Return to the Heating & Air Conditioning Forum | Post a Follow-Up

 o
Infinity thermostat programming

Posted by speedlever (My Page) on
Mon, May 17, 10 at 14:25

I'm new to programmable thermostats and have the Carrier Infinity thermostat as part of a recent replacement installation.

One question relative to programming it:
In setup- hybrid heat, I have the HP lockout set at <35*F. The Furnace lockout is defaulted to none. Should I set the furnace lockout to >35*F or leave it on none?

Is there a guide somewhere to tell me suggested tweaks? (I am an unapologetic tweaker to anything programmable!)

I found and enabled fan programming on the Advanced menu.. but don't find anywhere I can program the fan speed.

When I look at the schedules, I see only entries for day, time and heat and cool temps. Where do you find a place to program the fan?

If I press the fan control button (top right corner of the stat) and select low (instead of auto), I assume that takes it out of auto mode and it will just run 24/7 in low. Is that correct? I also assume this has nothing to do with the fan programming.

What am I missing here?

New equipment installed upstairs in 2 story house:
Carrier Infinity gas furnace: 58CVA070
Carrier HP: 25HPA524
Carrier coil: CNPHP3117ATA
Carrier Infinity thermostat

Downstairs is original split system: gas furnace and a/c.


Follow-Up Postings:

 o
RE: Infinity thermostat programming

Keep your furnace lockout default as none.
You may need the furnace on days that are above 35F

Unfortunately there is no guide, but you can teak all you want.

Programing Fan Speed, I can say I haven't ever looked into it, I guess I will now.
But you did go into advanced section under programming and set the programmable fan to ON? with this you should be able to select the speed.

yes if you choose low speed it will run the fan 24/7 on low until a cool or heat call is in demand. Then the demand will run the fan at the correct speed.


 o
RE: Infinity thermostat programming

As a for instance, in the installation instructions for the Infinity control, under hybrid heat, the example given shows a furnace lockout at >30*F and a HP lockout set for <15*F.

I have no idea what the furnace and the HP do in response to the settings on this page.

Per your suggestion, would both the HP and the gas furnace be operational at the same time in temps above 35*F if the furnace is set to none and the HP is set to lockout <35*F?

I sure would like to see where this is explained somewhere.

If the programmable fan option is set to on, where do you go to make changes to the fan speeds?

Regarding the fan control on the top right of the control, I have options of auto, low, med, and high. If I understand you correctly, any setting other than auto will continuously run the fan at that setting and will increase fan speed (if possible) should the control command it. I can't see that the programmable option has anything to do with this control.


 o
RE: Infinity thermostat programming

No, both HP and furnace do not run at the same time.
If by chance your heat pump has a high demand that will use it's axillary function then it will turn off the HP and go to axillary heat which is your furnace, then your furnace will take over.

As a program fan speed
1 Flip down the door at the bottom of the control.
2 Press the SCHEDULE button to access the schedule screen.
3 Press the FAN button to access the Fan Speed programming
screen.
4 Press the LEFT or RIGHT button to select the days you wish to
program ALLDAYS, WEEKDAYS, WEEKEND, or choose a
specific day (MON, TUES, WED, etc.).
5 Using the TIME (+\-) button, select your desired fan speed
LOW, MED, HIGH or AUTO.
6 Use the SCROLL button to highlight the next period, then
repeat steps 5 and 6 to select settings for DAY, EVENING and
SLEEP.
7 Press the FAN button to return to the standard scheduling
screen.
- OR -
8 Exit the scheduling mode by either closing the door or
pressing the SCHEDULE button.


 o
RE: Infinity Hybrid Heat

Hybrid Heat Setup / Operation
Furnace Lockout (in HYBRID HEAT SETUP menu) is the
outside temperature above which the furnace will not run except
for defrost (otherwise known as the aux heat lockout).
Heat Pump Lockout (in HYBRID HEAT SETUP) is the
outside temperature below which the heat pump will not run
(otherwise known as the balance point).
These values can be set identical to each other. If they are not
identical, the system will stage up and down normally from heat
pump to furnace when the outside temperature is between these
settings. The User Interface will not allow the heat pump lockout
setting to be above the furnace lockout setting.
The factory default settings for both of these is NONE (no
lockouts). Even though a heat pump lockout temperature may be
set, the system will still use the furnace in defrost operation, and
may stage back down to heat pump when defrost is completed after
a 2 minute delay.
Hybrid Heat Defrost (in HYBRID HEAT SETUP) When the
outdoor unit needs a defrost cycle, the furnace will run during
defrost regardless of lockout temperature, unless told not to in the
Hybrid Heat Setup screen. After defrost, the system may stage
down to heat pump after a 2 minute delay.


 o
RE: Infinity thermostat programming

Thanks for the fan programming tips. I'll check that out when I have a spare moment.

I'm still struggling with the control logic regarding lockout of the furnace and HP. If, as you suggested, I set the furnace lockout to NO and leave the HP at <35*F, I don't understand your comment about possibly needing the furnace above 35*F since the HP will be operational above that temp and the furnace will only run in defrost.

Playing with the control and running the HP lockout temp up, I could see that the furnace lockout would automatically track the HP lockout (as you mentioned above) not allowing the HP lockout to be higher than the furnace lockout.

There are 3 scenarios I can think of for lockout settings, and I do not understand why one would be chosen over another:
1) furnace lockout - no (your suggested setting)
HP lockout at 35*F (using 35*F as an arbitrary value)

2) furnace lockout - >30*F (lockout greater than the HP lockout)
HP lockout <15*F (instruction example)

3) furnace lockout - >35*F (lockout equal to the HP lockout)
HP lockout - <35*F (my current settings)

Perhaps the term staging up/down is what I don't understand. Keeping that in mind, how does the system operation differ between the examples above?

In a hybrid system like mine (with gas backup), does the HP have any other defrost capabilities (built in electric defrost?) than using the gas furnace for defrost?

Thanks for your tutoring!


 o
RE: Infinity thermostat programming

You come home and you were out of town and set the temp to 50 degrees. The house is cold but outside is 36 degrees. Do you want aux heat to run to heat the house faster? That is usually why you don't lockout the furnace based on outside temp. Now you could wait the six hours the heat pump takes to heat the house or you can allow the furnace to run.


 o
RE: Infinity thermostat programming

david_cary... another post from you that clears the mud from my eyes. You should rewrite the federal tax code. ;-)

Ok. Your explanation explains scenario #3... well, and also #2 for that matter... and scenario #1 as well.

Thank you.


 o
Hybrid system operation clarification

One thing that still puzzles me is that I understand that the HP and the furnace won't run at the same time. If in the situation described above where the emergency heat comes on (gas furnace in my case), does the HP not run at all during the time the gas furnace is running when above the HP temp lockout?

If only the gas furnace is running above the 35*F HP lockout due to the demand to bring the interior temp up from 50*F to 70*F, at what point will the furnace shut down and the HP take over reverting back to normal programming where the HP maintains temp until the OAT drops below 35*F?


 o
RE: Infinity thermostat programming

for a scenario #1 outside temp above 35F
The heat pump will run for 15 minutes, if it can not meet the demand in 15 minutes(default) it will then switch to the furnace.

Example #2 is efficency mode,
I would have this setting when the gas rate is high or I'm mad because I had my controller set for Example one and i had a big gas bill the prior month.
So example 2 is good for when the price for natural gas is high. Run the heat pump as much as you can before using gas.

3rd example is a compromise between 1 and 2.

So, when it come cold again, I would suggest setting your heatpump at a low lockout like #2 but raise it up if you want more instant heat when it's cold outside.

Remember you are a Tinker! and Bell would be proud! experiment with your own comfort level because the infinity controller does all the hard calculations for you, you just have to find your comfort level.


 o
RE: Infinity thermostat programming

Thanks classicdave. Very helpful info.

The trick will be to remember it when the cold weather comes back!


 o
RE: Infinity thermostat programming

classicdave,

I need to correct one of your very helpful posts. In the post where you include instructions on how to change the fan programming, you posted this:
"As a program fan speed
1 Flip down the door at the bottom of the control.
2 Press the SCHEDULE button to access the schedule screen.
3 Press the FAN button to access the Fan Speed programming
screen.
4 Press the LEFT or RIGHT button to select the days you wish to
program ALLDAYS, WEEKDAYS, WEEKEND, or choose a
specific day (MON, TUES, WED, etc.).
5 Using the TIME (+\-) button, select your desired fan speed
LOW, MED, HIGH or AUTO.
6 Use the SCROLL button to highlight the next period, then
repeat steps 5 and 6 to select settings for DAY, EVENING and
SLEEP.
7 Press the FAN button to return to the standard scheduling
screen.
- OR -
8 Exit the scheduling mode by either closing the door or
pressing the SCHEDULE button."

In step 5, you said to change the fan setting use the Time button. However, the Time button merely changes the time. I found (at least on my version of the Infinity control) that you have to press the fan button to cycle through the available choices).

No biggee, but I thought it worth correcting.

Note: without the programming option being turned on in the advanced menu, the fan option will not come up on the schedule page.


 o
RE: Infinity thermostat programming

Hello all. I cannot access the "fan" or "program" modes in the advanced setup dialog on my thermostat. What am I missing?


 o
RE: Infinity thermostat programming

I may be able to help if you describe what you are trying to do.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Heating & Air Conditioning Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Please review our Rules of Play before posting.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here