| We're getting a new heat pump compressor. I've read a proper install is crucial in order to get the best performance. We're buying a new Lennox or Trane (salesman appointment has been made), but I don't know what questions to ask to determine which installer to use. The salesman's company has been in business since 1912. Does anyone know install questions to ask? Thank you. |
Follow-Up Postings:
|
| Additional info to my prior email about Heat Pump compressor install questions... live in Harrisburg PA area. Currently have a 1996 heat pump (Lennox) for 1st floor / basement (2500 combined sq ft), plus a 1996 heat pump for 2nd floor (2000 sq ft). |
|
- Posted by tigerdunes (My Page) on Thu, Jan 17, 13 at 12:23
| What size are each system? Do you plan on replacing both? What size heat strip do you have? What are the issues if any with these old systems? How have they performed? I assume you are in an all electric situation. When I see a post like yours I get a bit annoyed. If you want to know about a good install, then take a course at your local tech or community Here is my general checklist. There are three equally important aspects of a new installation. Correctly sized and quality HVAC, the install itself by the dealer and his techs, andbfinally and perhaps the most disregarded and overlooked is a decent ductwork system. Here is my general spec sheet for new system. both outside and inside units should be replaced to have a properly matched system. 15 SEER, 12.5+ EER, 9 HSPF you want a thorough inspection of your ductwork system. size, overall condition, supply and return lines, insulation qualities, leak test, etc. any hot/cold spot issues in your home should be addressed. My personal recommendation is Trane/AmStd, Rudd/Rheem, and Carrier/Bryant. Depending on your location, I would not purchase a new system that did not have electronic demand defrost. IMO |
|
| Thanks so much for all the information. The HVAC men are here now inspecting the existing units, duct work and measuring. I just told them about hot/cold spots based upon your instructions. Your other information will be used as my guide when discussing their recommendations. I've been reading online the last few days trying to figure it out, but your condensed version is a blessing. |
|
- Posted by tigerdunes (My Page) on Thu, Jan 17, 13 at 18:17
| Good luck! IMO |
|
| Well Tigerdunes, do you think your checklist helped? You bet! In case you were wondering how the first dealer visit went, I'll give a rundown. First, here is the recommendation: XP16 for attic 4T (since it handles 2nd floor and 1st floor addition) and basement 3T (1st floor and basement. Needless to say, it's more than a mouthful of $$$. Attic: $8892, Basement $7179. Can't do them both at once, that's for sure. The dealer has been in business since 1912 and one of largest in area; they emphasized their install. 16 SEER, 12.5+ EER, 8.5 HSPF you want a thorough inspection of your ductwork system. size, overall condition, supply and return lines, insulation qualities, leak test, etc. = he did a visual check of duct work and measured the house. No recommended changes. any hot/cold spot issues in your home should be addressed. = the back two north facing bedrooms are hot/cold. He suggested adjusting supply run dampers closer to furnace as to push air to back rooms. New HP units will not help cold/hot issue he said. Well, there you have my first QA with dealer #1. Monday Lennox dealer #2 comes for price and install compare. Any suggestion as to whether a 3rd estimate by a non-Lennox dealer is needed ? He said the embedded lines would be an issue for non-Lennox, although exterior lines with siding to cover could be added. Thanks in advance for all responses. |
|
- Posted by tigerdunes (My Page) on Sat, Jan 19, 13 at 6:25
| JoJo Which system do you plan on replacing? Never accept a quote that does not include complete details including model numbers of both outside HP condenser and inside air handler. Please provide. What size heat strip? Is it staged? Do you already have in place a whole house air filter cabinet? How is your return air filtered? If not, you should add one. How many returns do you have for each system? Just so you know, refrigerant lineset must be sized correctly to the manufacturer spec. Close does not count if you expect to achieve the performance/efficiency numbers that new system is capable of achieving. Not opposed to flushing existing as long as it's properly performed. But I want to know that existing is correct size. Do you know your size? If not find out. Now is the time to address hot/cold spots in your home. Usually this is due to poorly designed and/or sized ductwork. Ask for recommendations to improve. Obviously, you should seek several more quotes. I would want to hear from a Trane or AmStd dealer. IMO |
|
| Did this HVAC contractor do a load calculation? You have a total of 7 tons of cooling. This seems oversized for this size house and location. What are the areas of the first and second floors each area will serve? Does the current second floor unit service the first floor addition? Where are the units currently located? Is the contractor proposing any zoning? |
|
| Hi Tigerdune. Thanks for the response. The basement unit needs to be replaced first since it's short 8 lbs refrigerant. Running on electic backup at this point -$$$. Tomorrow will be a second quote from Lennox dealer #2. As suggested,I'll also get a Trane/American Standard quote. I'll circle back with the first Lennox quote to get the details you outlined, as with all other quotes. Time to get down and dirty with all this! Hi Mike_home: Thanks to everyone. I need to keep telling myself; I can do this... I can do this... |
|
- Posted by philip1965 (My Page) on Mon, Jan 21, 13 at 18:57
| This message is for Tiger dunes, do you do installations in northern va you seem very knowledgeable. Let me know. |
|
- Posted by tigerdunes (My Page) on Mon, Jan 21, 13 at 19:06
| For Phillip, Luv Va because I went to college in that state. But unfortunately I live many miles South. Wish I could help you even long distance. IMO |
|
| Hi TigerDune and Mike_Home. Just finished the last of three assessments this week; Lennox, American Standard and Bryant. Proposals are expected by early next week. Even ventured out into goethermal territory, since both heat pumps will need to be replaced soon. I expect a proposal shortly. |
|
- Posted by tigerdunes (My Page) on Fri, Jan 25, 13 at 12:01
| JoJo If going conventional HP system, I would not purchase one that did not have electronic demand defrost. EDD eliminates/reduces unnecessary, nuisance, and expensive defrost calls. Not to mention the extra wear and tear to the condenser. IMO |
|
| Will do. Thanks |
|
- Posted by countryboymo (My Page) on Sat, Jan 26, 13 at 12:41
| I would meet or exceed Tigers specs because that is the best bang for the buck and usually when you venture into the 15 seer range electronic demand defrost and a txv rather than piston orifice come standard because these are two items that are the biggest boost to get good enough numbers to get into the 15 seer range of performance numbers. I am sure if someone took the time with a decent numbered 13 seer piston orifice unit with timed defrost and added a txv and set it up correctly and added demand defrost that the numbers would climb into the lower 15 seer range but the cost to do so would be high. What I am trying to say is it seems like tiger is asking for a lot of options that might be hard to achieve but they are options that make it easiest for a unit to produce good numbers. I am sure there are 16 seer units that have piston orifices or timed defrost but the real performance numbers will stink.. This is why I say that what he is posting for a target to meet or beat is the best bang for the buck for the cost of the unit and the cost to operate and honestly the comfort level is increased tremendously. With better real humidity control of the txv and variable speed blower many times the old favorite summer temp of 74 might be 76-77 which saves even more $$. |
|
- Posted by countryboymo (My Page) on Sat, Jan 26, 13 at 13:28
| I would meet or exceed Tigers specs because that is the best bang for the buck and usually when you venture into the 15 seer range electronic demand defrost and a txv rather than piston orifice come standard because these are two items that are the biggest boost to get good enough numbers to get into the 15 seer range of performance numbers. I am sure if someone took the time with a decent numbered 13 seer piston orifice unit with timed defrost and added a txv and set it up correctly and added demand defrost that the numbers would climb into the lower 15 seer range but the cost to do so would be high. What I am trying to say is it seems like tiger is asking for a lot of options that might be hard to achieve but they are options that make it easiest for a unit to produce good numbers. I am sure there are 16 seer units that have piston orifices or timed defrost but the real performance numbers will stink.. This is why I say that what he is posting for a target to meet or beat is the best bang for the buck for the cost of the unit and the cost to operate and honestly the comfort level is increased tremendously. With better real humidity control of the txv and variable speed blower many times the old favorite summer temp of 74 might be 76-77 which saves even more $$. |
|
| Tigerdunes, I have organized all proposal info. into a word chart format, which can't be uploaded to the post. If you don't mind reviewing it, you can contact me at glk54@live.com. |
|
| mike_home and countryboymo; my error to have not included you too. Your input has been helpful and is welcome. Contact me directly at the above addy to get the comparison chart of the 3 proposals. |
|
| Well, no one seemed interested in viewing the 3 proposals I laid out in chart form via email, so I'll just give the American Standard heat pump proposal I'm leaning toward. Thoughts? BACKGROUND: Basement unit covers 2400 sq ft (includes 600 sq ft finished basement). Attic unit covers 2540 sq ft. for 2nd floor and 1st floor addition. CURRENT BASEMENT HEAT PUMP: Lennox 42000 BTU, 13.05 SEER, 11.25 EER, 8.25 HSPF. CURRENT ATTIC HEAT PUMPS: Lennox rated at 35,200 BTU, 12.5 SEER, 11.05 EER, 8.2 HSPF CURRENT ATTIC INSULATION: R-19 (6"). An energy audit recommended R-38 (10-12") which will be done after the ducts are modified. DUCT WORK: new ducts R-8. Current ducts are 4.2. Increase trunk duct size, increase branch duct size on attic system, change ducts to facilitate better airflow to end bedrooms. Duct work cost = $2250.00. American Standard Heat Pumps: AIR HANDLER: atam7a0c42h31 I'm good with the product and dealer has good reputation. However, the cost for both units and duct work is more than I can handle. Does this price seem reasonable? Any modifications to bring down the cost? For example: omit the humidifier (I don't have one now). Thanks.
|
|
| I will ask this question again, was a heating and cooling load calculation done? Your contractor wants to increase your 7 tons of cooling to 8 tons! In addition you want to increase your attic insulation. This would decrease your load. Properly sized equipment would reduce the cost. If you think your house is not dry, then you don't need a humidifier. You could reduce the cost by going with a single stage heat pump. |
|
- Posted by ryanhughes (My Page) on Wed, Jan 30, 13 at 20:22
| Any reason for the 3.5 ton air handler with a 4 ton heat pump? It is a match, but I would not go this route... Unless ~5" of height was an issue. |
|
- Posted by tigerdunes (My Page) on Thu, Jan 31, 13 at 8:37
| JoJo First of all, I sent my email address to you but never rec'd proposal. Several things. I agree about the sizing questions. You need a load calc for both heating and cooling both zones performed and given to you on the software letterhead in writing. I prefer the Heritage 15 over the Heritage 16 that was quoted. With the best rated matching VS air handler. I prefer the AS Perfect Fit air filter media cabinet over the AprilAire. I prefer the 803 stat, HW mdl #8321 with outdoor sensor. For ductwork, specify type. You want R-8 insulation or better. How many returns do you have on lower system? Just a few random thoughts. IMO |
|
| "DUCT WORK: new ducts R-8. Current ducts are 4.2. Increase trunk duct size, increase branch duct size on attic system, change ducts to facilitate better airflow to end bedrooms. Duct work cost = $2250.00." There is a proposal to improve the duct work. |
|
- Posted by tigerdunes (My Page) on Thu, Jan 31, 13 at 9:12
| Put it another way. Is flex involved? What about returns? |
|
| Hello, I really appreciate your follow-up to my questions. I reached out Friday to American Standard for answers listed in your emails and info. about the Heritage 15. I'm also requesting load calcs for proposals. I'll be in touch on this. Monday is a conference call with Lennox. Proposal for both units is below. He will work with me on labor cost if both units are installed at same time. Basement: XP16-048 2 stage /4 Ton/ 47,000 BTU, 16 SEER, 8.5 HSPF, 12.5 EER with R410A Attic: XP16-036 2 stage /3 Ton/ 16 SEER, 12.5 EER 8.5 HSPF/ 36,000 BTUs, 2 stage with R410 A Any suggestions/comments are welcome. Once again, thanks!
|
Please Note: Only registered members are able to post messages to this forum. If you are a member, please log in. If you aren't yet a member, join now!
Return to the Heating & Air Conditioning Forum
Instructions
- You must be a registered member and logged in to post messages on our forums.
- Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review the contents and make changes.
- After posting your message, you may need to refresh the forum page in order to see it.
- It is illegal to post copyrighted material without the owner's consent.
- HTML codes are allowed in the message field only.
- No advertising is allowed in any of the forums.
- If you would like to practice posting or uploading photos, please visit our Test forum.
- If you need assistance, please Contact Us and we will be happy to help.