I installed a sub-panel in our garage/barn. 100 amps. Put 2-2-2-4 mobile home service cable in 2 inch conduit. Now I would like to connect my backup generator at the barn instead of the house. (outside) I have an interlock on the main panel, so would need to run #10 wire (for 30 amps) between the generator input plug box (to be moved to the barn) and the main panel. About 70 feet. Here's the question--can I run the wire from the barn to the main panel in the 2" conduit which feeds the sub-panel. Of course, the #10 wire from the main panel would have no connection in the sub-panel. I just would like to use the conduit. Thanks.

Thank you for reporting this comment. Undo
Ron Natalie

There's no prohibition on running unrelated things like this in the same conduit if that is what you are asking.

You have two issues however. One is regulatory and the other is practical.

The regulatory issue is conduit fill. I'm not going to work it out but I suspect you're OK. You can typically get 8 #2 wires into a 2" conduit legitimately.

The practical matter is I assume you already have the cable in the conduit you will probably find it daunting to pull additional #10's through there.

    Bookmark   December 5, 2012 at 9:05AM
Thank you for reporting this comment. Undo
Bob_on_JennysCreek

Thanks for the info, and yup, you're probably right about pulling the #10s. Could be a bad day.

    Bookmark   December 12, 2012 at 11:03PM
Sign Up to comment
More Discussions
Electrical Problem.
My mom's house has a problem with the lights temporarily...
Debra Johnson
Confused & need help please
I know just about zero when it comes to electricity....
bicyclegirl1
Testing a fluorescent bulb
I've got a light box that isn't lighting up when I...
kudzu9
Outdoor subpanel as AC disconnect
Can we use an outdoor subpanel as an AC disconnect?...
ylmzm
Please Critique Low-Volt (Home Automation) Plan/Proposal
GW/Houzz Community, As always, I want to thank this...
Andrew K.
Sponsored Products
Corner Eclipse LED Wall Sconce
Lightology
Humanscale | Element 790 LED Light
$309.00 | YLighting
Nikko/G Outdoor Wall Sconce by LBL Lighting
$240.00 | Lumens
Ceeley Toilet Paper Holder
Signature Hardware
Stella Quilted Patchwork Throw
Overstock.com
Patton Energy Star Brushed Nickel One Light Vanity Fixture with Frosted Glass
$41.99 | Bellacor
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™