Ready to Make Decision - Good System?

Posted by engine15 (My Page) on
Tue, May 8, 12 at 11:59

I have been looking into replacing my heating system for a few months now, and I finally had a manual J calculation done for my house. The results came back with 33,000 Btuh equipment load for heat, and 25600 Btuh for cooling. I am looking at this system:

YORK TG9S060B12MP11 60,000 BTU furnace
YORK MC30B3X 2.5-ton coil
YORK YCJD30S21S1 2.5-ton 13.00 SEER condenser

I am looking for a basic, reliable system, would this work? It's a 1650SF house in NJ.


Follow-Up Postings:

 o
RE: Ready to Make Decision - Good System?

So if your load calc is correct, then the heating BTUs of this furnace will be over 70% of what you need!

Madness!

That is a basic furnace. I would not have it!

IMO


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Heating & Air Conditioning Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Please review our Rules of Play before posting.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here