New Construction Roof - No step flashing?

Posted by Denarius (My Page) on
Tue, Jun 11, 13 at 9:56

On our new construction inspector noted that the roof does not have "step" flashing and may be prone to leaking. Said it is not an approved flashing. Roofing sub when questioned said that this is a "new" way of flashing and that step is not in favor any more as it can lead to the flashing pulling away and allowing rodents and leaks in. Not sure what to do with this...is this flashing correct? Here is a picture. Any help is appreciated.


Follow-Up Postings:

 o
RE: New Construction Roof - No step flashing?

If it is the new way, ask for the manufacturer specs and verify with them! Your picture isn't that helpful to me as I can't tell if any of that is rigid, or if it is all some sort of paint-on/topical application substance; nor what that substance is.


 o
RE: New Construction Roof - No step flashing?

IRC 2012 mandates either continuous or step flashing. So if your jurisdiction has adopted IRC 2012, the continuous flashing conforms. Building Science Corp. in US Energy Department publications describes other acceptable approaches--including integrating a water shedding membrane behind the brick wall with the adjacent roof below.

Nevertheless, between continuous or stepped flashing, most experienced builders seem to favour the stepped approach.

The Code in my jurisdiction, OBC [Ontario Building Code] (see below) prescribes step flashings between masonry walls and shingle roofs.

This post was edited by worthy on Wed, Jun 12, 13 at 14:49


 o
RE: New Construction Roof - No step flashing?

There are 3 issues: 1) how the flashing integrates with the shingles (whether short pieces of the flashing are "stepped" ie, inserted between the shingles or run in one piece under all of the shingles), 2) how the flashing integrates with the brick (whether short pieces are tucked into the brick joints and stepped down the brickwork or one continuous piece is mechanically fastened to the brick and sealant is added), and 3) whether the elements 1 & 2 are one continuous piece or two pieces (upper flashing overlapping the lower flashing).

The traditional and best method is to separate the upper and lower flashing so the upper overlaps the lower and to step them both. There should also be a flexible flashing installed against the bare roof sheathing and the bare brick (Grace Ice & Water Shield roof flashing or Perm-A-Barrier wall flashing set in Grace WB Primer)

If the better flashing detail was not in the contract documents and this kind of detailing is commonly done in your area then there's no reason to argue with this contractor and I recommend hiring another contractor to replace the work.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Building a Home Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Please review our Rules of Play before posting.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here