| Had our system replaced last week with a 3.5 ton XR13 AC, 80k XV80 furnace, and Honeywell IAQ stat. I was reading the various manuals and looking at the settings (I am a nerd mechanical engineer and like to know how things work) and found a few things that seemed off, wanted to get some insight before the tech comes back later this week for a checkup (the furnace makes a rattling/clunking noise at fan start up). System maintained temp at 75 deg and humidity ~50% during our ridiculous heat of the past few days FWIW.
Dip switches S4-1 and 2 are both set to On and it seems the ComfortR profile is active whenever a cooling call is made.
The IAQ is set up for dehumidify with AC (379=1). The system definitely turns on the AC if the measured humidity goes 5% higher than the setting. Overcooling limit is set to 3 deg (383=3) and this seems to work correctly too. What is not clear is if the wiring is set up correctly to run the blower at the reduced speed for dehumidification. Here's what I see inside the EIM:
From EIM:
All other terminals are unused. At the furnace I see the following:
Additionally, some of the dip switches are confusing. Note 9 in the furnace install guide states "...S5-2 switch must be set in the 'Off' position if humidistat is used. The 'S5-2' switch must also be turned to 'Off' when applying an airflow command signal to 'BK'." The S5-2 switch is actually set to On. I guess since the wiring described above isn't there this is "correct" for the time being? Last, for 2 stage heating - the wiring looks correct per the manuals (EIM W1 and W2 wired to furnace W and W2). Dip switches S7-4 are all Off, so I think that means no 2nd stage heat delay (correct for stat control of this feature?) and the default 90 second heat off delay. But then in the stat, it appears to be set for 1 stage heating - 176=1 and option 250 (CPH for 2nd stage heat) does not appear. So, it appears that both the dehumidification and 2-stage heating features are setup sorta half correctly, and that while ComfortR is definitely working I saw a few references to jumpers that should be in place that aren't. Any thoughts would be greatly appreciated, want to make sure this thing is set up correctly. jeff |
Follow-Up Postings:
Please Note: Only registered members are able to post messages to this forum. If you are a member, please log in. If you aren't yet a member, join now!
Return to the Heating & Air Conditioning Forum
Instructions
- You must be a registered member and logged in to post messages on our forums.
- Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review the contents and make changes.
- After posting your message, you may need to refresh the forum page in order to see it.
- It is illegal to post copyrighted material without the owner's consent.
- HTML codes are allowed in the message field only.
- No advertising is allowed in any of the forums.
- If you would like to practice posting or uploading photos, please visit our Test forum.
- If you need assistance, please Contact Us and we will be happy to help.