HRV off/Furnace on

Posted by saskatoon123 (My Page) on
Fri, Jun 22, 12 at 22:15

Hi,

Wow, I haven't posted hear in a long while but it was very helpful last time so I'll try again. Thanks.

We have a brand new HRV and HE furnace installed in our older home. The HRV is a partially dedicated system. When the HRV is turned on the furnace fan turns on in unison. It was recommended to me by the installer to keep the HRV on at all times summer and winter. I have since been reading that the HRV should be off in the summer in my climate as it may increase humidity in the home. (I'm in Saskatoon,SK Canada, think cold/dry winter and warm summers). I was thinking of just letting the furnace fan run for circulation and leaving HRV off but I was wondering if this will bugger anything up? If my HRV is off, will the furnace still pull air in and circulate it properly? Now that I think about it would it make any difference at all? Either device would pull air in it's just that the HRV would precondition that air. I must be missing something. Any advice would be appreciated. Thanks.


Follow-Up Postings:

 o
RE: HRV off/Furnace on

I don't understand why you say that that either device (the furnace in particular) would pull air in. Certainly the HRV will, but when that is off the inlet duct should automatically be dampered off. At least that's the way mine works (a Lifebreath 195ECM). The furnace fan should just circulate air within the house, unless there is an outside air inlet connected to it.

A lot of how you should run your system depends on the nature of the house, mainly how tight it is, and on how the air distribution ductwork is set up. An HRV usually is installed to ensure adequate ventilation in a very tight house. In such a house, the HRV indeed should be on all the time, or nearly so, at a low flow rate matched to the proper ventilation rate as specified by ASHRAE 62.2 (or Canadian equivalent).

In my system, the HRV dumps the conditioned incoming air into the return duct of the heat pump. There are three zones, and when none is calling for heating or cooling all zone dampers are open, so that air fed in by the HRV is distributed through the house. The heat pump fan does not have to be on to move the air.

If you have windows open in the summer, then yes the HRV might as well be off to save power. Otherwise it can be left on to provide fresh air if the house is tight, because you won't get much ventilation at all from leakage in summer if the windows are closed. Furthermore, human occupancy produces a fair amount of moisture (cooking, showers, plants, breathing). Bringing in humid outside air will contribute to the humidity in the house, but without ventilation the air in a tight house could get humid just from human activity. A dehumidifier could be a solution if there is no AC installed.


 o
RE: HRV off/Furnace on

Thanks for the reply DickRNH.
I guess I just made the assumption that the furnace fan would pull air from outside through HRV even with HRV off. I still got alot to learn how this system works. I seem to have a lot of moisture in the basement air. I mean it's not dripping but 55% humidity or more. I thought maybe the HRV was pulling the humid air in. I'll try some experimenting with HRV and will maybe invest in a better dehumidifier.
Thanks for your help.


 o
RE: HRV off/Furnace on

Humidity in the basement could be from the ground, especially if the foundation walls are not insulated and there is no insulation and vapor barrier under the slab. Concrete is very porous. Even if the surface does not look damp, that could be just due to evaporation as fast as it diffuses through from the soil.

You can test this by taping a sheet of polyethylene perhaps 3 feet square to the concrete surface. After a day or so, if you see condensation under the surface of the poly, then you have damp concrete. Even if there is little moisture coming in from the surrounding soil, you could be getting condensation of humidity at times from humid summer air against the cold surface of the concrete.

Given where you are, if the concrete walls are not insulated then you ought to do so. Rigid foam board 2" thick can be glued (PL-300) or fastened mechanically to the walls, then covered with sheetrock for ignition protection. If you have electrical outlets along the walls, then you could erect a framed wall of 2x4s on the flat against the foam sheets, use shallow "pancake" electrical boxes for the outlets, then cover the frame with sheetrock. A good reference for information on stuff like this is at www.buildingscience.com.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Heating & Air Conditioning Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here