Newly installed older dryer kicking off breaker

Posted by gale1965 (My Page) on
Thu, Oct 17, 13 at 1:58

This is a few - years-old dryer that was moved to a newly built house. We had to replace the old 3 prong cord with a 4 prong to fit the outlet in the new house. It runs for 10 minutes or so and then kicks off the breaker which appears to be two 20 amp switches. It is a Kenmore dryer, probably 5 or 6 yrs old. Any ideas?


Follow-Up Postings:

 o
RE: Newly installed older dryer kicking off breaker

Somewhere on the unit, and certainly in the installation manual, will be a specification about the required current. Mine uses a 30A circuit.

Breakers for 240 Vac circuits have to be two-pole so that both hot wires are interrupted at the same time. Using two single-pole breakers for such a circuit is a violation of NFPA 70.

Wiring has to be suitable for the current, so if 30A, the cable should be at least 10 gauge, 3-wire, w/ground. You would have to look into the outlet or into the breaker panel or at the cable itself if accessible to determine whether your wiring is adequate.

If the above is not obvious, please hire an electrician to take a look for you.

kas


 o
RE: Newly installed older dryer kicking off breaker

Electric dryers typically take 30 amp breakers so you likely are running it on an undersized circuit.

Two single-pole breakers were often used in the past so maybe this is an "old" wiring situation.


 o
RE: Newly installed older dryer kicking off breaker

As kas says, most 240V dryers require a 30 amp circuit. Do not just change the breaker, unless you can verify #10 wire.


 o
RE: Newly installed older dryer kicking off breaker

thanks. I have no idea why they would automatically put in a 20 amp breaker. My husband switched it out for a 30 amp so I'll have him check the wire size.


 o
RE: Newly installed older dryer kicking off breaker

Also, I found the book for the dryer (which I thought was long gone) and it says 30 amp in it. The wiring he has to check-would that be the wire that connects to the actual breaker?

He ran the dryer this morning and it didn't kick off the breaker.


 o
RE: Newly installed older dryer kicking off breaker

The wire between the breaker and the dryer. Fire hazard if it's undersized, please check!


 o
RE: Newly installed older dryer kicking off breaker

Called the builder and his electrical chart for the house shows 10-3 in that location. It also shows a 30 amp breaker so I suspect whoever was wiring grabbed the wrong breaker. How annoying.


 o
RE: Newly installed older dryer kicking off breaker

Hope whoever was wiring grabbed the right wire. ;)

Easy enough to check yourself, (might even see it printed on wire itself, if enough is exposed) but being as this is new construction I think you have enough cause for concern that they would send someone qualified to confirm. Personally I would not have changed the breaker without checking the wire first.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Appliances Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here