| For my kitchen renovation, my contractor is planning to install a 30" Whirlpool 400 CFM vent hood with a 6" duct. We are also planning to install a 30" RNB Bluestar range (which has 2 22,000 btu burners). Bluestar recommends a 600 CFM vent hood, but our contractor doesn't want to install one that large because it will require an air recovery system. Is the 400 CFM vent hood powerful enough? Opinions please!!!! |
Follow-Up Postings:
|
- Posted by GreenDesigns (My Page) on Tue, Jul 10, 12 at 21:55
| If you only use one burner at a time or don't use your oven, then 400 CFM might work. If that's the case, then you probably wouldn't buy a Blue Star! In many places, it violates code to install an appliance without following the manufacturer's installation instructions----including ventilation. Bottom line is, if you want a pro grade range, then you're looking at buying a pro grade vent. It's not optional. |
|
- Posted by SparklingWater (My Page) on Tue, Jul 10, 12 at 22:08
| 400 CFM's of vent flow for a 30" Blue Star four burner isn't enough. Tell your contractor 600 CFM's minimum as that is what Blue Star recommends and that's what you need arranged. MUA isn't that hard to add in and you'll need it especially if your house is "tight", i.e., limited inherent air leaks. Good luck. |
|
| Sparkling, What do you mean make up air isn't that hard to add? Depending on where you live, code requires conditioned make up air. The cheapest make up air unit that I could find that would meet code here was $7,000 not including installation. Make up air is a serious issue not to be taken lightly. The consequences of not properly addressing the issue are at best, not meeting code and at worst depressurizing your house and death due to CO poisoning. |
|
- Posted by SparklingWater (My Page) on Wed, Jul 11, 12 at 0:01
| Sorry ribs1, you're caught in a situation many of us don't face and I surely empathize with the expense of conditioned Make Up Air (MUA) due to code. I read the OP asking about Blue Star BTU and venting CFM's. MUA is increasingly considered and discussed when re-doing or building a kitchen, and should be discussed pre-purchase of a pro-range. MUA has been an active topic of interest here on GW as well as on greenbuildingsdesign.com in "Makeup Air for Range Hoods" (linked below) and on many HVAC forums. Good reading and sources for solutions for industrial conditioned MUA (which perhaps will help you somehow too ribs) are also found on http://www.greenheck.com. MUA, passive or active, is available without excessive expense for most of us as we are not restricted, as yet, by specific code requirements. I'm firmly in the camp of matching one's cooktop/range purchase to one's budget for proper ventilation and MUA and more to avoid any risk of acute illness/death due to carbon monoxide poisoning from lack of replacement air. |
Here is a link that might be useful: Makeup Air for Range Hoods
|
| As I replied on the kitchen forum, YOU need to make the tradeoff between CFMs and the cost of makeup air. Depending on what you cook, 400 CFMs may be adequate. CFM recommendations by manufacturers make the assumption that you are running all the burners on maximum. I have a 600 CFM hood over a pro-style range and in 10 years I have hardly ever needed to put the hood on max - mostly low or med. As long as you're getting a real range hood and not an OTR, 400 CFMs may meet your needs. |
|
| Make sure your contractor is correct about the code requirement in your area. In many locales you don't need makeup air for 600 CFMs, but some of the colder climates have lower limits. |
|
| I live in the mild SF Bay area, and can run into make up air requirements, if there are gravity gas appliances or fireplaces in the conditioned envelope. I got rid of my fireplace, put my water heater in a sealed (from house, not from crawlspace/attic) closet, and moved the furnace to the attic. Otherwise, I'd be limited to about 425CFM without MUA. So, check your local code. Here is mine: 1. Make up air |
|
| Two good messages there, attofarad. The first is that at least in one locale the MUA requirement is worded to accommodate both house size and configuration of combustion appliances. The second is that one escape from deliberately adding MUA can be to seal off those combustion appliances that have CO backdraft risk. I think gravity appliance would exclude blower-fired oil burners, but at a somewhat higher negative pressure than for gravity appliance backdraft, these too can backdraft, so an even more refined requirement would list negative pressures vs. appliances. I have seen such a list somewhere. I'll report the link if I find it. kas |
Please Note: Only registered members are able to post messages to this forum. If you are a member, please log in. If you aren't yet a member, join now!
Return to the Appliances Forum
Instructions
- You must be a registered member and logged in to post messages on our forums.
- Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review the contents and make changes.
- After posting your message, you may need to refresh the forum page in order to see it.
- It is illegal to post copyrighted material without the owner's consent.
- HTML codes are allowed in the message field only.
- No advertising is allowed in any of the forums.
- If you would like to practice posting or uploading photos, please visit our Test forum.
- If you need assistance, please Contact Us and we will be happy to help.