help with heat strip wiring Ruud

Posted by countryboymo (My Page) on
Sat, Feb 11, 12 at 17:45

I have a Ruud RHLL 3 ton and it seems I might have a dead stage of strips.

I was looking at the wiring and was wondering on a 15kw heat kit if the white with black tracer or white with blue tracer was the higher kw stage.

I also noticed on the control board where the wires for the strips plug in the board is stamped for common which is brown w1 which has a white with black tracer and w2 that has a blank hole. The other white with black tracer is in the far left hole which is also blank. Did someone snap the wire into the wrong hole on the connector?

I would think I should have a brown common... w2 with a wire and w1 with a wire.


Follow-Up Postings:

 o
RE: help with heat strip wiring Ruud

here is a pic of the connection I am trying to describe.

Here is a link that might be useful: connector photo


 o
RE: help with heat strip wiring Ruud

When the white with blue tracer is in W1 and the stat is calling for aux heat I am only drawing 3kw from the heat pump and air handler which is the same reading with no aux heat call. I moved the white with black tracer to w1 and now have 14kw total 4 mins on and 4 mins off because the cycle per hour was set at 9 which I backed down to 5.

I remember when the unit was installed the air temp in defrost was bone chilling and I assumed that the 'blue' leg of strips was not powerful enough for a defrost call. I moved it to the white with black and it worked perfectly. I think I never have had more than the one stage of strips.

Any Ideas or thoughts?


 o
RE: help with heat strip wiring Ruud

Hey can anyone give a tip on this?


 o
RE: help with heat strip wiring Ruud

First tip a 240 heat strip has no common. Heat strips can be very difficult you can get a good shock so you ought to invest in some help.


 o
RE: help with heat strip wiring Ruud

Ok let me rephrase... if you looked at the photo there is a W1 pin location a W2 and a "C". and a open hole with no designation.

If it comes down to it I will wear my low volt gloves (600v). I think with my fluke meter and the fact that I am dealing with the control circuit from the W1 and W2 thermostat terminals I will be ok. That is why I called the "C" port common.

Thanks for the concern heet. Can you look at the pic and tell me what you would do if you didn't have a 2nd stage of strip heat?


 o
RE: help with heat strip wiring Ruud

white/bl is 1 stage,white blue 2nd stage, brown is common to time delay control 1 and tdc2, the plug Pl1 1,2,3 are low voltage control pin 4 is a high voltage pin.

your photo shows missing pin 2(w2) second stage.
if wire was removed during install was it because they DID NOT want 15 kw operating??? can the incoming supply voltage to unit large enough to handle 15 kws?Was it removed for saftey reasons and 15 kw was not needed ( to large btu)?
I would simply jumper out w1/w2 to R where t-stat wires connect to A/H then take voltage/amp readings


 o
RE: help with heat strip wiring Ruud

I have two stages wired into the stat and only the black stage works. The blue one is on the far left. The hvac installer told me to swap the blue/white to the correct hole and without thinking plugged the connector back in and turned on the main breaker at the furnace and POP went the switching transistor for the W2 so something else is wrong. Voltage is different on the W2 than W1 but it wasn't substantial and its been a few days so I can't remember the numbers. I don't know if its a wiring issue or if my IAQ had a bad circuit which is doubtful since it didn't just kind of smoke. It went like a firecracker. The unit did not kick on or anything as I had it turned off at the stat. I flipped the breaker and pop. Its a warranty issue now and the hvac guy is coming to figure out why it is wired right now but popped the iaq. everything else still functions correctly.


 o
RE: help with heat strip wiring Ruud

I figured it out. The installer grabbed a 10kw strip with no staging accidently which explains why the w2 connection on the circuit board was vacant. I called him and when the temp stays at least 50 I will take a day off and he will install the correct strip set and replace the IAQ module that gave up the ghost.

I used to have a 20kw heat strip set in the old unit when it was horribly leaky and the house needed more insulation and sealing also. I still kill the heat pump below 10 degrees and the 10kw of strips can handle the task.

I can leave things be and just warranty the IAQ module or change the strips and module. The good thing is I could stage 5kw of strips to boost the heat pump and run defrost even though defrosting is rare which would help but if it went into the second stage of strips I would be into all 15kw with the heat pump.

I guess I should be thrilled that I sealed and insulated enough to cut my strip load in half.

I guess the moral to the story is even if the tech says swap wires and you have the meters and tools... pull them out and check his advice. I put 120v ac on the w2 termination which was more than the circuits design limits which made the magic smoke jump out with ferocity.


 o
RE: help with heat strip wiring Ruud

oops , the installer or company rep should have never been giving you instructions over the phone4. Is he paying for the repair? He should for being a moron.


 o
RE: help with heat strip wiring Ruud

Especially when he has the wrong strip listed in my file and he installed it. He is paying.


 o
RE: help with heat strip wiring Ruud

good job.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Heating & Air Conditioning Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here