| I have a Trane XV80 and a XL15i connected to a HW Visionpro IAQ. The following connection exist.
HP Furnace EIM ----> O ---> W/O/B Is this correct? Other connections below:
There is no connection on Furnace BK interface
|
Follow-Up Postings:
|
- Posted by ryanhughes (My Page) on Sun, Jul 17, 11 at 9:51
| The wiring looks okay for a dual fuel system, but they haven't set up the dehumidification feature which will lower the blower speed upon a call for dehumidification from the IAQ. This would utilize the BK and DHM 1/2 terminals. |