So moving if toilet is out of the equation...off center toilet???

piscesgirl
11 years ago

Our master bathroom is only 7'x7.5' Against the left wall we have a 35"x35" shower, an 8" wide divider wall which contains the shower plumbing pipes, and then the toilet in a 40" wide space.

Our plan was to move the toilet over creating a 30" toilet space and create a larger frameless glass shower by removing the shower plumbing to a different wall and eliminating the 8" thick wall.

Our contractor opened the floor only to determine that the joists run the wrong way to move the toilet (he says it can't be moved) and the toilet appears to already be as far over within the joist as it can move. (see picture with black marker line that indicates center line of joist)

If we move the toilet to the other side of the joist (which is what our neighbor had done) the toilet space would be 28". We were hoping our joists were positioned differently but apparently they are not. DH and I are concerned with the thought of cutting joists. Don't know if we can do it to code (joists 9" tall) and not to mention we were ok with a 30" cozy toilet area, but 28" may be a little too tight (and for all we know not to code as well).

Trying to figure out other options. Would it look bad if the toilet was not centered. Does anyone have any pictures of this? We were thinking 35" toilet space with 20" on far wall side and 15" on the side to shower glass wall side.

What about off center toilet flanges? Are they code anymore? Any other suggestions? Thoughts? Should we just leave it as is at 40". Again, the desired end result is a larger shower and smaller toilet area, and no we can't make the room bigger....I wish!

Thanks!
PS: Don't you love our 1970's blue spin-art looking tile? Yikes!

Comments (9)

  • User
    11 years ago

    Leave well enough alone and just do a cosmetic redo. What you are proposing does not pass code. Or look in the other direction for the shower expansion. What's on the other side of the shower wall?

  • piscesgirl
    Original Author
    11 years ago

    GreenDesigns-
    So a 35" toilet space with 15" on one side and 20" on the other doesn't pass code? What is the reasoning behind that? I would have thought that if a 30" space with 15" on each side meets code, why would having extra space to the one side not be to code? A toilet isn't always between two walls.

    We can't expand the other direction for the shower as that wall goes into our bedroom and the way the doors and an exterior window are positioned we can't move the wall any further into the room.

  • piscesgirl
    Original Author
    11 years ago

    Ok..not sure if Google has led me down the right path but here is what I found according to IRC (International Residential Code) sec. 2705

    http://archive.org/stream/gov.law.icc.irc.2012/icc.irc.2012_djvu.txt

    "SECTION P2705
    INSTALLATION
    5. Water closets, lavatories and bidets. A water closet,
    lavatory or bidet shall not be set closer than 15 inches
    (381 mm) from its center to any side wall, partition or
    vanity or closer than 30 inches (762 mm) center-to-cen-
    ter between adjacent fixtures. There shall be a clearance
    of not less than 21 inches (533 mm) in front of a water
    closet, lavatory or bidet to any wall, fixture or door."

    It doesn't say anything about the two sides being equal, just that they need to be a minimum of 15" from center, or 30" total center to center. Now you may tell me it will look horrible, that's another story, but I am not sure if I am following why it isn't to code.

    Here is a picture I found online of an off center toilet. It is a toilet stall, and I think it is closer to walls/partitions than we would be...but it was all I could find. I don't think it looks terribly bad and to be honest I think ours will be less noticeable since the wall to the left will be a glass wall to the floor...so it will feel more open. Thoughts?

  • kmcg
    11 years ago

    I did an off center toilet in our new bath because the toilet alcove is next to a low window with plantation shutters. The measurements from center might be more like 16" on the close side and 22" on the wider side. I am traveling so I can't check. But it really looks fine. By the time you put in a tp holder in the wider space, it's hardly noticeable.

  • piscesgirl
    Original Author
    11 years ago

    kmcg- I would love to see a picture if you have one.

  • piscesgirl
    Original Author
    11 years ago

    Hi KevinMP- Sorry if I wasn't clearer in my 1st post. That is exactly what we are planning doing. We currently have a 35" x 35" shower, 8" divider wall and 40" toilet space. Total wall length 83"

    Plan is to move plumbing and eliminate divider wall...freeing up an additional 8" of shower space. We also have room to make the shower another 2" deeper...so it will be 37" deep (including shower curb)

    We were also hoping we could have also easily move the toilet over 5-10" figuring we only needed a 30" toilet area, not 40".....ultimately creating a 37" x 53" shower. However once we opened the floor we realized that is not feasible.

    So now our choices are as follows:
    1) Keep a 40" toilet space, which makes the shower area 37" x 43" (including shower curbs)
    2) Make the toilet area 35" by making the shower area another 5" wider...thus creating a 37" x 48" shower area (including shower curbs). However this option creates an off center toilet.

    I just want the shower to be as spacious as possible, but if 5" isn't going to make a noticeable difference maybe we won't bother and will just leave the toilet at 40".
    Thoughts?

  • KevinMP
    11 years ago

    The benefit you have is that you know from using your shower how much more space you need to be comfortable. Start with that as the baseline. If you think the extra 8" is enough, that's important to know. As long as you have 15" on either side of the toilet center, you should be good. Mine was 27", believe it or not, because my house is nearly 200 years old and didn't even have plumbing to begin with. I fixed it when I remodeled, and it's about 30" now, but it was very tight before with shoulder room. It all depends on what the dimensions are once it's off-centered. It sounds to me like you might have enough room to make it work. I wouldn't worry about the asymmetry if that's all it comes down to.

  • kmcg
    11 years ago

    Here is what I have available, but it's not the best angle.


    Here's a broader view with shower and toilet edge. This shower is 48" plus a half wall about 6" thick.