Need Advice - Kitchen Hood/Makeup Air

Posted by malcience (My Page) on
Wed, Nov 18, 09 at 8:09

My wife and I are building a new house in the Pittsburgh area and we are getting close to our pre-construction meeting and plan confirmation. Our builder has said that according to 2006 IRC any kitchen hood that will produce more than 3 Pa of negative pressure needs to have a make-up air system installed with it. For our home the pressure requirement converts to 400+ CFM hood and we will have a Bluestar RNB 36" range so we want > 400 CFM. Our appliance vendor has apparently never heard this before.

I dont know anything about makeup air, our builder said it could be installed in-line with the hood (Independant INBQ) but again our appliance folks said they have never heard of it.

Could someone enlighten me as to what exactly a make-up air system entails?

What viable work-arounds exist? (or are we violating our home warrenty if we try?).

I am also going to be looking for any manufacturer sites and calling Independant to see if they can straighten me out, any other sites that could help me figure out what we need to get done would also be appreciated.

Thanks!


Follow-Up Postings:

 o
RE: Need Advice - Kitchen Hood/Makeup Air

Things to check:

* Does 2006 IRC apply to your jurisdiction?

* How did he compute 3 Pa? How does he know the physics to determine that?

Make-up air is basically a blower system that replaces the air that the hood takes out. You can see its importance, for example, if you think about a fireplace that could have the smoke "sucked" into the house, instead of going up the flue.

Another good source of moderately-priced, high-quality hoods is Prestige.


 o
RE: Need Advice - Kitchen Hood/Makeup Air

2006 IRC does apparently apply, the builder said that without make-up air the house won't pass code.

Chapter 15:
M15001.2 Indoor depressurization. Ducted exhaust systems shall not induce or create a negative pressure sufficient to cause backdrafting of naturally vented, open combustion-chamber, fuel-burning appliances, or create negative pressure in excess of negative 3 Pa. in the immediate proximity of combustion chambers of such appliances.

The builder (their HVAC engineering department) has the A/C capacity and the minimum air flow through the house, since there are minimum requirements for Energy Star certification. With this he can back out how much additional draw would be needed to violate code. 400 CFM was the number they quoted me, without seeing their model and inputs thats all I know.

I dont think the hood is the problem, we have contacted BlueStar, since they are in PA, they make hoods as well and they are the manufacturer of our range, to see what they can tell us about the regulations.

I still cant find much about make-up air systems though everything I've found is industrial.


 o
RE: Need Advice - Kitchen Hood/Makeup Air

Try Prestige Hoods -- they make the BlueStar hood and were very helpful when I called them on some ducting questions.

Your builder seems to know what will and won't pass plan review or inspection. I'm not an inspector, but as I read that, it is saying that the back-drafting or pressure drop is for other naturally-vented appliances, not the range. I don't think the range even falls into the "naturally-vented" category, as it doesn't have a vent to the exterior at all. I would interpret that requirement to apply to, for examples; gas hot-water heater, gas fireplace, gas furnace, but not the range or ovens. With the exception of the gas fireplace, I would be surprised (but not completely so, as I've never modeled it), if a hot-water heater or furnace in your garage or basement experienced significant pressure changes from a 600 (or even 1200) CFM hood on a different level and through several doors.

It might be worth a call to your local building inspection department and talk with what our jurisdiction calls a "Senior Inspector" who can give you guidance. That kind of thing saved us from having to put the gas shutoff in a cabinet (rather than behind/beneath the range) as our code recently changed from "readily accessible" to "accessible" and many local plumbers (and apparently some inspectors) were not aware of the change.

Here is a link that might be useful: Prestige Hoods


 o
RE: Need Advice - Kitchen Hood/Makeup Air

It's your HVAC guy you should be talking to about installing makeup air, not your appliance dealer. I can't give you any details but I know there are different kinds of systems - some that will heat the air if necessary so that you're not pulling in cold air in the winter.


 o
RE: Need Advice - Kitchen Hood/Makeup Air

Where is it is best for the make-up air to come in?

At the hood (e.g. make-up air enters the room at the front of the hood, the exhaust air is drawn out at the rear of the hood)? Somewhere behind/under the range? Elsewhere in the kitchen?

I'm asking because, in a cold climate like PA, I wonder if the need to pre-heat the make-up air (complication, cost) is affected by where it enters?

Also, is it possible that having make-up air enter at the hood, close to the exhaust vent, might make the system less effective at exhausting vapor/grease from the range top some 30" below? As in, the exhaust simply removes the make-up air, leaving the cooking vapor behind?


 o
RE: Need Advice - Kitchen Hood/Makeup Air

As weisman said, this isn't the venue of an appliance dealer. A good dealer will help you to figure out how much CFM you need to properly vent your range, but the whole home ventilation design, including makeup air, is your HVAC person's responsibility to design and implement. In your climate, you will probably also need a heat exchanger as well, and the whole shebang can get to be pretty darn pricy. If it's rolled into your home HVAC quote, it'll be less of an "ouch" though. HVAC is an ouch enough on a new build, but once you reach a certain point, there's little % difference in a 25K quote and a 30K quote if that 30K includes everything you need HVAC wise. Don't forget bathroom and dryer ventilation to talk about with your HVAC person.


 o
RE: Need Advice - Kitchen Hood/Makeup Air

Your HVAC guys are definitely the ones to talk to regarding all your make-up air questions. Appliance dealers have a vested interest in NOT knowing anything about MUA, since in your jurisdiction (and mine) it could easily mean lost sales for high powered vent systems and ranges when installation costs get included (my $2000 VAH cost over $7K to install).

MUA does not have to come into the kitchen. Mine enters the furnace room and straight into my duct system.

BTW, is 400cfm really enough for a 36" Bluestar???


 o
RE: Need Advice - Kitchen Hood/Makeup Air

Our MUA system was installed by the HVAC crew in our new build. No we couldn't pass inspection without it even though I was just willing to keep a window open. Anyhow, the outside air enters through a main vent and comes into our kitchen through 5 small outlets. The intake passage which branches into 5 is surrounded in a space blanket type insulation and each outlet has a heated coil because air coming in on cold days no longer makes the home heat system efficient. There is a sensor that makes the coils fire up when the outside air is colder than 65 F. The juice this system sucks up is unbelievable, it makes the lights in the kitchen and even the interior fridge light dim and pulsate. I had my electrician set the MUA to come on only when my hood was on the 4th and most powerful setting. Thankfully I don't use that setting very often. Unfortunately, last summer when it was really hot, the switch to make it come on would trip when it was at the 2nd powersetting which is the one I use most often. That managed to blow hot outside air into the house which otherwise would remain reasonably cool. Summer was over by the time that got fixed


 o
RE: Need Advice - Kitchen Hood/Makeup Air

If you have a gas furnace, or if this will be a tight house, the HVAC guys will be adding make-up air anyway.


 o
RE: Need Advice - Kitchen Hood/Makeup Air

Thanks for all the info folks! I really appreciate it, I am going to have a talk with our builder, again, to have them look at the additional HVAC work. I will give an update as the excitement unfolds.

I do have to say that I am kind of steamed that the appliance people are either disingenuous or ignorant about MUA. Had they let us know in the beginning that this would be an issue, they would have earned some points in our book and we probably would have gone with whoever they suggested for the installation (probably earning them a nice referal fee).

If I hadnt chased this down before the construction started I would have had to change everything and pay an amendment fee on each change to the original plan (nearly everything), which would have cost thousands just on the change fees.

Cooksnews - the 400 CFM definately wouldnt work with the BlueStar, that is why I need to chase this down... if I cant get the MUA worked out I will need to change the range hood to something < 400 CFM which would require a less powerful/smaller range or living with the consequences of not having the appropriate blower. Changing the range would then change the cabinet drawings, granite order, and just about everything else in the kitchen.


 o
RE: Need Advice - Kitchen Hood/Makeup Air

There is a lot of research on the best way to add makeup air that has been done for commercial Kitchens. If you want the details ask and I will dig up some links, but it is techie stuff aimed at commercial applications. My interpretation of the research is that the best arrangement is to introduce the makeup air behind and below the heat source. I designed mine to bring air in below and under the rangetop. The recommendation is to bring in ~70% of the makeup air at the heat source and pull the rest from vents in the room. I am not currently tempering the makeup air. I'm sure I am losing heat, but I use my grill a lot and so far the cold makeup air tempers the radiant heat from the gill and makes it more pleasant to work close to the range top.


 o
RE: Need Advice - Kitchen Hood/Makeup Air

There are several ways to get makeup air. You can use passive vents, that will open when needed (I believe through any neg pressure).

You can also use HVR (Heat Recovery Ventalators) or ERV (energy Recovery Ventalators). These exchange air so that in the winter months the warm air going out helps heat the cold air comming in. In the summer vice versa. The difference between a HRV and ERV is that an ERV also echanges humidity. In a cold weather climate the warm moist air in the house will humidify the air that is coming from the outside. In the summer the the humidity will be stripped from the hot air comming in from the outside.

These systems can either be ducted to your forced air system or be independent. Typically you would place vents to capture outgoing air from humid places like bathrooms, Laundry rooms & Kitchens and you would want the fresh air to enter in places like bedrooms. This keeps helps maintain proper humidity as well.


 o
RE: Need Advice - Kitchen Hood/Makeup Air

The steps you or your HVAC supplier need to follow are:

Determine the air flow needed to properly vent whatever you are going to cook on the stove, given your hood size. This may be well above 400 cfm.

Determine the duct size that will keep the air flow, when venting at full power, between 1000 and 2000 feet per minute in the duct.

Determine the exhaust fan that will pull this flow against the negative pressure of the hood and ducting when the house is at the negative pressure you intend to let the house get to before the MUA kicks in. (This may require a blower that is _rated_ 1.5 - 2 X the flow intended to go up the hood.

Design an MUA system that will supply this much air at that negative pressure. The MUA system can be a far more daunting project than choosing the cooking ventilation system.

First, one wants the air warmed in the winter, and maybe cooled in the summer.

Second, the air should be supplied to the kitchen so that it doesn't disturb the upward flow of cooking effluent into the hood. Air that flows down a hall to the kitchen, or is introduced under the stove, or via an opposite wall may be suitable. Turbulent air when it reaches the cooktop is your enemy.

Third, ideally one wants only as much MUA as one is pulling through the hood, bathroom fans, fireplace, etc. This may be the mother of all residential "tuning" jobs to achieve.

What I have planned and partly fabricated to do this is as follows, but I think your HVAC guys can probably integrate yours with your air conditioning. Or if you have the funds and roof space, you might get Greenheck to design and build one for you based on their commercial designs.

I will use a heat exchanger (think car radiator for looks) above a ceiling diffuser that has a 30 x 30 inch opening. The heat exchanger is fed hydronic heat water from my oil burner via a large 013 Taco pump. Pump control will be based on thermostats set to keep the air under the heat exchanger at around 72F AND the air over the heat exchanger above 40F. (I live in NH.)

Electric units are obviously easier to plumb and control, but do require a significant power feed, as a serious kitchen ventilation system may require 100,000 BTU/hr be put into the MUA when the outside is at minimum temperature.

The blower I plan to use for the MUA airflow will be the largest Fantech in-line unit. It will supply air against its duct losses to counteract the probable 1000 cfm I can pull through a Wolf island hood using a 1500 cfm rated exhaust fan, plus the probable 600 cfm I can pull through a 1000 cfm rated NuTone (Broan) exhaust fan pulling air from ceiling registers located above my wall ovens, plus whatever the bathroom fans are pulling at any time.

MUA fan control is _planned_ to be based on the differential air pressure between my attic (open to the outside) and my kitchen. A proportional/integral/differential (PID) controller should be capable of adjusting MUA flow to keep the differential pressure between 0 and -0.02 inches H2O (forget how many pascals that is).

The tricky part in this design is to tune the PID controller parameters so the dynamic response is good without overshoot or oscillation. Simpler control designs, such as scaling the MUA fan power to the hood fan power have their own issues. In my case, with three bathroom fans and two kitchen fans, scaling the MUA fan to the hood fan is not appropriate.

HTH

kas


 o
RE: Need Advice - Kitchen Hood/Makeup Air

Thanks for all of the information and support folks. I am in roud 7 of resolving the makeup air issue, but I think (hope!) we are close to closure. Here are the tidbits that I've picked up talking with inspectors, hood manufacturers and our builder.

The new residential code IRC 2009 Chapter M15 REQUIRES that any hood ventilation system now have a makeup air system. This may come as a suprize to people doing a remodel and expecting to get their inspector to sign off.

For EnergyStar certification, you cannot have air that is just brought in from outside as the standard makeup air system because of the loss of heating/cooling efficiency in the home.

sfjeff suggested I talk to Prestige. I originally tried to call the people we would have been buying a hood from, never got a call back after leaving a couple messages. When I called Prestige, they put me on with one of their technical folks and we have been working together to design a hood that works.

Their two best options were:

Using the basement as an air resavoir and ducting from the basement to the hood.

Develop a residential self-compensating hood (as has been suggested above). This sounds good but its pretty expensive just for the fabrication, and I dont believe this includes installation.


 o
RE: Need Advice - Kitchen Hood/Makeup Air

I don't know the answer on this but I had the same problem - couldn't have an exhaust fan greater than 300 CFM. In my case they would have brought the make-up air in through the basement somehow - with a system priced out at $4,000. That was 4.5 years ago. This was a remodel in an energy inefficient wind tunnel home built in the 70's so I said no thanks. I got a 300 CFM fan - really happy with that decision since I can't stand the fan noise and use it as little as possible. Fortunately I didn't have my heart set on a range with a lot of BTUs - also no regrets there. I guess I was fortunate to have an appliance dealer and a contractor who were familiar with the issue.


 o
RE: Need Advice - Kitchen Hood/Makeup Air

Does anyone know if a kitchen addition/remodel in Maryland will run into this requirement? I purchased a new 600 cfm thermador hood on craigslist but really don't want to deal with putting in makeup air.


 o
RE: Need Advice - Kitchen Hood/Makeup Air

You'll have to talk with your local building inspection department -- "local" codes are generally closely modeled after the national or "international" codes, but there may be many years' lag between the two, as well as sections not adopted or otherwise overridden for your state, municipality, or other level.

(As an example, San Francisco has had rather bizarre requirements on water and DWV piping -- nothing non-metallic; no ABS, no PVC, no PEX -- claimed for EQ safety, believed by most to be a strong union's "contribution" to the codes.)


 o
RE: Need Advice - Kitchen Hood/Makeup Air

Our 1980's townhouse certainly isn't energy star efficient :) We were required to provide make up air but were allowed to keep it simple. We have a register built into the toe kick on the island that we can open for make up air when the hood is on and close when it's not. We vented it right through to the outside...pretty basic, a simple vent from one side of the room to the other. No fancy heat make up goober etc.

Honestly, we don't need the make up air...the house is NOT tight, but in a new build it might be a very important thing. I'd certainly follow code.


 o
RE: Need Advice - Kitchen Hood/Makeup Air

To keep things simple, my city has the same codes for new builds and renovations. While it meant a big charge for MUA in my 40yo leaky house, it also means I don't pay ongoing taxes for a huge fleet of inspectors who have to know how to assess every single house/project for air exchange.


 o
RE: Need Advice - Kitchen Hood/Makeup Air

Its been a while, but we are in the final throws of finishing the house and so I thought that I would post about what we found/have had to deal with for those out there who may be in the same boat.

We basically had to dicker with the building company for essentially 4 months, delaying the start of the house, because they were not allowed (internal regulations), to build a house that did not meet ComfortHome EnergyStar compliance. We ended up needing to request Prestige Hoods to design a one-off self compensating hood for us. The hood performed its regular function and in addition had a seperate set of ducting and 'chamber' that pulled air back into the hood from outside inlet duct ~10' from outlet duct to avoid spitting the exhausted air back into the house. Getting this designed/built/installed has run 4-5x what a regular 1200 CFM hood/blower would cost.

On the other hand, the rest of the kitchen... minus the missing wall oven, has come out great, and so we're looking forward to kicking on the hood at the start of our first meal in the house. Though I'm afraid its going to sound like a train chasing a banshee.

Thanks for all the posts and help!

Andrew


 o
RE: Need Advice - Kitchen Hood/Makeup Air

And thanks for the feedback. You are a little ahead of me as I don't yet have all the parts of my MUA installed. Does your MUA have a blower in it for replacement air, or does it use a passive connection to the outside air?

kas


 o
RE: Need Advice - Kitchen Hood/Makeup Air

I don't have an intake blower, but that was my choice, Im on an outside wall and so there is ~8 feet of ducting for each the intake and exhaust exits. There is an option to install an inline intake but we opted out, I don't think well miss it, if you aren't on an external wall then I think I would go with the extra intake blower.

Andrew


 o
RE: Need Advice - Kitchen Hood/Makeup Air

I know my question won't apply to the OP and he's in a different state subject to different codes...

But I just bought a BS 36" and I plan to just crack open a near by window (even in winter) when I crank up the Wolf 42" hood I also just purchased. Ignoring the code side of it, will this plan work (and avoid any issue with fireplace or furnace air reversing?). Thanks


 o
RE: Need Advice - Kitchen Hood/Makeup Air

Canyonhome,

That should work perfectly well... thats the real rub of the new code set. There isn't anything wrong with whatever size hood you have if you have a ready source of external air, and a cracked window fits the bill.

You probably want to crack a window on the other side of the kitchen pretty much as far from the hood as you can. This will cause the airflow in the room to be drawn into the hood, better confining smoke and odors.

Andrew


 o
RE: Need Advice - Kitchen Hood/Makeup Air

Schleiren photography shows that the most important aspect of introducing make-up air is to keep down turbulence around the cooktop that will disturb the uprising effluent that one is trying to get into the hood. Hood testing is performed in laboratories with large perforated diffuser panels planted along the bottom of a wall well away from the system under test.

For our more limited kitchen spaces, an ideal would be to introduce the air under all the cabinets so that it enters the kitchen through all the toe-kick spaces, but that would be a project all of its own, and the basement likely would be cluttered by ducting. If the air is entering from an attic space via a roof vent or eve vent, a diffuser that is large and well away from the hood is probably best, preferably in the ceiling of a nearby hall or in another room open to the kitchen.

No matter how the air is introduced, unless one lives where the ambient temperature is always ideal, it will have to be conditioned -- at a minimum warmed when it is cold outside. This adds complication.

If the MUA is passive (no fan), the house pressure will fall until low enough that the MUA flow through the pressure losses of its ducting, plus house leakage at that pressure, equal the hood flow that will also be limited by the negative house pressure. This is a non-trivial problem to analyze for MUA fan requirements. There are MUA systems for furnaces, so that safety issue could be overcome without a kitchen MUA, but the code is the code. Otherwise, a passive MUA must have a pressure loss low enough that the furnace doesn't backdraft.

Another approach is to do the minimum that is required by code and then open a window to supplement it when necessary. Air heating is still desirable, of course, so the window should be where the incoming air has some chance of being tempered before everyone present gets to sample the ambient temperature.

In all cases, avoiding backdrafts of furnaces, water heaters, and fireplaces is important, and the allowable negative pressure will depend on which of these is present. A fan powered oil burner will be a lot more tolerant than a fireplace that depends for its initial draft on the small (0.02 inches of water, I recall) pressure difference between a typical room in a house and the pressure at the roof.

kas


 o
RE: Need Advice - Kitchen Hood/Makeup Air

Have there been any recent developments on this issue? I called BS and Signature Hoods today--the BS tech I spoke to never heard of MUA, and the Sig Hoods tech said they don't recommend MUA. It seems no progress has been made there.

We will be installing a 48" BS with 1200cfm hood in a super tight new home. One advantage is that all appliances are sealed combustion, and the woodstove and fireplace have their own supply air.

Some questions about current MUA thinking:

1) Where is the best location to locate the MUA airstream? Under the range...in the back of the range...in the backsplash on either side of the range...in toekicks?

2) It seems a waste to heat MUA only to have most of it be exhausted. Is it really necessary to warm or cool MUA in extreme climates, if the airstream is properly located?

3) Does it make a difference if MUA is boosted with a fan, or passive, but in either case with a solenoid damper?

Thanks for the help. --Mark


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Appliances Forum

Instructions

  • You must be a registered member and logged in to post messages on our forums.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review the contents and make changes.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • It is illegal to post copyrighted material without the owner's consent.
  • HTML codes are allowed in the message field only.
  • No advertising is allowed in any of the forums.
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.



 
Click here to learn more about in-text links on this page.