My kitchen will have a section of countertop that will have an adjacent toaster oven and microwave oven (each with its own receptacle.) It seems that it would make sense for thes to share a single 20A circuit, and to have all the others go another. Any ideas on the typical power draw for these appliances?

Thank you for reporting this comment. Undo
swampwiz

How many amps for that?

    Bookmark   June 3, 2009 at 8:57PM
Thank you for reporting this comment. Undo
sbcichocki

My electrician son says our microwave pulls 14.4 (average counter top model), and a toaster oven will pull more than 5. A breaker will trip at 80%. So, you can have them on the same circuit, you just can't run them at the same time.
I actually have this problem. My toaster and micro are on the same circuit. If I have them both on at the same time, the circuit flips. That WILL be fixed in my next kitchen, micro on it's own circuit.
S

    Bookmark   June 3, 2009 at 9:03PM
Thank you for reporting this comment. Undo
live_wire_oak

A toaster oven and a MW together will trip a breaker. A MW really needs a dedicated circuit, as they use up most of the 20 amps on a 20 amp circuit. Plus, you need 2 20 amp GFI countertop receptacle circuits. If you use your toaster oven a lot, I'd suggest a dedicated circuit for it as well. Appliances that heat use a LOT of electricity, and if you have it plugged into the same circuit as your coffee maker and try to use both at the same time, you run the risk of tripping it then too.

    Bookmark   June 3, 2009 at 9:49PM
Thank you for reporting this comment. Undo
lexluthor

My old kitchen had that too and it'd trip the circuit if both were on.

So happy to now have a dedicated line for the MW so I can run both at once.

I didn't get a dedicated drop for the toaster oven, but everything else is split on 3 more circuits, so I think O have enough power.

    Bookmark   June 3, 2009 at 10:24PM
Thank you for reporting this comment. Undo
2ajsmama

We don't use the toaster that much, and I don't think we've ever used it the same time as MW but it is a good idea to have MW on its own circuit. Coffeemakers can pull 8A or so too, so you might want to make sure where you plan to put your coffeepot is on a different circuit from toaster oven since there's a good chance the 2 will be on at the same time. As long as each is on a different small appliance circuit, no need for dedicated for either one. Look at what else you might have running at the same time - crockpot, electric frypan/wok/griddle, you might want a third small appliance circuit in a certain area, as well as the dedicated MW circuit.

Fridge should be on its own circuit - electrician should know that. I'd go 20A (not sure it's required by code but good idea), even though my Energystar fridge says max draw is just over 6A.

    Bookmark   June 4, 2009 at 8:17AM
Thank you for reporting this comment. Undo
davidro1

Isn't it a requirement to have double circuits at kitchen outlets? Then each hole in a double outlet gets 15 Amperes. Each appliance plugged in gets 15A.

    Bookmark   June 4, 2009 at 9:45AM
Thank you for reporting this comment. Undo
live_wire_oak

David you're confusing amperage with voltage. The requirement is for 2 20 amp "countertop" electrical services of 120 volts, and then code requires that each appliance installed be installed to manufacturer's requirements. Many times that means installing dedicated 120 amp circuits for the refrigerator, microwave, vent hood, and even a gas range. Some manufacturers stipulate that their appliance only go on a dedicated circuit, usually because the power draw at startup is a lot more than at running.

More information about planning proper kitchen wiring correctly can be found at the Electrical Wiring Forum. Be aware that many older homes must undergo an upgrade in service to the home in order to do a kitchen remodel and that needs to be factored into the budget.

Here is a link that might be useful: Electrical Wiring

    Bookmark   June 4, 2009 at 9:54AM
Thank you for reporting this comment. Undo
brickeyee

"A breaker will trip at 80%."

Breakers start to trip at 100% of rated current.

Residential breakers are 'inverse time' breakers, also known as thermal-magnetic.

They will tolerate short overloads for periods of up to minutes, while tripping in milliseconds at many times their rating.

This is accomplished by using both a heater to trip the breaker, and a coil to trip using the magnetic force generated by a large current overload.

Toasters can run well over 1000 watts and pull over 10 amps.
Microwaves have a starting surge that can pull 15 amps.

You can get away with using them on separate 20 amp counter circuits, and two are required by the NEC.

    Bookmark   June 4, 2009 at 9:58AM
Thank you for reporting this comment. Undo
yesdear

One other solution--we purchased a Panasonic microwave/convection oven. Expensive but saves space in the appliance garage and avoids this dilemma. Frankly, we use it mostly as a MW.

    Bookmark   June 4, 2009 at 12:00PM
Sign Up to comment
More Discussions
scrappy25 renovation Part 4, final reveal, white inset/soapstone
Finally got some "completed" pictures, please...
scrappy25
Would you please review kitchen floorplan? 1880s house
Hello, I am new to posting, though I have read the...
islandgarden
Help on Cabinet Approach / Selection
Hi, I've actively scoured the forum for useful tidbits...
fshine
Can you use IKEA base cabinets as wall cabinets?
Wanting something larger for over-the-fridge than their...
lookintomyeyes83
1880s house kitchen: need to work in the current space
Note this is cross-posted at suggestion of a reader Plans...
islandgarden
Sponsored Products
Gray & Red Deluxe Nonstick 9'' x 13'' Covered Cake Pan
$16.99 | zulily
Oster OGG3701 .7 cu. ft. Microwave Oven - 836321003969
$69.99 | Hayneedle
Juno Trac 12 150 Watt 12 Volt White Canopy Transformer
Lamps Plus
Spice Ramekin Bowl Set
$12.99 | zulily
Fiesta Ivory Chop Plate 11.75 in. - Set of 4 - HPJC911
$87.96 | Hayneedle
Kovacs Circuit Transitional Large Pendant
1800Lighting
Emile Henry 9 in. Pie Dish - Sand - 966131
$40.00 | Hayneedle
Nonstick 9'' x 5'' Loaf Pan
$7.99 | zulily
© 2015 Houzz Inc. Houzz® The new way to design your home™