While swapping out a bathroom wall mount fixture, I see there's a plastic, round "old work" box that was used with the BX cable. Any advice on an easy way to ground the fixture without getting too involved with redoing everything? If I were to temporarily remove the box, I could reach the cable. Could I wrap/clamp some extra copper to the BX so I have something to connect with the fixture ground wire when the box is reinstalled? Thanks.

Thank you for reporting this comment. Undo
mike_kaiser_gw

The term "BX" is sometime used a little loosely but I'm going to presume you have some kind of metal jacketed cable without a ground wire. For those kind of cables, the jacket is the equipment ground. With type AC cable there is also an aluminum bonding strap but that can't enter the box.

You need to either replace the box with a metal box or replace the cable with something with a "real" ground (NM-B [Romex] or metal clad cable, type MC).

I'm not sure an old work box is designed to support a fixture. Maybe someone could comment on that.

    Bookmark   December 7, 2009 at 9:53PM
Thank you for reporting this comment. Undo
homebound

Yes, I'm talking about the metal jacketed cable without a distinct ground wire. I was hoping to not replace the box, since the hole is round, I'd be patching drywall, etc. and the room just got painted. I was hoping to be able to attach a wire to the jacket and extend it into the box. No solution for that without swapping the box? BTW, the walls have metal and there is one adjacent to the box, for what it's worth.

    Bookmark   December 8, 2009 at 7:55AM
Thank you for reporting this comment. Undo
brickeyee

Plastic boxes are not listed for use with AC.

Without a cable clamp there is no way to obtain contact with the armor.

    Bookmark   December 8, 2009 at 8:12AM
Thank you for reporting this comment. Undo
homebound

I picked up a grounding wire clamp, size 3/8" to 1". Menat for pipe, of course, but think that will do it?

    Bookmark   December 8, 2009 at 2:39PM
Thank you for reporting this comment. Undo
mike_kaiser_gw

There's no way that will meet code to accomplish what you want to do without replacing the box or cable. Plastic boxes are simply not approved for use with that kind of cable. Can you jury rig something? Of course, but it's not recommended.

    Bookmark   December 8, 2009 at 3:04PM
Thank you for reporting this comment. Undo
kurto

That might provide an electrical path to ground, but it won't be code-compliant. Please refer to Brickeyee's comment.

    Bookmark   December 8, 2009 at 3:05PM
Thank you for reporting this comment. Undo
homebound

Got it. Thanks much.

    Bookmark   December 8, 2009 at 5:05PM
Thank you for reporting this comment. Undo
tom_in_sc

If it were MC cable (with a ground in it) would the plascit box be ok? How would the cable be connected to the box?

    Bookmark   November 10, 2010 at 12:44PM
Thank you for reporting this comment. Undo
pharkus

Fan box.

It's more than you need, but it will solve your problem.

Closest thing I can think of to what it is that you really need: a metal old-work box.

Here's an example

    Bookmark   November 10, 2010 at 1:58PM
Thank you for reporting this comment. Undo
brickeyee

"Fan box."

That would do the trick, and can be installed through the existing hole in the ceiling.

The clamps in the box are most likely for NM cable though, so you need to use a knockout with an AC cable clamp.

Hint: Attach the cable clamp to the cable and thread the wires through the knockout hole.
Place the box in the hole and pull the cable clamp into the hole and put the lock nut on and tighten.
Fasten the box to the bar.

    Bookmark   November 10, 2010 at 3:15PM
Sign Up to comment
More Discussions
Garage florescent light flickering - bulb or fixture problem?
I replaced the GE F40 RES garage lights with a GE F40...
bibbus 7b
Need to Understand GFCI Requirements.
I posted this in the remodeling section, but I think...
homechef59
Power to shed
Looking to run one 20 amp circuit to my shed and I'm...
ohio45424
Grounding Service panel 200amp
Is the new NEC saying to no longer run # 4 copper wire...
36066
Testing a fluorescent bulb
I've got a light box that isn't lighting up when I...
kudzu9
Sponsored Products
Visio Window Steam Cleaner
$59.99 | zulily
Bermuda King Headboard
Overstock.com
Radiax 3000K 35-Degree 6.5-Watt LED Beach Flood Light
Lamps Plus
Real Fyre Direct Vent Fireplace Insert with Wrought Iron Fire Screen - AMK310
Hayneedle
Hunter Ceiling Fans 24 in. Antique Pewter Extension Downrod 28056
$17.97 | Home Depot
Addison ross tungsten diamond pattern picture frame 5x7
Origin Crafts
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™