mikeinmayberry

220V mini-split A/C wiring questions...

mikeinmayberry
13 years ago

also posted on the wiring forum...

New here...I like what I've seen so far. I'm a jack of all trades, retired, working on a 2nd home I've recently purchased. This home, the money pit, is a 1-1/2 story with a full basement. The top room has a "mini-split" heat pump...darn thing wouldn't work. Upon further investigation I found the outside compressor was a 220V unit wired as a 110V. I called a local A/C outfit and they said I could remove the dedicated single 15A breaker, add a 15A 2 pole (30A) in its place. As the panel is 2 storys below in the basement, and all I have is 14/2 + bare grnd wiring, he suggested I hook the 2 pole breaker up with the black & white, and run the bare ground to the neutral bar. Now the A/C works (I do not need the heat pump to function). Everytime I leave this 2nd home, I shut the breaker off as I really have doughts this is correct. I haven't found a easy way to run a new 14/3 + grnd (or 14/4 if I want the heat pump to work) without tearing up a lot of sheetrock. An I over thinking this? I'd hate to burn the place down. Advice appriciated...Mike in Mayberry

Comments (8)

  • weedmeister
    13 years ago

    Well, lets see: a heat pump IS an A/C that can run in both 'directions'. You don't need extra electrical wiring for that (the heat) to work.

    It would be good to know if the unit requires both the neutral and the ground. It would also be nice to know how you connected it at the unit.

    Scenario 1: It requires two hots, neutral and ground. You connected two hots and neutral but no ground. It runs happily. But it is not a safe installation since the unit is not grounded.

    Scenario 2: It requires two hots, neutral and ground. You connected the two hots and ground but not the neutral. Then it would depend on whether the indoor unit uses a 120v blower. This probably would not work. but it might.

    Scenario 3: It requires two hots, neutral and ground. You connected the two hots and neutral. There is an internal jumper between neutral and ground. This is similar to how older 220v appliances used to be connected. It runs happily. IIRC, new code does not allow this type of installation (for appliances).

    The best long term solution will be to run the 14/3 from the box to the unit. Run it outside if necessary.

  • brickeyee
    13 years ago

    The straight 240 V setup is missing in the above examples.

    That would be two hots and ground.

    This is commonly done using 2-conductor plus ground wire.

    You only need the neutral if the unit is 120/240 V.

    What is on the nameplate of the outside unit?

  • mikeinmayberry
    Original Author
    13 years ago

    You guys are wonderful...here's the nameplate:

    Nordyne Model FT3BC-042K

    Voltage: 208/230V
    Phase: 1
    Hertz: 60
    Total Amps: 19.4
    Compressor Amps: R.L.A. 17.9, L.R.A. 104
    Outdoor Fan Amps: F.L.A. 1.5, HP 0.25
    Minimun Circuitry Ampacity (Amps): 23.9

  • mikeinmayberry
    Original Author
    13 years ago

    Message Preview
    Below is your message as submitted.

    If you wish to submit it, click on the submit button.
    If you wish to make changes, you can either use your browser's "Back" button and return to the original form, or use the form at the bottom of this page.

    --------------------------------------------------------------------------------

    RE: 220V mini-split A/C wiring questions...
    Posted by mikeinmayberry (My Page) on Tue, Jun 22, 10 at 20:48

    Let me try this again...I'm working off of pictures 140 miles away from the units...I fat fingered this the first time...pulled the info off of the wrong picture.
    Ductless mini-split
    Model S240HP-13K11-0
    Cooling Cap: 12500 BTU
    Heating Cap: 13000 BTU
    Voltage: 208V/240V
    1 PH/60 HZ
    Total Input Current: 6.22A
    Compressor RLA 5.7A, FLA 33A
    Fan Motor Outside: 0.064 HP, .56A
    Fan Motor Inside: 0.03HP, .16A

    NCP (made in China...uck)

  • brickeyee
    13 years ago

    "Voltage: 208V/240V "

    The unit is a straight 240 V load and does not need a neutral.

    It is common to run 2-conductor plus ground cable.

    The white wire should be marked black at the unit to indicate it is NOT a neutral but a hot.

    A wrap of black electrical tape is fine.
    It should also be marked at the breaker (and any other boxes it passes through) but that is not as important.
    Anyone working in the panel will instantly know it is a hot since it will be hooked to the breaker.
    At the unit this is not as readily apparent.

    If the panel is a main panel neutrals and grounds connect to the same bar.

    In a sub panel neutrals and grounds are separate.

  • JFM TRUST
    last year

    You would not mark the 2nd leg as a black, I would tape/mark it as red. Red is the common marking of the 2nd Load or power leg of a 220v circuit. It is of monumental importance that the Red wire/leg be connected to a different Busbar in the Main Panel than the black wire, meaning the Black power/load is connected to other Busbar than the Red lead, There are 2 Busbars in every Main Panel. An Alternating Current 220v circuit works in a way where the Black wire gets power for half a cycle, then when that power cycle/phase ends the Red wire gets power for half a cycle when the Black wire is dormant. Hence the current is alternating between the black and red wires.

  • Stephen Anderson
    last year

    Hey can i run a mini split 208 /240 v load and put a plug on it and plug it into a no longer used 220 hot tub outlet

  • Cold Sweat
    7 months ago
    last modified: 7 months ago

    I re-utilized a 50A hot tub panel for such minisplit operation, pulled the copper and foamed each end. Only used 25A on a three zone on the my north side, looking to run a line and upgrade box to two breakers to add a two zone on my south side. My east side used a 20A for a 36BTU from an previous AC for a vaulted ceiling addition that doubled my ground floor space on the SE side. Overall, nice operation, cost is considerable, but not an issue especially regarding comfort and uniformity throughout.