| Do I need to replace an air handeler if my evaporator coil is leaking? I have had two different tecnicians in and one told me he thought the evaporator coil would need to be replaced and the other put in 3 lbs. of freon charged me
$327.00 and told me I would need an air handelr as you could not just replace the evaporator coil. |
Follow-Up Postings:
|
- Posted by tigerdunes (My Page) on Mon, Apr 16, 12 at 18:50
| What age is system including air handler? Your service tech/dealer did you no favor both in price and quality of the service you received. A typical gas n go shows a tech/dealer of questionable ethics. Sorry. This is the truth. IMO |
|
| 8 years old this April, can you replace the evaporator coils? The first technician also found leaking at the outside valve. |
|
- Posted by tigerdunes (My Page) on Mon, Apr 16, 12 at 20:22
| Twee I would get a second opinion. Leaks at a valve are usually easy and relatively inexpensive to repair. Evap coil leaks In an air handler can be another matter entirely. Standard procedure when adding refrigerant is to include dye especially when tech did not attempt to find the leak. Let the system then run for several days and return to check Yes, evap coils can be replaced in an air handler. However, usually this s not cost effective due to the expense. I assume air handler is out of warranty. IMO |
|
- Posted by heatseeker (My Page) on Tue, Apr 17, 12 at 9:39
| Yes you can just replace a evap coil whether it's electric or gas appliance. When was the last time you put freon in the unit? If never I would see how long charge lasts if every couple months time for new equipment unless leak is at solder point. If there was a leak at shreader vlv. then that should fix it unless tech is guessing at leaky evap coil. Did he check with sniffer or bubbles? |
|
| tweedge, Shrader valve should be an easy job with shrader valve core removal. probably a 5 mins job. Leaky evaporater coil is totally a different story. Yes if it is leaking at the evaporater coil, it's better to replace the air handler due to the labor involved in replacement the evap coil itself. The question is it leaking at the evap coil? did you see any kind of proof? |
Please Note: Only registered members are able to post messages to this forum. If you are a member, please log in. If you aren't yet a member, join now!
Return to the Heating & Air Conditioning Forum
Instructions
- You must be a registered member and logged in to post messages on our forums.
- Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review the contents and make changes.
- After posting your message, you may need to refresh the forum page in order to see it.
- It is illegal to post copyrighted material without the owner's consent.
- HTML codes are allowed in the message field only.
- No advertising is allowed in any of the forums.
- If you would like to practice posting or uploading photos, please visit our Test forum.
- If you need assistance, please Contact Us and we will be happy to help.