Posted by WADIY1024 (My Page) on
Sun, Sep 15, 13 at 21:11

My wife & I are currently thinking about remodeling our bathroom. Part of our remodel is moving the toilet 90 degrees to the left about 2 feet. Do I need to move the vent also or can the current vent be used?


Follow-Up Postings:

 o
RE: Moving toilet

The toilet flange should be connected to the 3" fixture arm with a long heel closet bend. The max length of the horizontal run of the 3" arm can vary depending on code. Trap weir to vent limit under UPC is 6' max, IRC is 12' max.

The IRC length is predicated on the horizontal run of 3" pipe being pitched at 1/4" per foot, because with IRC the bottom of the pipe at the trap weir can not be higher than the top of the pipe at the vent opening. So a 3" pipe divided by 1/4" pitch equals 12' of run before that happens.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Bathrooms Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here