Posted by elk2000 (My Page) on
Thu, May 10, 12 at 17:13

We are planning to install Warming Systems heating floor mats along with Schluter Ditra. We always use Ditra and we love the product. I've read in multiple places that mats should be installed on subfloor then Ditra then tile. But Warming systems rep told us that we need to install Ditra under the mats, then tile. Is it true? Did anyone installed Ditra with heating mats?


Follow-Up Postings:

 o
RE: Radiant floor and Schluter Ditra

We just put in a Nuheat mat and Schluter Ditra in our masterbath, in the following order, from the wooden subfloor up:

1. Modified thinset
2. Nuheat mat
3. Modified thinset
4. Unmodified thinset
5. Ditra
6. Unmodified thinset (using a 1/4" x 1/4" square notch trowel)
7. Tile

You should check the Schluter site because I believe that installing a heating mat over the Ditra will void the warranty.


 o
RE: Radiant floor and Schluter Ditra

That's exactly what I've read on other forums. Warming Systems mats are not different from any other brand mats, so the technology should be the same.
Are tiles heating up OK with so many coats between mats an tiles? That is actually another concern we have. Is any heat lost or it's simply takes longer to heat?


 o
RE: Radiant floor and Schluter Ditra

We've only used it a few times in the 6 weeks since the room was done and I haven't kept track of the time it takes to warm up. It does start to get noticably warm within about a half hour, if I recall correctly... possibly less. It definitely gets warm enough to be wonderful and luxurious! We're going with the same system in the guest bath that we've just started to renovate.


 o
RE: Radiant floor and Schluter Ditra

To take advantage of Ditra as an uncoupling membrane you're best using it between the heating elements and the tile.


 o
RE: Radiant floor and Schluter Ditra

No, not to uncouple it from the heating source. Imho.

I know that the Schluter company asks for the heat to be installed under the membrane, but I would feel comfortable with it the other way too. The closer you get your heat to the tiles, hte better it works.

Uncoupling is for the other mechanical stresses in a building that moves a bit.


 o
RE: Radiant floor and Schluter Ditra

We've put Warming Systems + Ditra in multiple rooms in our house. Always wire on the bottom, Ditra in the middle, tile on top. That's actually how Ditra shows it in their installation guide. The tiles heat up just fine.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Bathrooms Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Please review our Rules of Play before posting.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here