts are going to start to warm up (insulation can slow warming, but will not stop it).

When the system comes back on the now warm ducts are an additional load on the system until they are cooled back down.

Less mass, less load.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Heating & Air Conditioning Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Please review our Rules of Play before posting.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here