Hard start kit

Posted by barrychan (My Page) on
Fri, Jun 1, 12 at 7:23

hi all!
My condenser unit (Carrier 38TKB036) for the past year has been having trouble starting. The fan would start but the compressor would not kick in until say half an hour later. The first two years it didn't have that problem only recently. I have a dual capacitor that I replaced and it did not solve the problem. I am looking into the hard start kits below but they call out a separate 'run' and 'start' capacitor. So does that imply I only need to purchase the relay from the kit or I have to change out my dual capacitor that is in there right now? Thanks for the attention.

http://www.captiveaire.com/CatalogContent/Fans/Sup_MPU/doc/Start Capacitor Relay Kit.pdf


Follow-Up Postings:

 o
RE: Hard start kit

Barrychan,

Since you have a 3 ton unit. Get this hard start kit. It comes with a relay.

http://www.amazon.com/Compressor-Saver-Hard-Start-Capacitor/dp/B003FNMADE/ref=pd_sim_sbs_hi_2

The instructions are easy.


 o
RE: Hard start kit

The hard start kits come with a start capacitor and relay. You need both items in addition to the run capacitor. The capacitor in the kit is wired in parrallel with the run capacitor for the compressor. The relay disconnects the start capacitor once the compressor starts up. This is important since the start capacitor will not allow the compressor motor to run correctly once it is started.

The 5-2-1 compressor saver is easier to install and seems to be popular with HVAC techs. Here is a link the web site. There is a good video explaining the installation and operation.

Here is a link that might be useful: 5-2-1 compressor saver


 o
RE: Hard start kit

Thank you all for your responses. I'm still a little confused since I have a dual capacitor. does that mean it is both a run and start cap? And will i just use the relay from the kits you recommended?

Thanks!


 o
RE: Hard start kit

The dual unit has run capacitors for the condenser and the fan. You add an additional capacitor which will be used for starting only.


 o
RE: Hard start kit

A hard start kit adds additional start capacitance, ad a timer relay t pull it out of the circuit.

It does not replace or change the capacitors you already have.


 o
RE: Hard start kit

I got it. Thanks for your patience. Will follow up with the forum once I have it installed to see if the problem went away.


 o
RE: Hard start kit

Just wanted to let you guys know the hard start kit helped. The compressor is starting faster. The fan still does start for a few minutes before the compressor kicks in but the compressor is starting a lot faster than the usual 45 minutes of waiting that I have been used to. THanks for all the help; you guys are great.


 o
RE: Hard start kit

It sounds like the condenser does not have much life left. If you make it through this summer, then start planning for a new unit in the spring.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Heating & Air Conditioning Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here