| We had a tech come out for the annual maintenance. Our numbers for the upstairs unit were skewed.
Here is the rundown. The Condenser is a 15 year old Rheem. It was manufactured on 4/96 and it is 2.5 ton. The model number is RAMA-030JAZ. The furnace is 6 years old. It is a Rheem Super Quiet 80. It was manufactured on 10/05 and the model number is RGDN-05EAUER.
Here are the numbers that the tech gave: Outdoor temp 89
In his notes he mentions system is running very high head pressure and low suction. He also has a different number for subcooling in his notes, 38.9. I did my due diligence and looked at the system myself. The furnace is actually a 3 ton system, so he was wrong on that account. The previous owner had the downstairs unit moved upstairs back in 05 and in the process put in a new coil and furnace. This is the workorder info from the install back in 05: 1 Rheem 50,000 BTU 80% efficient furnace with 3 ton Drive
The tech said my system was mismatched because he thought it was a 2 ton furnace and that it needed to be replaced. Obviously, I do not have faith in his assessment. Does anyone have any idea what the issue could be, and why my subcooling and super heat, and pressure numbers are so skewed, and what I can do to make the system run more efficiently? Thanks |
Follow-Up Postings:
|
| While waiting for a pro to answer, you may want to consider that you may have a partial blockage in the line somewhere between the compressor and the evaporator (in the liquid path). "If Superheat is very high and Sub-Cooling is a little high: Do you know whether you have a TXV? |
Here is a link that might be useful: He DOES ramble on
|
- Posted by Lazerath(Lazerath198266@yahoo.com) onFri, Jul 15, 11 at 11:04
| Your subcooling is way too high on that system. Either you have a restriction at the metering device and only if it's a txv since your superheat is ok, or you are way overcharged. Wash the condenser coil and check again. If necessary recover refrigerant until you have around 9 deg subcooling. It is actually worse to be overcharged than to be undercharged as far as system capacity goes. |
|
- Posted by heatseeker (My Page) on Wed, Jul 20, 11 at 15:39
| sounds like your issue is on the refrigerant side rather than air handler side. The furnace is 50,000 btu's which is considered equivalent to 2 tons I'm not sure what is meant by 3 ton drive although I would think 1200 cfm. |
|
| Terminology: Ton usually refers to A/C output(12000 BTU/ton). In reference to furnace, it is shorthand for fan speed based on 400CFM/ton. Since different size A/C units can be matched with difference size furnaces(depending on location and house characteristics), Furnaces are sold with two size parameters: heat output(BTU) and air fan speed. The latter must match the A/C unit(heating is much less sensitive to ducts). Fan speeds are adjustable within a range by dip switches on the main circuit board. Finally, furnace fan speed should be appropriate for the size of the main duct the air is blowing thru. Too small ducts cause a variety of problems including uneven air temperature, excessive temperature fluctuations in rooms closest to HVAC unit, excessive wind noise and coil freezeup. |
Please Note: Only registered members are able to post messages to this forum. If you are a member, please log in. If you aren't yet a member, join now!
Return to the Heating & Air Conditioning Forum
Instructions
- You must be a registered member and logged in to post messages on our forums.
- Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review the contents and make changes.
- After posting your message, you may need to refresh the forum page in order to see it.
- It is illegal to post copyrighted material without the owner's consent.
- HTML codes are allowed in the message field only.
- No advertising is allowed in any of the forums.
- If you would like to practice posting or uploading photos, please visit our Test forum.
- If you need assistance, please Contact Us and we will be happy to help.