Furnace backdraft being blown into home by forced hot air system

Posted by Mchris344 (My Page) on
Mon, Jan 14, 13 at 9:51

Help! I am completely out of solutions and need some advice. We moved into a new home in June. As soon as we turned the heat on in late October, we noticed an oil or exhaust smell entering the home when the furnace fired up and the blowers blew warm air into the home. Since then, we have had our furnace company out twice to inspect the furnace, and have also had our chimney inspected twice. Everyone has told us that nothing is wrong, and no one has offered a solution. The smell happens on and off, and has sometimes gone a full week without happening. So far, the carbon monoxide detectors in the house have not sounded, but the electronic unit in the basement indicates that the level is close to a low alarm level at 35. We had this unit in our second floor bedroom for a week or so, and the level read 12. Can anyone offer any suggestions? I've run out of ideas.


Follow-Up Postings:

 o
RE: Furnace backdraft being blown into home by forced hot air sys

Also, the furnace is less than one year old, but the hot water heater is pretty old.


 o
RE: Furnace backdraft being blown into home by forced hot air sys

Is this an oil fired furnace? Is the hot water heater oil fired or electric?

Do you have a powered exhaust fan in your attic?


 o
RE: Furnace backdraft being blown into home by forced hot air sys

Yes, everything is oil. There is no fan in the attic, and the house is 20 years old, so I don't think it's an issue of any exhaust fan creating a vacuum in a very tight home.


 o
RE: Furnace backdraft being blown into home by forced hot air sys

"exhaust smell entering the home when the furnace fired up and the blowers blew warm air into the home"

I would investigate to see if you have a cracked heat exchanger. You may also have a combustion and/or venting issue with the furnace or hot water heater.

Did the furnace tech smell the odor? Maybe you need to call in a new service company.


 o
RE: Furnace backdraft being blown into home by forced hot air sys

The furnace tech did smell the odor, and simply blamed it on the chimney. He actually made a comment that the smell was so strong that even someone like him, who is used to the smell, thought it was strong. It might be time to call another furnace company, but the furnace is under warranty with our current service provider. Maybe that is one of the reasons that they continue to tell us nothing is wrong...


 o
RE: Furnace backdraft being blown into home by forced hot air sys

Is this a brick chimney? Maybe there is a problem with chimney itself or how the venting was installed. Get an inspection by an independent chimney specialist. You need to get this resolved ASAP.


 o
RE: Furnace backdraft being blown into home by forced hot air sys

The chimney is brick, on the exterior of the home. I've read a lot about that not being an ideal system, but it's what we have. The furnace tech is currently in the basement for the 3rd time, and is talking about installing an exhaust fan on the exhaust pipe before it hits the chimney to help push the exhaust out. He says the draft is "crap." He also mentioned that the newer furnaces (which this is) don't produce enough heat to induce a strong draft, which I have heard about as well.

We did have the chimney inspected - twice. And both inspectors said that it's fine. This is why the problem has been so frustrating. Everyone is telling us everything is fine, and it clearly isn't.

Should we try the fan?


 o
RE: Furnace backdraft being blown into home by forced hot air sys

What is the rated efficiency of this furnace? The higher the efficiency, the cooler the exhaust gases. A cool exhaust has more difficulty rising up the chimney. There is some truth about the what the tech is stating.

I am not an expert, but I don't think an exhaust fan is the correct solution. You need to install a stainless steel chimney liner in order to solve your problem.


 o
RE: Furnace backdraft being blown into home by forced hot air sys

Thanks for the input. I think we'll get some quotes for a liner...


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Heating & Air Conditioning Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Please review our Rules of Play before posting.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here