| I have a natural gas fireplace which is having problem in igniting. I have replace it with a Honeywell S8610U Universal Intermittent Pilot Module. But the fireplace will only start up and lit for about 2 sec. and then shut off and start again.
I have checked all the grounds and connection and they seems OK. I am just wondering if the ignitor/sensor is the problem. Is there a way to check the output of the senor wire to the module ? The fireplace was lit and I assume the ignitor or spark is ok. Thanks in advance for any advices. |
Follow-Up Postings:
|
- Posted by seattlepioneer (My Page) on Wed, Oct 17, 07 at 17:31
| < Yes, there is. You need to measaure the DC microamps flowing from the ground connection to the module. A typical read would be 10-15 microamps, but the pilot will usually prove with 3-4 microamps.
|
|
| On some of these you can run a wire from the pilot flame to the sense port and see if it works too. |
Please Note: Only registered members are able to post messages to this forum. If you are a member, please log in. If you aren't yet a member, join now!
Return to the Fireplaces Forum
Instructions
- You must be a registered member and logged in to post messages on our forums.
- Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review the contents and make changes.
- After posting your message, you may need to refresh the forum page in order to see it.
- It is illegal to post copyrighted material without the owner's consent.
- HTML codes are allowed in the message field only.
- No advertising is allowed in any of the forums.
- If you would like to practice posting or uploading photos, please visit our Test forum.
- If you need assistance, please Contact Us and we will be happy to help.