Another vent hood mua question: please help

Posted by rovo (My Page) on
Mon, Apr 22, 13 at 14:11

Hello all: I have done my best to weed through the complex vent hood/make up air threads, and while I know codes vary by many factors, not the least of which is location, I am hoping for some general guidance here. My advanced apologies if this has been answered in previous threads; if so, I cannot find them or make sense of them :(

I have what I consider to be a relatively simple situation: small kitchen, budget DIY refresh with removal of useless OTR microwave that we want to replace with a vent hood. We have existing 7" venting that routes horizontally approximately 2 feet through the dreaded soffits and then up through the roof on our one story home. All we want to do is put in a vent hood we purchased, rated at 670 cfm's, or at this point, ANY vent hood to meet our meager needs. No wok frying, totally average (47k btu) Bosch gas cooktop with electric oven. One gas fireplace within the "open concept" kitchen/nook/family room combo; gas water heater in garage with simple venting (e.g. opening in garage walls with vents to the outside), furnace in attic, two underpowered bathroom fans. 2300 sq ft home in Northern California built in 1999.

I purchased a chimney style vent hood rated at (670 cfm) via amazon a while back, and did not realize that I could be wading into the mua world. I seriously doubt this hood really moves 670 cfm's, but still want to ensure that it meets code and does not pull co2 into our home. Not willing to get into mua solutions, both from a cost and over-improving standpoint.

I cannot find a single reference to what floor/lowest level cfm fan rating that we would need to avoid mua requirements. As far as i can tell, codes do not list this explicitly, nor was a call to our title 24 energy commission helpful. Apparently, there is some ASHRE calculation one must do for the whole house, but the information is not free and I was advised to consult an HVAC pro.

Willing to consult an HVAC pro, if that is the recommendation here. Or, if any of you GW experts have general guidelines on what the highest CFM rating for a vent hood is in my area, whom to contact, etc, it would be much appreciated. Thanks!


Follow-Up Postings:

 o
RE: Another vent hood mua question: please help

In San Jose, the link below applies. See C.1.

Edit:

Also, this link

http://resaveguide.lbl.gov/step-1-assess-the-home

Here is a link that might be useful: SJ ventilation requirements

This post was edited by attofarad on Mon, Apr 22, 13 at 18:30


 o
RE: Another vent hood mua question: please help

Thank you, great link. From what I gather, I will need to stick to a 300 cfm vent hood, give or take, to avoid MUA requirements. Much appreciated!


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Appliances Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Please review our Rules of Play before posting.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here