rheem ac a-coil replacement question

Posted by jmcqueen (My Page) on
Tue, Jan 13, 09 at 4:24

hi all:

i have been reading this forum with much enjoyment and have the following to run by the pro's. i have a 15 yr old rheem criterion 75k btu gas furnace and a 2.5T? rheem AC coil (Red-T-Coil), model RTB25ACU. assuming this means 2.5 ton??? here's the prob. i get good airflow from the furnace during the winter and my house is fairly evenly heated, but in the summer, the most pull-down i can get vs. the outside temp is 13 degrees. so, when it's 90 outside, it's a balmy 77 degrees inside the house. the AC won't turn off all day...and for most of the night. i have had our local AC guy out a couple of times and everything appears to be in order with the AC. no leaks, pressures check ok, etc... a couple of seasons ago, the tech did have to add some R22 when he discovered a small leak, which he also fixed. so....

i suspect that i simply have an undersized AC unit for my house. here's what my idea is, and tell me if this is even do-able and/or advisable. i am looking at bumping up the a-coil to a 3.0T or 3.5T (like a carrier CNRPV). would i be ok doing this without changing the compressor out? i suspect that the coil i have is just a piece of garbage based upon what i've read, but i don't want to spring for a $400 coil if what i am considering doing is just out of the question.

any advice/help would be greatly appreciated.

thx,
j


Follow-Up Postings:

 o
RE: rheem ac a-coil replacement question

That evaporator coil is a 2 ton coil. Do not mismatch the evaporator coil and the condenser coil. Besides mismatching size, you will end up mismatching the energy efficiency rating. That coil is what's called a 10 Seer coil, and nobody makes a 10 Seer coil anymore. The lowest you can go is a 13 Seer system. I would go ahead and do everything right the first time, that way you will not have any issues with mismatching the system.
Also, if you get a free estimate from someone, see if they can do a manual J load calculation on your house to make sure the unit is not undersized.
A very rough way of figuring out whether you unit is big enough is taking the square footage of your house dividing that number by 600. That will be a somewhat close estimate to what size unit you need.
Performing a manual J load calculation is much better because they account for the windows, doors, insulation, and position of the house.
Hope this helps.


 o
RE: rheem ac a-coil replacement question

tlewis:

thanks much! home is 2200 sq.ft. west-facing, colonial two-story which, at first glance based upon the formula you have mentioned, would put me at 3.66T. we live in the midwest (ohio) and have roughly a 5 month cooling season, so it's pretty important that the new unit be sized properly. i will check into getting a load calc done to be sure, but can i firmly conclude that 2.0T is just way too small? like i said, the furnace does a great job keeping up on cold days, so at least i know my system has the capacity in terms of air flow.


 o
RE: rheem ac a-coil replacement question

Can't confirm a system is too small without a load calculation done, but 2 tons does sound small for your size home. Increasing the coil size won't make the 2 ton cool better. If anything it will decrease its ability to remove moisture because it will run warmer. I wouldn't mismatch the coils, either. You're probably better off with a new properly-sized A/C system.


 o
RE: rheem ac a-coil replacement question

thanks for the pointers ryan. i am thinking about biting the bullet next spring. i did some checking online and saw a Carrier 3 ton 12 - 13 SEER R410A cased coil and a Bryant condensor (supposedly a matched setup) for $1500 (on e-bay). I will probably be in the house another 6 years or so, but don't want to buy crap. service tech changed the board and blower in the furnace last year and it runs just fine. just need a decent unit to make my house cold. any recommendations on a condensor/coil...with the consideration that the furnace might puke out within the next 5 or 6 years? i did a pretty close load calc using some online resources and came up with 3.49 ton needed for my house. i didn't fudge too many numbers...


 o
RE: rheem ac a-coil replacement question

The problem is going to be moving almost twice as much air through (supposedly) 2 tons worth of ductwork, assuming it was sized right to begin with. I would not trust an online load calculation. You want an ACCA-approved Manual J load calculation done by a professional, then your ductwork inspected to see what needs to be done. That would be the best way to do it. Good luck.


 o
RE: rheem ac a-coil replacement question

please pardon my lack of understanding. i think i'm finally getting it though. are you saying that because i would be increasing the tonnage of the AC by 50% (from 2T to 3T as in the above example), that i need to assure that the air flow and ducting is sufficient?

many thanks,
j


 o
RE: rheem ac a-coil replacement question

J, you got it. Without sufficient ductwork, your new system won't deliver the expected performance and capacity, and may not be much better than what you have now. I haven't seen your ductwork, though; I'm just stressing the importance of a professional evaluating your whole system and doing a load calculation to determine sizing, then making certain the new system will work with what you have now. Good luck in getting this taken care of.