| I live in a condo, on the 15th floor and have a large amount of condensation coming from the vent. The vent that this is coming from is 16 feet from the air handler, which is located in a closet. Any suggestions to the cause and possible repair would be greatly appreciated. Thanks. |
Follow-Up Postings:
|
- Posted by energy_rater_la (My Page) on Mon, Jun 13, 11 at 20:51
| could be that the supply box has a gap where it meets the ceiling. take the supply grill off and inspect the cut where the supply box rests on the sheetrock ceiling. Use a mastic tape..not foil, not caulk, but mastic tape make sure that the tape is covered by the this will keep the supply box in contact with the ceiling. what usually is occuring is @ that gap, hot attic air I seal all supply boxes this way. if the sheetrock needs minor cutting back you can use a razor knife. best of luck. |
Please Note: Only registered members are able to post messages to this forum. If you are a member, please log in. If you aren't yet a member, join now!
Return to the Heating & Air Conditioning Forum
Instructions
- You must be a registered member and logged in to post messages on our forums.
- Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review the contents and make changes.
- After posting your message, you may need to refresh the forum page in order to see it.
- It is illegal to post copyrighted material without the owner's consent.
- HTML codes are allowed in the message field only.
- No advertising is allowed in any of the forums.
- If you would like to practice posting or uploading photos, please visit our Test forum.
- If you need assistance, please Contact Us and we will be happy to help.