We picked up our Miele induction cooktop yesterday and I was hoping my husband could finish running the wire and hook it up this weekend. When he opened the box, the wires have this weird connector on the ends.

Miele Cooktop connection

The installation diagram just shows plain wires. Is there supposed to be a special connection that this hooks into or is this just some kind of protection for the wire ends that we just cut off? My husband went to Lowes to see if he could find anything. They sent him to an electrical supply place and they didn't have a clue either.

Miele is closed today and the sales rep didn't know. He has a call into the Miele rep but since it's a holiday he may not call until Mon.


Follow-Up Postings:

 o
RE: Help: Electrical Connection Miele Induction Cooktop

They are fairly standard on Euro kit. I believe they are designed for easy connection to control boards and plugs. If you were to open up the cooktop, or oven, ect... you'd see the other end has the same thing or sometimes eyes and those are attached to the control board with screw terminals.

I'd just get a plug and matching receptacle and wire it up. You could always cut those ends off and hardwire it into the box with wire nuts too. Would be a ba idea to check with your local inspector as some places don't like you to cut those and some don't like 220v plugs that don't come from the factory.

As long as your connections are tight and encased in a UL approved device you are gonna be safe.


 o
RE: Help: Electrical Connection Miele Induction Cooktop

Thanks! We were just at Ace Hardware buying a new chain saw and my husband saw a 220 v plug that he figured was what we needed for it but we held off to see if anyone had a response. Maybe after we cut down these trees we'll try it.


 o
RE: Help: Electrical Connection Miele Induction Cooktop

They're made to go into screw-on terminals. Or clamp-down, as it were.


 o
RE: Help: Electrical Connection Miele Induction Cooktop

Hopefully someone can give me a hand....So I am awaiting delivery of a Miele 5773 induction cooktop and I am getting ready to run the 6 gauge (50A) wire for the cooktop.

Do I need to install 6-2 wire or 6-3 wire? Based on the installation manual and the picture above, there are two hots and a ground. No neutral. So I assumed I need to install 6-2 wire but 6-2 wire has a hot, neutral and ground. So it seems I need to run 6-3 wire (2 hots, neutral and ground), but what do I do with the neutral that does not hook up to the cooktop?

Any help is greatly appreciated!!

Thanks!
Lou


 o
RE: Help: Electrical Connection Miele Induction Cooktop

No, 6-2 wire has two conductors and a ground. You are allowed to connect the two conductors to two breakers in the box for a 220v circuit (a double breaker). You must put a marking (piece of tape, black or brown) around the white wire at both ends to indicate that it is not a neutral but a 'power' conductor.

However, if this is a new circuit you might want to think about using 6-3 instead. Some time down the road that cooktop might be replace with something than requires a neutral. For the Miele, you would just cap it off inside the box where the other connections are made.


 o
RE: Help: Electrical Connection Miele Induction Cooktop

Great thanks for the info. I am going to run 6-3 for future proofing and just cap the neutral in the box.

Thanks for your help.


 o
RE: Help: Electrical Connection Miele Induction Cooktop

Because disconnection of power to the cooktop may require disconnection of this cable (unless the breaker box has or supports lock-out means or is in view of the cooktop), it is better to use tap type connectors (see link for one example) in the box where this cable terminates instead of, say, large wire nuts, such as the pale blue size. The box has to be big enough to fit the tap connectors, as well as handling the bend radius limits and volume that apply to number six conductors in boxes.

Alternatively, taped up u-bolt connectors can be used. In both cases, the crimp on the cable keeps the strands from wandering about and potentially not contributing to the current path. If stranded number six conductors are used on the supply side, similar crimp sleeves should be used for tap connectors and u-bolts. MSC Direct is one source of crimp sleeves.

kas

Here is a link that might be useful: Greaves Corp PBS2 for example, page 56


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Appliances Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Please review our Rules of Play before posting.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here